If you added the hose "allowance" to your calcs, then you have included it in 
the available water supply, i.e. if the remote area demand is 200gpm sprinkler 
flow  at 28 psi, and you add 250 gpm hose "allowance" to that and say that your 
total demand (hose and sprinkler) is 450 gpm at 28 psi, then you have INCLUDED 
the hose demand in your residual pressure demand of 28psi. If the available 
water supply curve shows there is more than 28 psi at 450 gpm, then you're good 
to go. Is this how your calculations were done?
Mark at Aero 

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Brian Harris
Sent: Tuesday, November 18, 2014 2:22 PM
To: [email protected]
Subject: RE: Hose added to calc's. no PSI

Craig-
The owner is very skeptical of there being enough water supply without adding a 
tank, we provided calculations for the sprinkler system and now he wants a 
civil engineer to provide fire calc's as well. The civil guy was asking why we 
didn't include any extra psi drop for the outside hose allowance.

Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of [email protected]
Sent: Tuesday, November 18, 2014 4:15 PM
To: [email protected]
Subject: RE: Hose added to calc's. no PSI

Why does he care?

Craig L. Prahl 
Fire Protection Group Lead
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Brian Harris
Sent: Tuesday, November 18, 2014 1:59 PM
To: [email protected]
Subject: Hose added to calc's. no PSI

I've been trying to explain to a civil engineer that we (fire sprinkler) 
include outside hose allowance into our calc's but only for the extra gpm, not 
as far as additional psi goes. I'm sure it's the way I'm trying to explain it 
that's not making any sense to him, can one of you more versed in the English 
language help me out and put it in layman's terms for me?

Brian Harris, CET
BVS Systems Inc.
Sprinkler Division
bvssystemsinc.com<http://bvssystemsinc.com/>
Phone: 704.896.9989
Fax: 704.896.1935

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to