The AHJ is following 2007 but the insurance carrier may be following a newer version.
-----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Richard Mote Sent: Wednesday, April 09, 2014 7:08 AM To: [email protected] Subject: RE: Diesel fuel tank The last couple of FM jobs I've done required both a double wall tank and a containment dike. NFPA 20, 2010 11.4.1.2.4 Fuel tansk shall be enclosed with a wall, curb or dike sufficient to hold the entire capacity of the tank. This isn't in the 2007 edition at least not in the fuel tank section, so it must be new. Richard Mote ET Design Manager Rowe Sprinkler Systems, Inc. -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Martinez, Dewayne Sent: Wednesday, April 09, 2014 7:45 AM To: SprinklerFORUM Subject: Diesel fuel tank We have an existing system with a diesel fuel pump and tank(280gpm) that was installed back in 1991. The insurance carrier is requesting that either a new duel wall tank or a dike containment system be installed. I have looked through NFPA 20 and didn't see anything requiring either. Should I be looking in a different place? Thanks, Dewayne _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler .org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler .org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org