Ok, thanks.

It would be interesting to find out what Tyco used during the U.L. listing!
The last I downloaded was for attic heads (very interesting stuff) but that
was several years ago, and I looked for it again a few years ago but it had
become too proprietary if I remember right.
On Feb 12, 2016 10:47 AM, "Travis Mack, SET" <[email protected]> wrote:

> Concealed combustible space less than 36" deep with slope less than 2:12.
> Therefore, specially listed sprinklers are required per 8.15.1.6.  Then,
> you go to the datasheet and draft curtains required.
>
> That requirement has been in the standard since 2002.  It was further
> clarified in the 2007 edition.  I don't think it has changed since 2007.
> The CC3 sprinklers are relatively new to get the 16' spacing.  Used to be
> max 12' spacing 144 sq ft with the Viking COIN and Tyco CC1/CC2.
>
> Travis Mack, SET
> MFP Design, LLC
> 2508 E Lodgepole Drive
> Gilbert, AZ 85298
> 480-505-9271
> fax: 866-430-6107
> email:[email protected]
>
> http://www.mfpdesign.com
> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
> Send large files to us via: https://www.hightail.com/u/MFPDesign
>
> On 2/12/2016 9:40 AM, Brad Casterline wrote:
>
>> Good advice Travis, I'll try to start thinking for myself.
>>
>> Why CC sprinklers though if this is your case?
>>
>> Brad
>> On Feb 12, 2016 10:32 AM, "Travis Mack, SET" <[email protected]> wrote:
>>
>> Think outside your bubble.  Tyco CC3...16' max spacing...5.6k sprinkler...
>>>
>>> Things are constantly evolving in this industry.  You have to stay on the
>>> edge to always keep up to date on available products.  It can be a full
>>> time job just doing that.
>>>
>>> Travis Mack, SET
>>> MFP Design, LLC
>>> 2508 E Lodgepole Drive
>>> Gilbert, AZ 85298
>>> 480-505-9271
>>> fax: 866-430-6107
>>> email:[email protected]
>>>
>>> http://www.mfpdesign.com
>>> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
>>> Send large files to us via: https://www.hightail.com/u/MFPDesign
>>>
>>> On 2/12/2016 9:28 AM, Brad Casterline wrote:
>>>
>>> I'm thinking very quick activation time, 10 x 10 max, min 10 psi on a 2.8
>>>> K, in a small volume--- I get visions not unlike what I imagine high
>>>> efficiency water mist systems might look like--
>>>> But I am not the mnf rep, pe, t.c. member or ahj--
>>>>
>>>> B
>>>> On Feb 12, 2016 10:16 AM, "Travis Mack, SET" <[email protected]>
>>>> wrote:
>>>>
>>>> The max application for CC3 is 60".  However, it is not the height. It
>>>> is
>>>>
>>>>> the sheer number of them that are needed.  Don't think single building.
>>>>> Think apartment complex...multiple buildings / multiple floors.
>>>>>
>>>>> Travis Mack, SET
>>>>> MFP Design, LLC
>>>>> 2508 E Lodgepole Drive
>>>>> Gilbert, AZ 85298
>>>>> 480-505-9271
>>>>> fax: 866-430-6107
>>>>> email:[email protected]
>>>>>
>>>>> http://www.mfpdesign.com
>>>>> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
>>>>> Send large files to us via: https://www.hightail.com/u/MFPDesign
>>>>>
>>>>> On 2/12/2016 8:57 AM, Brad Casterline wrote:
>>>>>
>>>>> For crying out loud though, isn't the max 'ceiling height' for this
>>>>>
>>>>>> application THREE FEET?
>>>>>> On Feb 12, 2016 9:54 AM, "Travis Mack, SET" <[email protected]>
>>>>>> wrote:
>>>>>>
>>>>>> You and I are on the same page.  We were just hoping to get a
>>>>>> definitive
>>>>>>
>>>>>> answer from the manufacturer.
>>>>>>>
>>>>>>> Travis Mack, SET
>>>>>>> MFP Design, LLC
>>>>>>> 2508 E Lodgepole Drive
>>>>>>> Gilbert, AZ 85298
>>>>>>> 480-505-9271
>>>>>>> fax: 866-430-6107
>>>>>>> email:[email protected]
>>>>>>>
>>>>>>> http://www.mfpdesign.com
>>>>>>> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
>>>>>>> Send large files to us via: https://www.hightail.com/u/MFPDesign
>>>>>>>
>>>>>>> On 2/12/2016 8:53 AM, Ed Kramer wrote:
>>>>>>>
>>>>>>> The AHJ is going to have to make the final call.  My pay scale isn't
>>>>>>> high
>>>>>>>
>>>>>>> enough to make those types decisions, but if it were,  I'd say no.
>>>>>>>> If
>>>>>>>> water
>>>>>>>> spray from the 1st sprinkler or 2 damages the insulation to allow
>>>>>>>> heat
>>>>>>>> to
>>>>>>>> flow past it, you've lost your heat barrier and the 1000 sf design
>>>>>>>> area
>>>>>>>> is
>>>>>>>> out-the-window.
>>>>>>>>
>>>>>>>> Back to my regularly scheduled program.
>>>>>>>>
>>>>>>>> Ed Kramer
>>>>>>>> Bamford Fire Sprinkler
>>>>>>>>
>>>>>>>> -----Original Message-----
>>>>>>>> From: Sprinklerforum [mailto:
>>>>>>>> [email protected]]
>>>>>>>> On Behalf Of Travis Mack, SET
>>>>>>>> Sent: Friday, February 12, 2016 9:28 AM
>>>>>>>> To: [email protected]
>>>>>>>> Subject: Re: Tyco CC sprinklers / draft curtain
>>>>>>>>
>>>>>>>> That is what the contractor is arguing.  The NFPA 13 definitions of
>>>>>>>> draft
>>>>>>>> curtains are in reference to separation of ESFR and SR, water spray
>>>>>>>> systems
>>>>>>>> and hazard separation.
>>>>>>>>
>>>>>>>> It is an outside the box thinking for sure.  As you say, if it is
>>>>>>>> stapled
>>>>>>>> to
>>>>>>>> the deck, that would prevent heat from passing through and over.
>>>>>>>> That
>>>>>>>> is
>>>>>>>> the only criteria in the datasheet.
>>>>>>>>
>>>>>>>>
>>>>>>>> Travis Mack, SET
>>>>>>>> MFP Design, LLC
>>>>>>>> 2508 E Lodgepole Drive
>>>>>>>> Gilbert, AZ 85298
>>>>>>>> 480-505-9271
>>>>>>>> fax: 866-430-6107
>>>>>>>> email:[email protected]
>>>>>>>>
>>>>>>>> http://www.mfpdesign.com
>>>>>>>> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
>>>>>>>> Send large files to us via: https://www.hightail.com/u/MFPDesign
>>>>>>>>
>>>>>>>> On 2/12/2016 8:19 AM, Matthew J Willis wrote:
>>>>>>>>
>>>>>>>> LOL.
>>>>>>>>
>>>>>>>> I say it does meet it.
>>>>>>>>> Insulation by default blocks heat..
>>>>>>>>>
>>>>>>>>> R/
>>>>>>>>> Matt
>>>>>>>>>
>>>>>>>>>
>>>>>>>>> Matthew J. Willis
>>>>>>>>> Project Manager
>>>>>>>>> Rapid Fire Protection Inc.
>>>>>>>>> *NEW ADDRESS*
>>>>>>>>> 1530 Samco Road
>>>>>>>>> Rapid City, SD 57702
>>>>>>>>> Office-605.348.2342
>>>>>>>>> Direct Line-605.593.5063
>>>>>>>>> Cell-605.391.2733
>>>>>>>>> Fax:-605.348.0108
>>>>>>>>>
>>>>>>>>>
>>>>>>>>>
>>>>>>>>>
>>>>>>>>>
>>>>>>>>>
>>>>>>>>> -----Original Message-----
>>>>>>>>> From: Sprinklerforum
>>>>>>>>> [mailto:[email protected]] On Behalf
>>>>>>>>> Of
>>>>>>>>> Travis Mack
>>>>>>>>> Sent: Friday, February 12, 2016 8:16 AM
>>>>>>>>> To: [email protected]
>>>>>>>>> Subject: Re: Tyco CC sprinklers / draft curtain
>>>>>>>>>
>>>>>>>>> Well, the customer called Tyco and they could not say definitively
>>>>>>>>> if
>>>>>>>>> the
>>>>>>>>>
>>>>>>>>> insulation would meet the requirements or not.
>>>>>>>>>
>>>>>>>>> Travis Mack, SET
>>>>>>>>
>>>>>>>>> MFP Design, LLC
>>>>>>>>> "Follow" us on Facebook:
>>>>>>>>> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
>>>>>>>>> Send large files to MFP Design via:
>>>>>>>>> https://www.hightail.com/u/MFPDesign
>>>>>>>>>
>>>>>>>>> Sent from my iPhone
>>>>>>>>>
>>>>>>>>> On Feb 11, 2016, at 4:49 PM, Travis Mack, SET <[email protected]
>>>>>>>>> >
>>>>>>>>> wrote:
>>>>>>>>> I have a customer that is asking if batt insulation can be secured
>>>>>>>>> to
>>>>>>>>> the
>>>>>>>>> roof decking and used as a draft curtain for the Tyco CC
>>>>>>>>> sprinklers.  I
>>>>>>>>>
>>>>>>>>> have
>>>>>>>>>
>>>>>>>> never seen an application such as this, but it doesn't seem to be
>>>>>>>> prohibited
>>>>>>>> in the datasheet.  The only requirement is that it must be
>>>>>>>> constructed
>>>>>>>> of
>>>>>>>> a
>>>>>>>> material so that heat can not pass through or over.
>>>>>>>>
>>>>>>>> What do you think?  Could insulation secured to the roof/floor deck
>>>>>>>>
>>>>>>>> serve
>>>>>>>>> as a draft curtain for these sprinklers?  My gut feeling is that it
>>>>>>>>> would
>>>>>>>>>
>>>>>>>>> not be suitable, but I can't find something in the data sheet to
>>>>>>>>>
>>>>>>>> support
>>>>>>>> that.  My only thought is that activation of a sprinkler could
>>>>>>>> possibly
>>>>>>>> knock the insulation down.
>>>>>>>>
>>>>>>>> --
>>>>>>>>
>>>>>>>> Travis Mack, SET
>>>>>>>>>
>>>>>>>>>> MFP Design, LLC
>>>>>>>>>> 2508 E Lodgepole Drive
>>>>>>>>>> Gilbert, AZ 85298
>>>>>>>>>> 480-505-9271
>>>>>>>>>> fax: 866-430-6107
>>>>>>>>>> email:[email protected]
>>>>>>>>>>
>>>>>>>>>> http://www.mfpdesign.com
>>>>>>>>>> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
>>>>>>>>>> Send large files to us via: https://www.hightail.com/u/MFPDesign
>>>>>>>>>>
>>>>>>>>>> _______________________________________________
>>>>>>>>>> Sprinklerforum mailing list
>>>>>>>>>> [email protected]
>>>>>>>>>>
>>>>>>>>>>
>>>>>>>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
>>>>>>>>>> ler.org
>>>>>>>>>>
>>>>>>>>>> _______________________________________________
>>>>>>>>>>
>>>>>>>>>> Sprinklerforum mailing list
>>>>>>>>> [email protected]
>>>>>>>>>
>>>>>>>>>
>>>>>>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>>>>>>>>> er.org
>>>>>>>>>
>>>>>>>>> _______________________________________________
>>>>>>>>> Sprinklerforum mailing list
>>>>>>>>> [email protected]
>>>>>>>>>
>>>>>>>>>
>>>>>>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>>>>>>>>> er.org
>>>>>>>>>
>>>>>>>>> _______________________________________________
>>>>>>>>>
>>>>>>>>> Sprinklerforum mailing list
>>>>>>>> [email protected]
>>>>>>>>
>>>>>>>>
>>>>>>>>
>>>>>>>>
>>>>>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>>>>>>>
>>>>>>>> _______________________________________________
>>>>>>>> Sprinklerforum mailing list
>>>>>>>> [email protected]
>>>>>>>>
>>>>>>>>
>>>>>>>>
>>>>>>>>
>>>>>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>>>>>>>
>>>>>>>> _______________________________________________
>>>>>>>>
>>>>>>>> Sprinklerforum mailing list
>>>>>>> [email protected]
>>>>>>>
>>>>>>>
>>>>>>>
>>>>>>>
>>>>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>>>>>>
>>>>>>> _______________________________________________
>>>>>>>
>>>>>>> Sprinklerforum mailing list
>>>>>> [email protected]
>>>>>>
>>>>>>
>>>>>>
>>>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>>>>>
>>>>>> _______________________________________________
>>>>>>
>>>>> Sprinklerforum mailing list
>>>>> [email protected]
>>>>>
>>>>>
>>>>>
>>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>>>>
>>>>> _______________________________________________
>>>>>
>>>> Sprinklerforum mailing list
>>>> [email protected]
>>>>
>>>>
>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>>>
>>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>>
>>>
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>>
>>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>>
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to