For 3 psi, I think you'd be doing the owner a dis-service by installing
PRV's - he has to test and maintain those things (supposedly).

Ed Kramer
Lawrence, KS

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Tuesday, February 18, 2014 1:50 PM
To: [email protected]
Subject: Static Pressure/Working Pressure

3.8.1.9.2 Static Pressure. The pressure that exists at a given point under
normal distribution system conditions measured ...
We have a project with an electric pump and when combined with the current
water supply the churn pressure is 178 psi. A nationally known engineering
firm wants us to install PRV's on the lowest level of the building because
of the 3 psi. Our position is that the pressure only exists at churn and
that is similar to an overnight pressure surge in a municipal water system.
The over pressure will be compensated for by the pressure relief valves once
the pump stops. Are we being overly loose with our interpretation of
"normal" or is the engineering firm correct?
Ron F  