Don't forget Reliable they have had 16 foot spacing on their KFR-CCS head for a 
while now 

Sent from my iPhone

> On Feb 12, 2016, at 11:47 AM, Travis Mack, SET <[email protected]> wrote:
> 
> Concealed combustible space less than 36" deep with slope less than 2:12.  
> Therefore, specially listed sprinklers are required per 8.15.1.6.  Then, you 
> go to the datasheet and draft curtains required.
> 
> That requirement has been in the standard since 2002.  It was further 
> clarified in the 2007 edition.  I don't think it has changed since 2007.  The 
> CC3 sprinklers are relatively new to get the 16' spacing.  Used to be max 12' 
> spacing 144 sq ft with the Viking COIN and Tyco CC1/CC2.
> 
> Travis Mack, SET
> MFP Design, LLC
> 2508 E Lodgepole Drive
> Gilbert, AZ 85298
> 480-505-9271
> fax: 866-430-6107
> email:[email protected]
> 
> http://www.mfpdesign.com
> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
> Send large files to us via: https://www.hightail.com/u/MFPDesign
> 
>> On 2/12/2016 9:40 AM, Brad Casterline wrote:
>> Good advice Travis, I'll try to start thinking for myself.
>> 
>> Why CC sprinklers though if this is your case?
>> 
>> Brad
>>> On Feb 12, 2016 10:32 AM, "Travis Mack, SET" <[email protected]> wrote:
>>> 
>>> Think outside your bubble.  Tyco CC3...16' max spacing...5.6k sprinkler...
>>> 
>>> Things are constantly evolving in this industry.  You have to stay on the
>>> edge to always keep up to date on available products.  It can be a full
>>> time job just doing that.
>>> 
>>> Travis Mack, SET
>>> MFP Design, LLC
>>> 2508 E Lodgepole Drive
>>> Gilbert, AZ 85298
>>> 480-505-9271
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to