The last couple of FM jobs I've done required both a double wall tank and a 
containment dike.

NFPA 20, 2010 11.4.1.2.4 Fuel tansk shall be enclosed with a wall, curb or dike 
sufficient to hold the entire capacity of the tank.

This isn't in the 2007 edition at least not in the fuel tank section, so it 
must be new.

Richard Mote ET
Design Manager
Rowe Sprinkler Systems, Inc.




-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Martinez, 
Dewayne
Sent: Wednesday, April 09, 2014 7:45 AM
To: SprinklerFORUM
Subject: Diesel fuel tank

We have an existing system with a diesel fuel pump and tank(280gpm) that was 
installed back in 1991.  The insurance carrier is requesting that either a new 
duel wall tank or a dike containment system be installed.
I have looked through NFPA 20 and didn't see anything requiring either.
Should I be looking in a different place?

Thanks,

Dewayne

 