Sidewall heads without a wall is one thing, but what about sidewalls at the
bottom of elevator shafts that have a wall but no ceiling?



*Success Through Code Compliance*

*Rahe Loftin, PE  *
*Regional Fire Protection Engineer*
*General Services Administration*
*Region 7 - TX, OK, NM, AR, LA*
*Facilities Management & Support 7PMC*
*c - 817-371-3102*
*o - 817-978-7299*

On Wed, Dec 23, 2015 at 7:42 PM, Brad Casterline <[email protected]>
wrote:

> A few more things Sean then I'll be able to sleep-
> 1) you're welcome
> 2) you have put a lot of good thought into this, and thank you for
> prompting the ponderance
> 3) distinct sidewalls back-to-back in the middle of a space without a
> baffle or beam to prevent cold soldering is a no go I realize now, but with
> a baffle or beam the head on the opposite side of the ignition point might
> not activate due to the way the ceiling jet hits the beam, goes under it,
> and comes back up the other side-- the opposite side spinkler, being above
> the bottom and close to the side of the beam leaves it in a "slow and cold
> pocket".
> The best thing would be a Tyco type back to back attic head, (2 sidewalls
> with one element) but they would have to bend both deflectors up to work
> with a flat ceiling :) unless the ceiling height was up there a ways.
> 4) seems like you guys there at Aero are really on the ball!!!-- prime
> candidates for some serious fire modeling.  .  .
>
> wbr, Brad
> On Dec 22, 2015 5:05 PM, "Brad Casterline" <[email protected]> wrote:
>
> > *coarse. And an 18" deep draft stop is for containing smoke, not to
> > enhance sprinkler activation, and, I apologise for not knowing how to
> trim
> > threads when at home using my phone.
> > On Dec 22, 2015 4:48 PM, "Brad Casterline" <[email protected]>
> wrote:
> >
> >> No better subject to ramble on about than sprinkler activation.
> >> I think citing sidewalls under an overhead door is misplaced though
> >> because in that case there is an 'above AND below' setup, and whether
> the
> >> door is up or down the fire has to be pretty much right under the
> 'exposed
> >> sidewall'. Not so with one compliment.
> >> If you did the back-to-back sidewalls in the middle of the space I would
> >> advocate no wall, baffle, or beam, that being based on some primitive,
> >> course modeling I did several years ago looking at activation times for
> >> water curtains with and without a draft stop: with seemed to 1) slow the
> >> velocity of the ceiling jet a tad and 2) block half the pattern-- RTI is
> >> based on temp AND velocity.
> >>
> >> I've been modeling this all afternoon in my mind because I skated a
> >> little early today-
> >> I'll actually do it I'm sure, soon, make a youtube movie, and post the
> >> link to that here-- but, you should resign yourself, re. any real life
> >> application to using a sideWALL  essentially with a 'wall' :) ;) :)
> >>
> >> B-rad
> >> On Dec 22, 2015 11:54 AM, <[email protected]> wrote:
> >>
> >>> Thank you Richard and Brad.
> >>>
> >>> These are some of the exact points I was looking at/for.  Up to this
> >>> point we had only used them under garage doors.  But like Duane
> brought up,
> >>> we were wondering if they can be installed under garage doors and be
> >>> expected to operate, then shouldn't they also be allowed to be
> installed in
> >>> "exposed" scenarios.  Maybe this just one of those "calculated risks"
> by
> >>> the committee if no other testing has been done.
> >>>
> >>> Moving on, so if I follow 8.7.4.1.2.2, and located the deflector
> >>> accordingly off the "wall".  What are the other defining
> characteristics of
> >>> this "wall"?  How deep is it?  How long does it have to be?  As far as
> I
> >>> know "wall" isn't defined in Chapter 3.  You may laugh and think I am
> going
> >>> too far with this, but one of the major sprinkler manufactures states
> the
> >>> following in one of their product listings "Horizontal sidewall
> sprinklers
> >>> are designed for installation along a wall or the side of a beam".
> Since
> >>> they are clearly indicating beams are acceptable for proper operation,
> can
> >>> I assume "wall" in 8.7.4.1.2.2 doesn't mean it has to run from floor to
> >>> ceiling.  From this point going forward I can see someone arguing from
> (6)
> >>> different routes, some of which could be considered "educated guesses".
> >>> First (2) should be completely acceptable but not preferred, Next (3)
> have
> >>> their pros/cons and varying degrees of applicability, last (1) is the
> most
> >>> preferred but probably won't be
> >>>  accepted.
> >>>
> >>> (1) Build a wall.
> >>> (2) Install a beam.
> >>> (3) Use the definition of Compartment from 3.3.6.  A sidewall can be
> >>> installed in a "compartment", so an 8" lintel should be sufficient.
> Since
> >>> the 8" lintel allows a maximum opening of 8ft in the wall, space the
> heads
> >>> every 8ft and run the lintel the length of the sidewalls.
> >>> (4) Use the definition of Draft Curtain from 8.4.6.4.1.  Since this is
> >>> acceptable to separate sprinklers with different response times, it
> will
> >>> clearly delay the heat travel long enough for a sprinkler to operate.
> This
> >>> would require a barrier 2ft deep running the length of the
> sprinklers.  No
> >>> apparent restriction on sprinkler spacing.
> >>> (5) Use the definition of Draft Stop from 8.15.4.2.  Since this is
> >>> acceptable to delay heat traveling vertically from floor to floor.
> This
> >>> would require a barrier 18in deep with heads spaced 6ft apart.
> >>> (6) If we decide the wall/beam isn't required to be a heat trap, but
> >>> rather a protection of spray from other sprinklers.  Use the
> definition for
> >>> Baffles with Sidewalls 8.7.3.4.  Baffles are at least 8" long, 6"
> high, be
> >>> between 2in and 3in above the deflector, and the bottom be at least
> even
> >>> with the deflector.
> >>>
> >>> Obviously I would like to choose (6) if acceptable.  However do you see
> >>> any viability of these (4) "educated guesses"?
> >>>
> >>> I appreciate any further input/opinion and of course your time to
> listen
> >>> to me ramble on.
> >>>
> >>> Thanks,
> >>> Sean VG
> >>>
> >>>
> >>>
> >>> -----Original Message-----
> >>> From: Sprinklerforum [mailto:
> >>> [email protected]] On Behalf Of Brad
> >>> Casterline
> >>> Sent: Tuesday, December 22, 2015 9:58 AM
> >>> To: [email protected]
> >>> Subject: RE: can sidewalls be installed when not located next to a
> wall?
> >>>
> >>> Sean, I found this in the archives:
> >>> *****
> >>> Can a horizontal sidewall sprinkler be installed in the center of a
> room
> >>> (flat, smooth clg) provided sprinkler coverage is added behind the
> >>> sidewall?  In other words, not installed near a wall or soffit.
> >>>
> >>> In reality a sidewall installed 4" to 6" below the ceiling (away from a
> >>> wall/soffit) should activate in similar fashion as exposed pendents and
> >>> uprights (1" - 12" below clg).  If code permits "exposed" sidewalls to
> be
> >>> installed below roll up doors without soffits, can't an "exposed"
> >>> sidewall be installed elsewhere?
> >>>
> >>> Is there anything in the listing of a sidewall that requires the
> >>> sprinkler be installed on a wall or soffit?  Are there any ROP/ROC
> >>> responses from the committee that would help answer the question?
> >>>
> >>> Thoughts?
> >>>
> >>> Duane Johnson, PE
> >>> Program Manager
> >>> Division of the Fire Marshal (Support Contractor) Office of Research
> >>> Services National Institutes of Health
> >>> 301-496-0487
> >>>
> >>>
> >>> Duane,
> >>>
> >>> NFPA 13(2007) 8.7.4.1.2 addresses the location of vertical and
> >>> horizontal sidewalls in relation to the wall that they are projected
> from.
> >>>
> >>> Sidewall sprinklers cannot be positioned in the center of a room as a
> >>> pendant.
> >>>
> >>>
> >>>
> >>> Dale F. Wingard, SET
> >>> Design Manager
> >>> Triple "A" Fire Protection, Inc.
> >>> 251.649.2034
> >>> [email protected]
> >>>
> >>>
> >>> ********
> >>> Brad
> >>>
> >>>
> >>> -----Original Message-----
> >>> From: Sprinklerforum [mailto:
> >>> [email protected]]
> >>> On Behalf Of Richard Carr
> >>> Sent: Tuesday, December 22, 2015 10:19 AM
> >>> To: [email protected]
> >>> Subject: RE: can sidewalls be installed when not located next to a
> wall?
> >>>
> >>> Under overhead doors is only place I know is acceptable without a wall.
> >>>
> >>>
> >>>
> >>> Sent from my T-Mobile 4G LTE Device
> >>>
> >>>
> >>> -------- Original message --------
> >>> From: [email protected]
> >>> Date: 12/22/2015 11:14 AM (GMT-05:00)
> >>> To: [email protected]
> >>> Subject: can sidewalls be installed when not located next to a wall?
> >>>
> >>> Hi All,
> >>>
> >>> I can't check the forum archives right now because the website isn't
> >>> loading for me for some reason.  Based on NFPA 13 2013.
> >>>
> >>> Can sidewalls be installed when not located next to a wall?
> >>>
> >>> Assuming we meet the all the minimum/maximum spacing requirements,
> >>> vertical distance below the deck requirements, standard spray
> sprinklers,
> >>> ordinary hazard occupancy, noncombustible construction.  Walking from
> >>> branchline to branchline left to right, can I install upright, upright,
> >>> sidewall facing right, sidewall facing left, upright, upright.  With
> >>> spacing from upright to upright equal to 12ft, spacing from upright to
> >>> backside of sidewall of 6ft, and spacing from sidewall face to sidewall
> >>> face equal to 20ft.  Is this acceptable?
> >>>
> >>> The first thing most people say is "will the sidewall be next to
> >>> something like a baffle or installed with the pipe in a soffit?"  As of
> >>> now, no, there is nothing behind the sidewalls.  If something is
> required,
> >>> please help me find the direction in the code for this requirement and
> >>> design parameters.
> >>> Because right now all I am finding is a lot of "grey" area that people
> >>> can interpret whichever way suits their needs.  I'm looking for "black
> and
> >>> white" if it is in there.  If it's only "grey", opinions are greatly
> >>> appreciated.
> >>>
> >>> Thank you for your time and help!
> >>>
> >>> Thanks,
> >>> Sean VG
> >>>
> >>>
> >>>
> >>>
> >>>
> >>> _______________________________________________
> >>> Sprinklerforum mailing list
> >>> [email protected]
> >>>
> >>>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >>> _______________________________________________
> >>> Sprinklerforum mailing list
> >>> [email protected]
> >>>
> >>>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >>>
> >>> _______________________________________________
> >>> Sprinklerforum mailing list
> >>> [email protected]
> >>>
> >>>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >>> _______________________________________________
> >>> Sprinklerforum mailing list
> >>> [email protected]
> >>>
> >>>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >>>
> >>
> _______________________________________________
> Sprinklerforum mailing list