Thank you Richard and Brad.

These are some of the exact points I was looking at/for.  Up to this point we 
had only used them under garage doors.  But like Duane brought up, we were 
wondering if they can be installed under garage doors and be expected to 
operate, then shouldn't they also be allowed to be installed in "exposed" 
scenarios.  Maybe this just one of those "calculated risks" by the committee if 
no other testing has been done.

Moving on, so if I follow 8.7.4.1.2.2, and located the deflector accordingly 
off the "wall".  What are the other defining characteristics of this "wall"?  
How deep is it?  How long does it have to be?  As far as I know "wall" isn't 
defined in Chapter 3.  You may laugh and think I am going too far with this, 
but one of the major sprinkler manufactures states the following in one of 
their product listings "Horizontal sidewall sprinklers are designed for 
installation along a wall or the side of a beam".  Since they are clearly 
indicating beams are acceptable for proper operation, can I assume "wall" in 
8.7.4.1.2.2 doesn't mean it has to run from floor to ceiling.  From this point 
going forward I can see someone arguing from (6) different routes, some of 
which could be considered "educated guesses".  First (2) should be completely 
acceptable but not preferred, Next (3) have their pros/cons and varying degrees 
of applicability, last (1) is the most preferred but probably won't be 
 accepted.

(1) Build a wall.
(2) Install a beam.
(3) Use the definition of Compartment from 3.3.6.  A sidewall can be installed 
in a "compartment", so an 8" lintel should be sufficient.  Since the 8" lintel 
allows a maximum opening of 8ft in the wall, space the heads every 8ft and run 
the lintel the length of the sidewalls.
(4) Use the definition of Draft Curtain from 8.4.6.4.1.  Since this is 
acceptable to separate sprinklers with different response times, it will 
clearly delay the heat travel long enough for a sprinkler to operate.  This 
would require a barrier 2ft deep running the length of the sprinklers.  No 
apparent restriction on sprinkler spacing.
(5) Use the definition of Draft Stop from 8.15.4.2.  Since this is acceptable 
to delay heat traveling vertically from floor to floor.  This would require a 
barrier 18in deep with heads spaced 6ft apart.
(6) If we decide the wall/beam isn't required to be a heat trap, but rather a 
protection of spray from other sprinklers.  Use the definition for Baffles with 
Sidewalls 8.7.3.4.  Baffles are at least 8" long, 6" high, be between 2in and 
3in above the deflector, and the bottom be at least even with the deflector.

Obviously I would like to choose (6) if acceptable.  However do you see any 
viability of these (4) "educated guesses"?

I appreciate any further input/opinion and of course your time to listen to me 
ramble on.

Thanks,
Sean VG



-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Brad Casterline
Sent: Tuesday, December 22, 2015 9:58 AM
To: [email protected]
Subject: RE: can sidewalls be installed when not located next to a wall?

Sean, I found this in the archives:
*****
Can a horizontal sidewall sprinkler be installed in the center of a room (flat, 
smooth clg) provided sprinkler coverage is added behind the sidewall?  In other 
words, not installed near a wall or soffit.

In reality a sidewall installed 4" to 6" below the ceiling (away from a
wall/soffit) should activate in similar fashion as exposed pendents and 
uprights (1" - 12" below clg).  If code permits "exposed" sidewalls to be 
installed below roll up doors without soffits, can't an "exposed"
sidewall be installed elsewhere?

Is there anything in the listing of a sidewall that requires the sprinkler be 
installed on a wall or soffit?  Are there any ROP/ROC responses from the 
committee that would help answer the question?

Thoughts?

Duane Johnson, PE
Program Manager
Division of the Fire Marshal (Support Contractor) Office of Research Services 
National Institutes of Health
301-496-0487


Duane,

NFPA 13(2007) 8.7.4.1.2 addresses the location of vertical and horizontal 
sidewalls in relation to the wall that they are projected from.

Sidewall sprinklers cannot be positioned in the center of a room as a pendant.



Dale F. Wingard, SET
Design Manager
Triple "A" Fire Protection, Inc.
251.649.2034
[email protected]


********
Brad


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Richard Carr
Sent: Tuesday, December 22, 2015 10:19 AM
To: [email protected]
Subject: RE: can sidewalls be installed when not located next to a wall?

Under overhead doors is only place I know is acceptable without a wall.



Sent from my T-Mobile 4G LTE Device


-------- Original message --------
From: [email protected]
Date: 12/22/2015 11:14 AM (GMT-05:00)
To: [email protected]
Subject: can sidewalls be installed when not located next to a wall?

Hi All,

I can't check the forum archives right now because the website isn't loading 
for me for some reason.  Based on NFPA 13 2013.

Can sidewalls be installed when not located next to a wall?

Assuming we meet the all the minimum/maximum spacing requirements, vertical 
distance below the deck requirements, standard spray sprinklers, ordinary 
hazard occupancy, noncombustible construction.  Walking from branchline to 
branchline left to right, can I install upright, upright, sidewall facing 
right, sidewall facing left, upright, upright.  With spacing from upright to 
upright equal to 12ft, spacing from upright to backside of sidewall of 6ft, and 
spacing from sidewall face to sidewall face equal to 20ft.  Is this acceptable?

The first thing most people say is "will the sidewall be next to something like 
a baffle or installed with the pipe in a soffit?"  As of now, no, there is 
nothing behind the sidewalls.  If something is required, please help me find 
the direction in the code for this requirement and design parameters.
Because right now all I am finding is a lot of "grey" area that people can 
interpret whichever way suits their needs.  I'm looking for "black and white" 
if it is in there.  If it's only "grey", opinions are greatly appreciated.

Thank you for your time and help!

Thanks,
Sean VG





_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to