Yes, thank you Steve. I was just trying to get a consensus from the forum on 
does the CBC exception to tamper monitoring apply to a 13D, option one, stand 
alone system? Building details being a 5 unit building served by a 2" service 
with double OS&Y. No domestic water service off this line. 
Thanks for your input. 
Owen

Sent from my iPhone

> On Oct 5, 2015, at 11:09 AM, Steve Leyton <st...@protectiondesign.com> wrote:
> 
> Owen:
> 
> I don't think that I, or anyone else on this forum is going to affirm or
> reject the adequacy of a particular condition based on theoreticals,
> especially when it's being done in the context of an
> after-the-fact-over-the-shoulder inspection, i.e. second guessing.
> Again and finally, my best advice is that if you have a question about
> something like this, ask the AHJ.  You were once one yourself - wouldn't
> you appreciate the opportunity to learn from a past mistake or affirm a
> decision made previously?
> 
> SL
> 
> 
> 
> 
> -----Original Message-----
> From: Sprinklerforum
> [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of
> firs...@aol.com
> Sent: Monday, October 05, 2015 11:05 AM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: Re: Monitoring 13D control valves in California 
> 
> No, it's a stand alone. No domestic service. 
> 
> Sent from my iPhone
> 
>>> On Oct 5, 2015, at 10:57 AM, Steve Leyton <st...@protectiondesign.com>
>> wrote:
>> 
>> Good points, which also beg the question:  Does the 2" meter also feed
>> the domestic water?   If so, you can take the handles off the
>> double-check, or lock them open if they're not already or ... or ... 
>> 
>> Really, if you have questions about that basis of design or want to 
>> play the part of community gadfly, take it to the AHJ.
>> 
>> SL
>> 
>> 
>> 
>> 
>> 
>> -----Original Message-----
>> From: Sprinklerforum
>> [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of 
>> Larry Keeping
>> Sent: Monday, October 05, 2015 10:50 AM
>> To: sprinklerforum@lists.firesprinkler.org
>> Subject: RE: Monitoring 13D control valves in California
>> 
>> If I've read things correctly the only shutoff to the system is at the
> 
>> BFP which serves 5 units.
>> 
>> Since 13D in Section 6.2.3 says that where more than one dwelling unit
> 
>> are served by the same water supply, each unit must have its own 
>> individual control valve, so I am having trouble seeing the set up 
>> described as a 13D system.
>> 
>> It looks like a 13R application to me.
>> 
>> Larry Keeping
>> 
>> -----Original Message-----
>> From: Sprinklerforum
>> [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of 
>> firs...@aol.com
>> Sent: October-05-15 1:44 PM
>> To: sprinklerforum@lists.firesprinkler.org
>> Subject: Re: Monitoring 13D control valves in California
>> 
>> It appears that both the AHJ and contractor  have made mistakes on 
>> this project. I am interested in finding out what exactly happened. We
> 
>> should all play by the same rules. Im trying to figure out what is 
>> correct here according to standard, CFC & CBC. Like I said, it looks 
>> like a 13R but now they're saying its a 13D without DCVA monitoring.
>> 
>> Sent from my iPhone
>> 
>>>> On Oct 5, 2015, at 9:48 AM, Steve Leyton 
>>>> <st...@protectiondesign.com>
>>> wrote:
>>> 
>>> Are you doing a 3rd party inspection or some sort of risk
>> management/loss prevention analysis?  Why not just call the AHJ or 
>> installing contractor and ask for approved basis of design?
>>> 
>>> SL
>>> 
>>> 
>>> -----Original Message-----
>>> From: Sprinklerforum on behalf of firs...@aol.com
>>> Sent: Mon 10/5/2015 9:37 AM
>>> To: sprinklerforum@lists.firesprinkler.org
>>> Subject: Re: Monitoring 13D control valves in California
>>> 
>>> Hi Steve, thanks for responding. Isn't the CBC more restrictive
>> therefore you can't allow something less? This particular system looks
> 
>> like a 13R but they failed to provide electrical for tamper switches. 
>> So now they argue it is a 13D serving a building with 5 townhouse's 
>> separated by 1 hour construction. My thinking is since it is 5 units, 
>> not one or two family dwelling, the exception for electrical
> monitoring
>> does not apply. Therefore tampers are required. Am I correct?   
>>> 
>>> Sent from my iPhone
>>> 
>>>> On Oct 5, 2015, at 8:52 AM, Steve Leyton 
>>>> <st...@protectiondesign.com>
>> wrote:
>>>> 
>>>> It's possible the AHJ has accepted these to be of limited area if 
>>>> the
>> 
>>>> sub-systems serve less than 20 sprinklers.  NFPA offers multiple 
>>>> solutions for "monitoring", including the locking of valves.
> Perhaps
>>>> the AHJ approved an alternative to electronic supervision.   
>>>> 
>>>> Steve L.
>>>> 
>>>> 
>>>> 
>>>> 
>>>> 
>>>> -----Original Message-----
>>>> From: Sprinklerforum
>>>> [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of
> 
>>>> firs...@aol.com
>>>> Sent: Monday, October 05, 2015 7:38 AM
>>>> To: sprinklerforum@lists.firesprinkler.org
>>>> Subject: Monitoring 13D control valves in California
>>>> 
>>>> The California Building Code requires sprinkler control valves to be
> 
>>>> electrically monitored. One of the exceptions is One and Two Family 
>>>> Dwellings, 13D.
>>>> 
>>>> What if it is a stand alone 13D system? (2" water meter with one 
>>>> DCVA
>> 
>>>> to a 2" underground, serving a row of 5 town homes with one hour 
>>>> separations between units. The 2" underground branches off to each
>> unit.
>>>> Each unit has it's own flow switch and test valve).
>>>> 
>>>> The exception specifically states for one and two family dwellings 
>>>> because the control valve is before the domestic service so shutting
> 
>>>> off the sprinklers shuts off the domestic therefor it is self
>> monitoring.
>>>> The stand alone serving 5 units does not have this valve arrangement
> 
>>>> therefore it would require electric monitoring per CBC.
>>>> 
>>>> Am I thinking correctly? According to CBC the two control valves on 
>>>> the DCVA would need tampers, correct?
>>>> 
>>>> Owen Evans
>>>> 
>>>> Sent from my iPad
>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> Sprinklerforum@lists.firesprinkler.org
>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
>>>> k
>>>> ler
>>>> .org
>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> Sprinklerforum@lists.firesprinkler.org
>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
>>>> k
>>>> ler.org
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> Sprinklerforum@lists.firesprinkler.org
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
>>> l
>>> er.org
>>> 
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> Sprinklerforum@lists.firesprinkler.org
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
>>> l
>>> er.org
>> _______________________________________________
>> Sprinklerforum mailing list
>> Sprinklerforum@lists.firesprinkler.org
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>> er
>> .org
>> _______________________________________________
>> Sprinklerforum mailing list
>> Sprinklerforum@lists.firesprinkler.org
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>> er
>> .org
>> _______________________________________________
>> Sprinklerforum mailing list
>> Sprinklerforum@lists.firesprinkler.org
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>> er.org
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
> .org
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org