Hi All,

I can't check the forum archives right now because the website isn't loading 
for me for some reason.  Based on NFPA 13 2013.

Can sidewalls be installed when not located next to a wall?

Assuming we meet the all the minimum/maximum spacing requirements, vertical 
distance below the deck requirements, standard spray sprinklers, ordinary 
hazard occupancy, noncombustible construction.  Walking from branchline to 
branchline left to right, can I install upright, upright, sidewall facing 
right, sidewall facing left, upright, upright.  With spacing from upright to 
upright equal to 12ft, spacing from upright to backside of sidewall of 6ft, and 
spacing from sidewall face to sidewall face equal to 20ft.  Is this acceptable?

The first thing most people say is "will the sidewall be next to something like 
a baffle or installed with the pipe in a soffit?"  As of now, no, there is 
nothing behind the sidewalls.  If something is required, please help me find 
the direction in the code for this requirement and design parameters.  Because 
right now all I am finding is a lot of "grey" area that people can interpret 
whichever way suits their needs.  I'm looking for "black and white" if it is in 
there.  If it's only "grey", opinions are greatly appreciated.

Thank you for your time and help!

Thanks,
Sean VG