He decided to "throw it away...."

Sent from my iPhone

> On Apr 9, 2014, at 12:45 PM, John Denhardt <[email protected]> 
> wrote:
> 
> Funny but true story:
> 
> I had a client who was worried about security with the test header 
> penetrating the exterior of the building.  They had us remove the test header 
> after each test and store in the fire pump/mechanical room.  We were 
> instructed to install a blind flange using sealant on the bolts so the blind 
> flange would not be easily removed.  Well, the client decided to have the 
> area cleaned up.  To everyone surprise, when showed up for the annual fire 
> pump system test, no test header was in the room.  After the investigation, 
> the employee that cleaned the room said he did not know what it was but it 
> was big, heavy and had brass valves.  He made the decision to throw it away.
> 
> Amazing - you can not make this stuff up!
> 
> John
> 
> 
> John August Denhardt, P.E., FSFPE 
> Strickland Fire Protection Incorporated 
> 5113 Berwyn Road 
> College Park, Maryland 20740 
> Office Telephone Number:  301-474-1136 
> Mobile Telephone Number:  301-343-1457 
> FIRE SPRINKLERS SAVE LIVES - Can you live without them?
> 
> -----Original Message-----
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of David 
> Autry
> Sent: Wednesday, April 09, 2014 2:32 PM
> To: [email protected]
> Subject: RE: pump test header valves
> 
> LOL, I was think of one that I did, that had sixteen (16) valves.
> 
> 
> David Autry
> 
> Meininger Fire Protection Inc.
> 2521 W L St. Suite No.4
> Lincoln, Ne 68522
> Voice (402) 466-2616
> Fax (402) 466-2617
> [email protected]
> 
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of
> rongreenman .
> Sent: Wednesday, April 09, 2014 12:43 PM
> To: [email protected]
> Subject: Re: pump test header valves
> 
> Too bad, I was liking the 2 1/2" plastic pipe caps idea a lot. The
> removing the entire test header is Ok but that has to be at least two and
> probably three guys on anything bigger that a couple of three valves.
> 
> 
> On Wed, Apr 9, 2014 at 10:20 AM, Bobby McCullough <
> [email protected]> wrote:
> 
>> My mistake.  The 2.5" plastic caps are hose threads & installed on the
>> valve where only the caps were stolen, which is common.  I only have a
>> few projects with valves stolen & there we used threaded ductile caps
>> on the nipples & locked the valves in the pump room.
>> 
>> -----Original Message-----
>> From: [email protected]
>> [mailto:[email protected]] On Behalf Of
>> Ben Young
>> Sent: Wednesday, April 09, 2014 12:05 PM
>> To: [email protected]
>> Subject: Re: pump test header valves
>> 
>> Bobby,
>> 
>> Do you mean screw-on PVC caps, or the plastic break caps for FDC snoots?
>> 
>> Thanks for the feeback everyone, I didn't realize this was so common.
>> I'll have to start recommending this to some of our clients in high
>> theft areas from now on.
>> 
>> 
>> Benjamin Young
>> 
>> 
>> On Wed, Apr 9, 2014 at 9:50 AM, Bobby McCullough
>> <[email protected]
>>> wrote:
>> 
>>> We use 2.5" plastic caps.  Not much value at the scrap yard.  Take
>>> the
>> 
>>> valves in the pump room and use a bicycle cable & lock to keep them
>>> from wandering off.
>>> 
>>> Bobby McCullough
>>> Atlanta Sprinkler
>>> 
>>> 
>>> -----Original Message-----
>>> From: [email protected]
>>> [mailto:[email protected]] On Behalf Of
>>> Morey, Mike
>>> Sent: Wednesday, April 09, 2014 8:49 AM
>>> To: [email protected]
>>> Subject: RE: pump test header valves
>>> 
>>> They make test header outlets with male threaded outlets (basically
>>> the opposite of an FDC) with hose caps that you remove and then
>>> screw on hose valves that have a female swivel on the inlet side.
>>> Of course
>> 
>>> there's still the risk of someone stealing the hose caps and/or
>>> brass adapteer fittings that provide the male hose thread, but at
>>> least the valves aren't sitting out there too.
>>> 
>>> Mike Morey, CFPS, SET
>>> Planner Scheduler/Designer
>>> BMWC Constructors, Inc.
>>> 1740 W. Michigan St, Indianapolis, IN 46222
>>> O: 317.651.0596 | C: 317.586.8111
>>> [email protected] | www.bmwc.com
>>> 
>>> ________________________________________
>>> From: [email protected]
>>> <[email protected]> on behalf of Ben
>>> Young <[email protected]>
>>> Sent: Wednesday, April 09, 2014 8:40 AM
>>> To: [email protected]
>>> Subject: pump test header valves
>>> 
>>> Last week I was at an ASCET meeting where a pump presentation was
>> given.
>>> 
>>> Someone asked the presenter if it was allowed to remove the test
>>> header valves and keep them in the pump room to stop them from being
>> stolen.
>>> 
>>> The presenter and few other attendees chimed in that this was ok,
>>> and nothing in 20 or 25 said the valves had to be constantly in place.
>>> 
>>> I didn't think of it at the time, but now I'm asking myself how then
>>> do you keep debris out of the test header?  The only thing I can
>>> think
>> 
>>> of is that you would have to cap the nipples or if you remove the
>>> nipples, plug the holes in the test header.  This sounds like it
>>> will cause problems down the road to me.
>>> 
>>> Have you guys ever seen this done before?
>>> 
>>> Benjamin Young
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
>>> kl
>>> er
>>> .org
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
>>> kl
>>> er
>>> .org
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> 
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
>>> kl
>>> er.org
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>> er
>> .org
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> 
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>> er.org
> 
> 
> 
> --
> Ron Greenman
> Instructor
> Fire Protection Engineering Technology
> Bates Technical College
> 1101 So. Yakima Ave.
> Tacoma, WA 98405
> 
> [email protected]
> 
> http://www.bates.ctc.edu/fireprotection/
> 
> 253.680.7346
> 253.576.9700 (cell)
> 
> Member:
> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
> 
> They are happy men whose natures sort with their vocations. -Francis
> Bacon, essayist, philosopher, and statesman (1561-1626)
> 
> A problem well stated is a problem half solved. -Charles F. Kettering,
> inventor and engineer (1876-1958)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.o
> rg
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to