This strikes me as somewhat counter-productive. Even in this mild climate
(PacNW coastal) we do experience freezing event os long enough duration to
freeze things. Even a slight leak in the control valve to the test header
can fill the header and valves sufficiently between tests that damage could
occur. There's a reason to allow them in the room. What's a good reason to
not?



On Wed, Apr 9, 2014 at 3:01 PM, John Denhardt
<[email protected]>wrote:

> NFPA 20 was modified recently.  It does not allow the header in the room.
> I was told the intent was not to allow the fire hose connection in the room
> under any situation. We used to install the header in the room all the time.
>
> John
>
>
> John August Denhardt, P.E., FSFPE
> Strickland Fire Protection Incorporated
> 5113 Berwyn Road
> College Park, Maryland 20740
> Office Telephone Number:  301-474-1136
> Mobile Telephone Number:  301-343-1457
> FIRE SPRINKLERS SAVE LIVES - Can you live without them?
>
> -----Original Message-----
> From: [email protected] [mailto:
> [email protected]] On Behalf Of
> [email protected]
> Sent: Wednesday, April 09, 2014 5:58 PM
> To: [email protected]
> Subject: Re: pump test header valves
>
> Or, if possible keep headed in the pump room without valves, run hoses out
> to a truck mounted test rack with hose gates on the rack. This way the
> person reading the pitot can adjust the valves,
> Sent from my iPhone3200
> USA Parkway
> McCarran NV 89434
> United States
>
> > On Apr 9, 2014, at 12:49 PM, "John Denhardt" <
> [email protected]> wrote:
> >
> > Funny but true story:
> >
> > I had a client who was worried about security with the test header
> penetrating the exterior of the building.  They had us remove the test
> header after each test and store in the fire pump/mechanical room.  We were
> instructed to install a blind flange using sealant on the bolts so the
> blind flange would not be easily removed.  Well, the client decided to have
> the area cleaned up.  To everyone surprise, when showed up for the annual
> fire pump system test, no test header was in the room.  After the
> investigation, the employee that cleaned the room said he did not know what
> it was but it was big, heavy and had brass valves.  He made the decision to
> throw it away.
> >
> > Amazing - you can not make this stuff up!
> >
> > John
> >
> >
> > John August Denhardt, P.E., FSFPE
> > Strickland Fire Protection Incorporated
> > 5113 Berwyn Road
> > College Park, Maryland 20740
> > Office Telephone Number:  301-474-1136
> > Mobile Telephone Number:  301-343-1457
> > FIRE SPRINKLERS SAVE LIVES - Can you live without them?
> >
> > -----Original Message-----
> > From: [email protected] [mailto:
> [email protected]] On Behalf Of David Autry
> > Sent: Wednesday, April 09, 2014 2:32 PM
> > To: [email protected]
> > Subject: RE: pump test header valves
> >
> > LOL, I was think of one that I did, that had sixteen (16) valves.
> >
> >
> > David Autry
> >
> > Meininger Fire Protection Inc.
> > 2521 W L St. Suite No.4
> > Lincoln, Ne 68522
> > Voice (402) 466-2616
> > Fax (402) 466-2617
> > [email protected]
> >
> > -----Original Message-----
> > From: [email protected]
> > [mailto:[email protected]] On Behalf Of
> > rongreenman .
> > Sent: Wednesday, April 09, 2014 12:43 PM
> > To: [email protected]
> > Subject: Re: pump test header valves
> >
> > Too bad, I was liking the 2 1/2" plastic pipe caps idea a lot. The
> > removing the entire test header is Ok but that has to be at least two and
> > probably three guys on anything bigger that a couple of three valves.
> >
> >
> > On Wed, Apr 9, 2014 at 10:20 AM, Bobby McCullough <
> > [email protected]> wrote:
> >
> >> My mistake.  The 2.5" plastic caps are hose threads & installed on the
> >> valve where only the caps were stolen, which is common.  I only have a
> >> few projects with valves stolen & there we used threaded ductile caps
> >> on the nipples & locked the valves in the pump room.
> >>
> >> -----Original Message-----
> >> From: [email protected]
> >> [mailto:[email protected]] On Behalf Of
> >> Ben Young
> >> Sent: Wednesday, April 09, 2014 12:05 PM
> >> To: [email protected]
> >> Subject: Re: pump test header valves
> >>
> >> Bobby,
> >>
> >> Do you mean screw-on PVC caps, or the plastic break caps for FDC snoots?
> >>
> >> Thanks for the feeback everyone, I didn't realize this was so common.
> >> I'll have to start recommending this to some of our clients in high
> >> theft areas from now on.
> >>
> >>
> >> Benjamin Young
> >>
> >>
> >> On Wed, Apr 9, 2014 at 9:50 AM, Bobby McCullough
> >> <[email protected]
> >>> wrote:
> >>
> >>> We use 2.5" plastic caps.  Not much value at the scrap yard.  Take
> >>> the
> >>
> >>> valves in the pump room and use a bicycle cable & lock to keep them
> >>> from wandering off.
> >>>
> >>> Bobby McCullough
> >>> Atlanta Sprinkler
> >>>
> >>>
> >>> -----Original Message-----
> >>> From: [email protected]
> >>> [mailto:[email protected]] On Behalf Of
> >>> Morey, Mike
> >>> Sent: Wednesday, April 09, 2014 8:49 AM
> >>> To: [email protected]
> >>> Subject: RE: pump test header valves
> >>>
> >>> They make test header outlets with male threaded outlets (basically
> >>> the opposite of an FDC) with hose caps that you remove and then
> >>> screw on hose valves that have a female swivel on the inlet side.
> >>> Of course
> >>
> >>> there's still the risk of someone stealing the hose caps and/or
> >>> brass adapteer fittings that provide the male hose thread, but at
> >>> least the valves aren't sitting out there too.
> >>>
> >>> Mike Morey, CFPS, SET
> >>> Planner Scheduler/Designer
> >>> BMWC Constructors, Inc.
> >>> 1740 W. Michigan St, Indianapolis, IN 46222
> >>> O: 317.651.0596 | C: 317.586.8111
> >>> [email protected] | www.bmwc.com
> >>>
> >>> ________________________________________
> >>> From: [email protected]
> >>> <[email protected]> on behalf of Ben
> >>> Young <[email protected]>
> >>> Sent: Wednesday, April 09, 2014 8:40 AM
> >>> To: [email protected]
> >>> Subject: pump test header valves
> >>>
> >>> Last week I was at an ASCET meeting where a pump presentation was
> >> given.
> >>>
> >>> Someone asked the presenter if it was allowed to remove the test
> >>> header valves and keep them in the pump room to stop them from being
> >> stolen.
> >>>
> >>> The presenter and few other attendees chimed in that this was ok,
> >>> and nothing in 20 or 25 said the valves had to be constantly in place.
> >>>
> >>> I didn't think of it at the time, but now I'm asking myself how then
> >>> do you keep debris out of the test header?  The only thing I can
> >>> think
> >>
> >>> of is that you would have to cap the nipples or if you remove the
> >>> nipples, plug the holes in the test header.  This sounds like it
> >>> will cause problems down the road to me.
> >>>
> >>> Have you guys ever seen this done before?
> >>>
> >>> Benjamin Young
> >>> _______________________________________________
> >>> Sprinklerforum mailing list
> >>> [email protected]
> >>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
> >>> kl
> >>> er
> >>> .org
> >>> _______________________________________________
> >>> Sprinklerforum mailing list
> >>> [email protected]
> >>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
> >>> kl
> >>> er
> >>> .org
> >>> _______________________________________________
> >>> Sprinklerforum mailing list
> >>> [email protected]
> >>>
> >>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
> >>> kl
> >>> er.org
> >> _______________________________________________
> >> Sprinklerforum mailing list
> >> [email protected]
> >> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> >> er
> >> .org
> >> _______________________________________________
> >> Sprinklerforum mailing list
> >> [email protected]
> >>
> >> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> >> er.org
> >
> >
> >
> > --
> > Ron Greenman
> > Instructor
> > Fire Protection Engineering Technology
> > Bates Technical College
> > 1101 So. Yakima Ave.
> > Tacoma, WA 98405
> >
> > [email protected]
> >
> > http://www.bates.ctc.edu/fireprotection/
> >
> > 253.680.7346
> > 253.576.9700 (cell)
> >
> > Member:
> > ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
> >
> > They are happy men whose natures sort with their vocations. -Francis
> > Bacon, essayist, philosopher, and statesman (1561-1626)
> >
> > A problem well stated is a problem half solved. -Charles F. Kettering,
> > inventor and engineer (1876-1958)
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.o
> > rg
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)

A problem well stated is a problem half solved. -Charles F. Kettering,
inventor and engineer (1876-1958)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to