Sounds like it's outside the scope of a simple 13d system. 13d is a combination 
domestic/fire 1&2 family dwelling not dwellings.

"For I am not ashamed of the gospel, because it is God's power for salvation to 
everyone who believes..." HCS Romans 1:16 
"Therefore having overlooked the times of ignorance, God is now declaring to 
men that all people everywhere should repent,..." NASB Acts 17:30

> On Oct 5, 2015, at 12:44 PM, firs...@aol.com wrote:
> 
> It appears that both the AHJ and contractor  have made mistakes on this 
> project. I am interested in finding out what exactly happened. We should all 
> play by the same rules. Im trying to figure out what is correct here 
> according to standard, CFC & CBC. Like I said, it looks like a 13R but now 
> they're saying its a 13D without DCVA monitoring. 
> 
> Sent from my iPhone
> 
>> On Oct 5, 2015, at 9:48 AM, Steve Leyton <st...@protectiondesign.com> wrote:
>> 
>> Are you doing a 3rd party inspection or some sort of risk management/loss 
>> prevention analysis?  Why not just call the AHJ or installing contractor and 
>> ask for approved basis of design?
>> 
>> SL
>> 
>> 
>> -----Original Message-----
>> From: Sprinklerforum on behalf of firs...@aol.com
>> Sent: Mon 10/5/2015 9:37 AM
>> To: sprinklerforum@lists.firesprinkler.org
>> Subject: Re: Monitoring 13D control valves in California 
>> 
>> Hi Steve, thanks for responding. Isn't the CBC more restrictive therefore 
>> you can't allow something less? This particular system looks like a 13R but 
>> they failed to provide electrical for tamper switches. So now they argue it 
>> is a 13D serving a building with 5 townhouse's separated by 1 hour 
>> construction. My thinking is since it is 5 units, not one or two family 
>> dwelling, the exception for electrical monitoring does not apply. Therefore 
>> tampers are required. Am I correct?   
>> 
>> Sent from my iPhone
>> 
>>> On Oct 5, 2015, at 8:52 AM, Steve Leyton <st...@protectiondesign.com> wrote:
>>> 
>>> It's possible the AHJ has accepted these to be of limited area if the
>>> sub-systems serve less than 20 sprinklers.  NFPA offers multiple
>>> solutions for "monitoring", including the locking of valves.  Perhaps
>>> the AHJ approved an alternative to electronic supervision.   
>>> 
>>> Steve L.
>>> 
>>> 
>>> 
>>> 
>>> 
>>> -----Original Message-----
>>> From: Sprinklerforum
>>> [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of
>>> firs...@aol.com
>>> Sent: Monday, October 05, 2015 7:38 AM
>>> To: sprinklerforum@lists.firesprinkler.org
>>> Subject: Monitoring 13D control valves in California 
>>> 
>>> The California Building Code requires sprinkler control valves to be
>>> electrically monitored. One of the exceptions is One and Two Family
>>> Dwellings, 13D.
>>> 
>>> What if it is a stand alone 13D system? (2" water meter with one DCVA to
>>> a 2" underground, serving a row of 5 town homes with one hour
>>> separations between units. The 2" underground branches off to each unit.
>>> Each unit has it's own flow switch and test valve).
>>> 
>>> The exception specifically states for one and two family dwellings
>>> because the control valve is before the domestic service so shutting off
>>> the sprinklers shuts off the domestic therefor it is self monitoring.
>>> The stand alone serving 5 units does not have this valve arrangement
>>> therefore it would require electric monitoring per CBC.
>>> 
>>> Am I thinking correctly? According to CBC the two control valves on the
>>> DCVA would need tampers, correct? 
>>> 
>>> Owen Evans
>>> 
>>> Sent from my iPad
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> Sprinklerforum@lists.firesprinkler.org
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
>>> .org
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> Sprinklerforum@lists.firesprinkler.org
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> _______________________________________________
>> Sprinklerforum mailing list
>> Sprinklerforum@lists.firesprinkler.org
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> Sprinklerforum@lists.firesprinkler.org
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to