Look in 13/2013 8.15.5.1. Specifically says to use a sidewall in an
elevator pit. Commentary in the Handbook (p. 397) discusses the
justification(s).

On Fri, Dec 25, 2015 at 3:30 PM, Rahe Loftin - 7PMC <[email protected]>
wrote:

> Charles,
> True if the elevator car is within 12 inches of the head but, of course,
> not when it is any other position. Furthermore, what about the listing of
> the sidewall head for a flat, horizontal, smooth ceiling?  This certainly
> does not describe the bottom of an elevator car.
>
>
>
> *Success Through Code Compliance*
>
> *Rahe Loftin, PE  *
> *Regional Fire Protection Engineer*
> *General Services Administration*
> *Region 7 - TX, OK, NM, AR, LA*
> *Facilities Management & Support 7PMC*
> *c - 817-371-3102*
> *o - 817-978-7299*
>
> On Fri, Dec 25, 2015 at 7:37 AM, Charles Thurston <[email protected]>
> wrote:
>
> > Hello Rahe,
> >
> > Works good when the car is at the bottom of the shaft.
> >
> > Friday, December 25, 2015, 7:11:21 AM, you wrote:
> >
> > > Sidewall heads without a wall is one thing, but what about sidewalls at
> > the
> > > bottom of elevator shafts that have a wall but no ceiling?
> >
> >
> >
> > > *Success Through Code Compliance*
> >
> > > *Rahe Loftin, PE  *
> > > *Regional Fire Protection Engineer*
> > > *General Services Administration*
> > > *Region 7 - TX, OK, NM, AR, LA*
> > > *Facilities Management & Support 7PMC*
> > > *c - 817-371-3102*
> > > *o - 817-978-7299*
> >
> > > On Wed, Dec 23, 2015 at 7:42 PM, Brad Casterline <
> [email protected]
> > >
> > > wrote:
> >
> > >> A few more things Sean then I'll be able to sleep-
> > >> 1) you're welcome
> > >> 2) you have put a lot of good thought into this, and thank you for
> > >> prompting the ponderance
> > >> 3) distinct sidewalls back-to-back in the middle of a space without a
> > >> baffle or beam to prevent cold soldering is a no go I realize now, but
> > with
> > >> a baffle or beam the head on the opposite side of the ignition point
> > might
> > >> not activate due to the way the ceiling jet hits the beam, goes under
> > it,
> > >> and comes back up the other side-- the opposite side spinkler, being
> > above
> > >> the bottom and close to the side of the beam leaves it in a "slow and
> > cold
> > >> pocket".
> > >> The best thing would be a Tyco type back to back attic head, (2
> > sidewalls
> > >> with one element) but they would have to bend both deflectors up to
> work
> > >> with a flat ceiling :) unless the ceiling height was up there a ways.
> > >> 4) seems like you guys there at Aero are really on the ball!!!-- prime
> > >> candidates for some serious fire modeling.  .  .
> >
> > >> wbr, Brad
> > >> On Dec 22, 2015 5:05 PM, "Brad Casterline" <[email protected]>
> > wrote:
> >
> > >> > *coarse. And an 18" deep draft stop is for containing smoke, not to
> > >> > enhance sprinkler activation, and, I apologise for not knowing how
> to
> > >> trim
> > >> > threads when at home using my phone.
> > >> > On Dec 22, 2015 4:48 PM, "Brad Casterline" <[email protected]>
> > >> wrote:
> > >> >
> > >> >> No better subject to ramble on about than sprinkler activation.
> > >> >> I think citing sidewalls under an overhead door is misplaced though
> > >> >> because in that case there is an 'above AND below' setup, and
> whether
> > >> the
> > >> >> door is up or down the fire has to be pretty much right under the
> > >> 'exposed
> > >> >> sidewall'. Not so with one compliment.
> > >> >> If you did the back-to-back sidewalls in the middle of the space I
> > would
> > >> >> advocate no wall, baffle, or beam, that being based on some
> > primitive,
> > >> >> course modeling I did several years ago looking at activation times
> > for
> > >> >> water curtains with and without a draft stop: with seemed to 1)
> slow
> > the
> > >> >> velocity of the ceiling jet a tad and 2) block half the pattern--
> > RTI is
> > >> >> based on temp AND velocity.
> > >> >>
> > >> >> I've been modeling this all afternoon in my mind because I skated a
> > >> >> little early today-
> > >> >> I'll actually do it I'm sure, soon, make a youtube movie, and post
> > the
> > >> >> link to that here-- but, you should resign yourself, re. any real
> > life
> > >> >> application to using a sideWALL  essentially with a 'wall' :) ;) :)
> > >> >>
> > >> >> B-rad
> > >> >> On Dec 22, 2015 11:54 AM, <[email protected]> wrote:
> > >> >>
> > >> >>> Thank you Richard and Brad.
> > >> >>>
> > >> >>> These are some of the exact points I was looking at/for.  Up to
> this
> > >> >>> point we had only used them under garage doors.  But like Duane
> > >> brought up,
> > >> >>> we were wondering if they can be installed under garage doors and
> be
> > >> >>> expected to operate, then shouldn't they also be allowed to be
> > >> installed in
> > >> >>> "exposed" scenarios.  Maybe this just one of those "calculated
> > risks"
> > >> by
> > >> >>> the committee if no other testing has been done.
> > >> >>>
> > >> >>> Moving on, so if I follow 8.7.4.1.2.2, and located the deflector
> > >> >>> accordingly off the "wall".  What are the other defining
> > >> characteristics of
> > >> >>> this "wall"?  How deep is it?  How long does it have to be?  As
> far
> > as
> > >> I
> > >> >>> know "wall" isn't defined in Chapter 3.  You may laugh and think I
> > am
> > >> going
> > >> >>> too far with this, but one of the major sprinkler manufactures
> > states
> > >> the
> > >> >>> following in one of their product listings "Horizontal sidewall
> > >> sprinklers
> > >> >>> are designed for installation along a wall or the side of a beam".
> > >> Since
> > >> >>> they are clearly indicating beams are acceptable for proper
> > operation,
> > >> can
> > >> >>> I assume "wall" in 8.7.4.1.2.2 doesn't mean it has to run from
> > floor to
> > >> >>> ceiling.  From this point going forward I can see someone arguing
> > from
> > >> (6)
> > >> >>> different routes, some of which could be considered "educated
> > guesses".
> > >> >>> First (2) should be completely acceptable but not preferred, Next
> > (3)
> > >> have
> > >> >>> their pros/cons and varying degrees of applicability, last (1) is
> > the
> > >> most
> > >> >>> preferred but probably won't be
> > >> >>>  accepted.
> > >> >>>
> > >> >>> (1) Build a wall.
> > >> >>> (2) Install a beam.
> > >> >>> (3) Use the definition of Compartment from 3.3.6.  A sidewall can
> be
> > >> >>> installed in a "compartment", so an 8" lintel should be
> sufficient.
> > >> Since
> > >> >>> the 8" lintel allows a maximum opening of 8ft in the wall, space
> the
> > >> heads
> > >> >>> every 8ft and run the lintel the length of the sidewalls.
> > >> >>> (4) Use the definition of Draft Curtain from 8.4.6.4.1.  Since
> this
> > is
> > >> >>> acceptable to separate sprinklers with different response times,
> it
> > >> will
> > >> >>> clearly delay the heat travel long enough for a sprinkler to
> > operate.
> > >> This
> > >> >>> would require a barrier 2ft deep running the length of the
> > >> sprinklers.  No
> > >> >>> apparent restriction on sprinkler spacing.
> > >> >>> (5) Use the definition of Draft Stop from 8.15.4.2.  Since this is
> > >> >>> acceptable to delay heat traveling vertically from floor to floor.
> > >> This
> > >> >>> would require a barrier 18in deep with heads spaced 6ft apart.
> > >> >>> (6) If we decide the wall/beam isn't required to be a heat trap,
> but
> > >> >>> rather a protection of spray from other sprinklers.  Use the
> > >> definition for
> > >> >>> Baffles with Sidewalls 8.7.3.4.  Baffles are at least 8" long, 6"
> > >> high, be
> > >> >>> between 2in and 3in above the deflector, and the bottom be at
> least
> > >> even
> > >> >>> with the deflector.
> > >> >>>
> > >> >>> Obviously I would like to choose (6) if acceptable.  However do
> you
> > see
> > >> >>> any viability of these (4) "educated guesses"?
> > >> >>>
> > >> >>> I appreciate any further input/opinion and of course your time to
> > >> listen
> > >> >>> to me ramble on.
> > >> >>>
> > >> >>> Thanks,
> > >> >>> Sean VG
> > >> >>>
> > >> >>>
> > >> >>>
> > >> >>> -----Original Message-----
> > >> >>> From: Sprinklerforum [mailto:
> > >> >>> [email protected]] On Behalf Of Brad
> > >> >>> Casterline
> > >> >>> Sent: Tuesday, December 22, 2015 9:58 AM
> > >> >>> To: [email protected]
> > >> >>> Subject: RE: can sidewalls be installed when not located next to a
> > >> wall?
> > >> >>>
> > >> >>> Sean, I found this in the archives:
> > >> >>> *****
> > >> >>> Can a horizontal sidewall sprinkler be installed in the center of
> a
> > >> room
> > >> >>> (flat, smooth clg) provided sprinkler coverage is added behind the
> > >> >>> sidewall?  In other words, not installed near a wall or soffit.
> > >> >>>
> > >> >>> In reality a sidewall installed 4" to 6" below the ceiling (away
> > from a
> > >> >>> wall/soffit) should activate in similar fashion as exposed
> pendents
> > and
> > >> >>> uprights (1" - 12" below clg).  If code permits "exposed"
> sidewalls
> > to
> > >> be
> > >> >>> installed below roll up doors without soffits, can't an "exposed"
> > >> >>> sidewall be installed elsewhere?
> > >> >>>
> > >> >>> Is there anything in the listing of a sidewall that requires the
> > >> >>> sprinkler be installed on a wall or soffit?  Are there any ROP/ROC
> > >> >>> responses from the committee that would help answer the question?
> > >> >>>
> > >> >>> Thoughts?
> > >> >>>
> > >> >>> Duane Johnson, PE
> > >> >>> Program Manager
> > >> >>> Division of the Fire Marshal (Support Contractor) Office of
> Research
> > >> >>> Services National Institutes of Health
> > >> >>> 301-496-0487
> > >> >>>
> > >> >>>
> > >> >>> Duane,
> > >> >>>
> > >> >>> NFPA 13(2007) 8.7.4.1.2 addresses the location of vertical and
> > >> >>> horizontal sidewalls in relation to the wall that they are
> projected
> > >> from.
> > >> >>>
> > >> >>> Sidewall sprinklers cannot be positioned in the center of a room
> as
> > a
> > >> >>> pendant.
> > >> >>>
> > >> >>>
> > >> >>>
> > >> >>> Dale F. Wingard, SET
> > >> >>> Design Manager
> > >> >>> Triple "A" Fire Protection, Inc.
> > >> >>> 251.649.2034
> > >> >>> [email protected]
> > >> >>>
> > >> >>>
> > >> >>> ********
> > >> >>> Brad
> > >> >>>
> > >> >>>
> > >> >>> -----Original Message-----
> > >> >>> From: Sprinklerforum [mailto:
> > >> >>> [email protected]]
> > >> >>> On Behalf Of Richard Carr
> > >> >>> Sent: Tuesday, December 22, 2015 10:19 AM
> > >> >>> To: [email protected]
> > >> >>> Subject: RE: can sidewalls be installed when not located next to a
> > >> wall?
> > >> >>>
> > >> >>> Under overhead doors is only place I know is acceptable without a
> > wall.
> > >> >>>
> > >> >>>
> > >> >>>
> > >> >>> Sent from my T-Mobile 4G LTE Device
> > >> >>>
> > >> >>>
> > >> >>> -------- Original message --------
> > >> >>> From: [email protected]
> > >> >>> Date: 12/22/2015 11:14 AM (GMT-05:00)
> > >> >>> To: [email protected]
> > >> >>> Subject: can sidewalls be installed when not located next to a
> wall?
> > >> >>>
> > >> >>> Hi All,
> > >> >>>
> > >> >>> I can't check the forum archives right now because the website
> isn't
> > >> >>> loading for me for some reason.  Based on NFPA 13 2013.
> > >> >>>
> > >> >>> Can sidewalls be installed when not located next to a wall?
> > >> >>>
> > >> >>> Assuming we meet the all the minimum/maximum spacing requirements,
> > >> >>> vertical distance below the deck requirements, standard spray
> > >> sprinklers,
> > >> >>> ordinary hazard occupancy, noncombustible construction.  Walking
> > from
> > >> >>> branchline to branchline left to right, can I install upright,
> > upright,
> > >> >>> sidewall facing right, sidewall facing left, upright, upright.
> With
> > >> >>> spacing from upright to upright equal to 12ft, spacing from
> upright
> > to
> > >> >>> backside of sidewall of 6ft, and spacing from sidewall face to
> > sidewall
> > >> >>> face equal to 20ft.  Is this acceptable?
> > >> >>>
> > >> >>> The first thing most people say is "will the sidewall be next to
> > >> >>> something like a baffle or installed with the pipe in a soffit?"
> > As of
> > >> >>> now, no, there is nothing behind the sidewalls.  If something is
> > >> required,
> > >> >>> please help me find the direction in the code for this requirement
> > and
> > >> >>> design parameters.
> > >> >>> Because right now all I am finding is a lot of "grey" area that
> > people
> > >> >>> can interpret whichever way suits their needs.  I'm looking for
> > "black
> > >> and
> > >> >>> white" if it is in there.  If it's only "grey", opinions are
> greatly
> > >> >>> appreciated.
> > >> >>>
> > >> >>> Thank you for your time and help!
> > >> >>>
> > >> >>> Thanks,
> > >> >>> Sean VG
> > >> >>>
> > >> >>>
> > >> >>>
> > >> >>>
> > >> >>>
> > >> >>> _______________________________________________
> > >> >>> Sprinklerforum mailing list
> > >> >>> [email protected]
> > >> >>>
> > >> >>>
> > >>
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> > >> >>> _______________________________________________
> > >> >>> Sprinklerforum mailing list
> > >> >>> [email protected]
> > >> >>>
> > >> >>>
> > >>
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> > >> >>>
> > >> >>> _______________________________________________
> > >> >>> Sprinklerforum mailing list
> > >> >>> [email protected]
> > >> >>>
> > >> >>>
> > >>
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> > >> >>> _______________________________________________
> > >> >>> Sprinklerforum mailing list
> > >> >>> [email protected]
> > >> >>>
> > >> >>>
> > >>
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> > >> >>>
> > >> >>
> > >> _______________________________________________
> > >> Sprinklerforum mailing list
> > >> [email protected]
> >
> > >>
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >
> > > _______________________________________________
> > > Sprinklerforum mailing list
> > > [email protected]
> > >
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >
> >
> >
> > --
> > Best regards,
> >  Charles                            mailto:[email protected]
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)

A problem well stated is a problem half solved. -Charles F. Kettering,
inventor and engineer (1876-1958)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to