*coarse. And an 18" deep draft stop is for containing smoke, not to enhance
sprinkler activation, and, I apologise for not knowing how to trim threads
when at home using my phone.
On Dec 22, 2015 4:48 PM, "Brad Casterline" <[email protected]> wrote:

> No better subject to ramble on about than sprinkler activation.
> I think citing sidewalls under an overhead door is misplaced though
> because in that case there is an 'above AND below' setup, and whether the
> door is up or down the fire has to be pretty much right under the 'exposed
> sidewall'. Not so with one compliment.
> If you did the back-to-back sidewalls in the middle of the space I would
> advocate no wall, baffle, or beam, that being based on some primitive,
> course modeling I did several years ago looking at activation times for
> water curtains with and without a draft stop: with seemed to 1) slow the
> velocity of the ceiling jet a tad and 2) block half the pattern-- RTI is
> based on temp AND velocity.
>
> I've been modeling this all afternoon in my mind because I skated a little
> early today-
> I'll actually do it I'm sure, soon, make a youtube movie, and post the
> link to that here-- but, you should resign yourself, re. any real life
> application to using a sideWALL  essentially with a 'wall' :) ;) :)
>
> B-rad
> On Dec 22, 2015 11:54 AM, <[email protected]> wrote:
>
>> Thank you Richard and Brad.
>>
>> These are some of the exact points I was looking at/for.  Up to this
>> point we had only used them under garage doors.  But like Duane brought up,
>> we were wondering if they can be installed under garage doors and be
>> expected to operate, then shouldn't they also be allowed to be installed in
>> "exposed" scenarios.  Maybe this just one of those "calculated risks" by
>> the committee if no other testing has been done.
>>
>> Moving on, so if I follow 8.7.4.1.2.2, and located the deflector
>> accordingly off the "wall".  What are the other defining characteristics of
>> this "wall"?  How deep is it?  How long does it have to be?  As far as I
>> know "wall" isn't defined in Chapter 3.  You may laugh and think I am going
>> too far with this, but one of the major sprinkler manufactures states the
>> following in one of their product listings "Horizontal sidewall sprinklers
>> are designed for installation along a wall or the side of a beam".  Since
>> they are clearly indicating beams are acceptable for proper operation, can
>> I assume "wall" in 8.7.4.1.2.2 doesn't mean it has to run from floor to
>> ceiling.  From this point going forward I can see someone arguing from (6)
>> different routes, some of which could be considered "educated guesses".
>> First (2) should be completely acceptable but not preferred, Next (3) have
>> their pros/cons and varying degrees of applicability, last (1) is the most
>> preferred but probably won't be
>>  accepted.
>>
>> (1) Build a wall.
>> (2) Install a beam.
>> (3) Use the definition of Compartment from 3.3.6.  A sidewall can be
>> installed in a "compartment", so an 8" lintel should be sufficient.  Since
>> the 8" lintel allows a maximum opening of 8ft in the wall, space the heads
>> every 8ft and run the lintel the length of the sidewalls.
>> (4) Use the definition of Draft Curtain from 8.4.6.4.1.  Since this is
>> acceptable to separate sprinklers with different response times, it will
>> clearly delay the heat travel long enough for a sprinkler to operate.  This
>> would require a barrier 2ft deep running the length of the sprinklers.  No
>> apparent restriction on sprinkler spacing.
>> (5) Use the definition of Draft Stop from 8.15.4.2.  Since this is
>> acceptable to delay heat traveling vertically from floor to floor.  This
>> would require a barrier 18in deep with heads spaced 6ft apart.
>> (6) If we decide the wall/beam isn't required to be a heat trap, but
>> rather a protection of spray from other sprinklers.  Use the definition for
>> Baffles with Sidewalls 8.7.3.4.  Baffles are at least 8" long, 6" high, be
>> between 2in and 3in above the deflector, and the bottom be at least even
>> with the deflector.
>>
>> Obviously I would like to choose (6) if acceptable.  However do you see
>> any viability of these (4) "educated guesses"?
>>
>> I appreciate any further input/opinion and of course your time to listen
>> to me ramble on.
>>
>> Thanks,
>> Sean VG
>>
>>
>>
>> -----Original Message-----
>> From: Sprinklerforum [mailto:
>> [email protected]] On Behalf Of Brad
>> Casterline
>> Sent: Tuesday, December 22, 2015 9:58 AM
>> To: [email protected]
>> Subject: RE: can sidewalls be installed when not located next to a wall?
>>
>> Sean, I found this in the archives:
>> *****
>> Can a horizontal sidewall sprinkler be installed in the center of a room
>> (flat, smooth clg) provided sprinkler coverage is added behind the
>> sidewall?  In other words, not installed near a wall or soffit.
>>
>> In reality a sidewall installed 4" to 6" below the ceiling (away from a
>> wall/soffit) should activate in similar fashion as exposed pendents and
>> uprights (1" - 12" below clg).  If code permits "exposed" sidewalls to be
>> installed below roll up doors without soffits, can't an "exposed"
>> sidewall be installed elsewhere?
>>
>> Is there anything in the listing of a sidewall that requires the
>> sprinkler be installed on a wall or soffit?  Are there any ROP/ROC
>> responses from the committee that would help answer the question?
>>
>> Thoughts?
>>
>> Duane Johnson, PE
>> Program Manager
>> Division of the Fire Marshal (Support Contractor) Office of Research
>> Services National Institutes of Health
>> 301-496-0487
>>
>>
>> Duane,
>>
>> NFPA 13(2007) 8.7.4.1.2 addresses the location of vertical and horizontal
>> sidewalls in relation to the wall that they are projected from.
>>
>> Sidewall sprinklers cannot be positioned in the center of a room as a
>> pendant.
>>
>>
>>
>> Dale F. Wingard, SET
>> Design Manager
>> Triple "A" Fire Protection, Inc.
>> 251.649.2034
>> [email protected]
>>
>>
>> ********
>> Brad
>>
>>
>> -----Original Message-----
>> From: Sprinklerforum [mailto:
>> [email protected]]
>> On Behalf Of Richard Carr
>> Sent: Tuesday, December 22, 2015 10:19 AM
>> To: [email protected]
>> Subject: RE: can sidewalls be installed when not located next to a wall?
>>
>> Under overhead doors is only place I know is acceptable without a wall.
>>
>>
>>
>> Sent from my T-Mobile 4G LTE Device
>>
>>
>> -------- Original message --------
>> From: [email protected]
>> Date: 12/22/2015 11:14 AM (GMT-05:00)
>> To: [email protected]
>> Subject: can sidewalls be installed when not located next to a wall?
>>
>> Hi All,
>>
>> I can't check the forum archives right now because the website isn't
>> loading for me for some reason.  Based on NFPA 13 2013.
>>
>> Can sidewalls be installed when not located next to a wall?
>>
>> Assuming we meet the all the minimum/maximum spacing requirements,
>> vertical distance below the deck requirements, standard spray sprinklers,
>> ordinary hazard occupancy, noncombustible construction.  Walking from
>> branchline to branchline left to right, can I install upright, upright,
>> sidewall facing right, sidewall facing left, upright, upright.  With
>> spacing from upright to upright equal to 12ft, spacing from upright to
>> backside of sidewall of 6ft, and spacing from sidewall face to sidewall
>> face equal to 20ft.  Is this acceptable?
>>
>> The first thing most people say is "will the sidewall be next to
>> something like a baffle or installed with the pipe in a soffit?"  As of
>> now, no, there is nothing behind the sidewalls.  If something is required,
>> please help me find the direction in the code for this requirement and
>> design parameters.
>> Because right now all I am finding is a lot of "grey" area that people
>> can interpret whichever way suits their needs.  I'm looking for "black and
>> white" if it is in there.  If it's only "grey", opinions are greatly
>> appreciated.
>>
>> Thank you for your time and help!
>>
>> Thanks,
>> Sean VG
>>
>>
>>
>>
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>>
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>>
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>>
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>>
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to