Was the containment nothing more than concrete curbs around the tank?

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
Bobby Gillett
Sent: Wednesday, April 09, 2014 7:30 AM
To: [email protected]
Subject: Re: Diesel fuel tank

The last couple FM projects I did also required both, and the
containment dike had to contain 130% of the capacity of the tank.

Bobby Gillett
*Living Water Fire Protection, LLC*
1160 McKenzie Rd.
Cantonment, FL 32533
(850) 937-1850
livingwaterfp.com  <http://livingwaterfp.com/>


On Wed, Apr 9, 2014 at 7:07 AM, Richard Mote
<[email protected]>wrote:

> The last couple of FM jobs I've done required both a double wall tank 
> and a containment dike.
>
> NFPA 20, 2010 11.4.1.2.4 Fuel tansk shall be enclosed with a wall, 
> curb or dike sufficient to hold the entire capacity of the tank.
>
> This isn't in the 2007 edition at least not in the fuel tank section, 
> so it must be new.
>
> Richard Mote ET
> Design Manager
> Rowe Sprinkler Systems, Inc.
>
>
>
>
> -----Original Message-----
> From: [email protected] [mailto:
> [email protected]] On Behalf Of Martinez,

> Dewayne
> Sent: Wednesday, April 09, 2014 7:45 AM
> To: SprinklerFORUM
> Subject: Diesel fuel tank
>
> We have an existing system with a diesel fuel pump and tank(280gpm) 
> that was installed back in 1991.  The insurance carrier is requesting 
> that either a new duel wall tank or a dike containment system be
installed.
> I have looked through NFPA 20 and didn't see anything requiring
either.
> Should I be looking in a different place?
>
> Thanks,
>
> Dewayne
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to