Don't forget Reliable they have had 16 foot spacing on their KFR-CCS head for a while now
Sent from my iPhone > On Feb 12, 2016, at 11:47 AM, Travis Mack, SET <[email protected]> wrote: > > Concealed combustible space less than 36" deep with slope less than 2:12. > Therefore, specially listed sprinklers are required per 8.15.1.6. Then, you > go to the datasheet and draft curtains required. > > That requirement has been in the standard since 2002. It was further > clarified in the 2007 edition. I don't think it has changed since 2007. The > CC3 sprinklers are relatively new to get the 16' spacing. Used to be max 12' > spacing 144 sq ft with the Viking COIN and Tyco CC1/CC2. > > Travis Mack, SET > MFP Design, LLC > 2508 E Lodgepole Drive > Gilbert, AZ 85298 > 480-505-9271 > fax: 866-430-6107 > email:[email protected] > > http://www.mfpdesign.com > https://www.facebook.com/pages/MFP-Design-LLC/92218417692 > Send large files to us via: https://www.hightail.com/u/MFPDesign > >> On 2/12/2016 9:40 AM, Brad Casterline wrote: >> Good advice Travis, I'll try to start thinking for myself. >> >> Why CC sprinklers though if this is your case? >> >> Brad >>> On Feb 12, 2016 10:32 AM, "Travis Mack, SET" <[email protected]> wrote: >>> >>> Think outside your bubble. Tyco CC3...16' max spacing...5.6k sprinkler... >>> >>> Things are constantly evolving in this industry. You have to stay on the >>> edge to always keep up to date on available products. It can be a full >>> time job just doing that. >>> >>> Travis Mack, SET >>> MFP Design, LLC >>> 2508 E Lodgepole Drive >>> Gilbert, AZ 85298 >>> 480-505-9271 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org