NFPA 20 2013 edition added:
11.4.1.2.4 Single wall fuel tanks shall be enclosed with a wall, curb, or dike 
sufficient to hold
the entire capacity of the tank.

and

11.4.1.2.8 Tank Venting. If a double-wall tank is installed, the interstitial 
space be tween the
shells of the diesel fuel storage tank shall be monitored for leakage and 
annunciated by the
engine drive controller. The signal shall be of the supervisory type.

but of course those wouldn't apply to an existing installation 

Mike Morey, CFPS, SET
Planner Scheduler/Designer
BMWC Constructors, Inc.
1740 W. Michigan St, Indianapolis, IN 46222
O: 317.651.0596 | C: 317.586.8111
[email protected] | www.bmwc.com

________________________________________
From: [email protected] 
<[email protected]> on behalf of Martinez, Dewayne 
<[email protected]>
Sent: Wednesday, April 09, 2014 8:05 AM
To: [email protected]
Subject: RE: Diesel fuel tank

That makes sense, I was thought I was missing something from NFPA.

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Matt Grise
Sent: Wednesday, April 09, 2014 6:49 AM
To: [email protected]
Subject: RE: Diesel fuel tank

Agreed. The insurance carrier may be concerned about the cost of a diesel fuel 
remediation.

Matt Grisé PE*, LEED AP, NICET II
Sales Engineer
Alliance Fire Protection
130 w 9th Ave.
North Kansas City, MO 64116

*Licensed in KS & MO

913.888.0647 ph
913.888.0618 f
913.927.0222 cell
www. AFPsprink.com

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Todd - Work
Sent: Wednesday, April 09, 2014 6:47 AM
To: [email protected]
Subject: Re: Diesel fuel tank

EPA

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com
860-535-2080 (ofc)

> On Apr 9, 2014, at 7:45 AM, "Martinez, Dewayne" 
> <[email protected]> wrote:
>
> We have an existing system with a diesel fuel pump and tank(280gpm)
> that was installed back in 1991.  The insurance carrier is requesting
> that either a new duel wall tank or a dike containment system be installed.
> I have looked through NFPA 20 and didn't see anything requiring either.
> Should I be looking in a different place?
>
> Thanks,
>
> Dewayne
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to