Good advice Travis, I'll try to start thinking for myself.

Why CC sprinklers though if this is your case?

Brad
On Feb 12, 2016 10:32 AM, "Travis Mack, SET" <[email protected]> wrote:

> Think outside your bubble.  Tyco CC3...16' max spacing...5.6k sprinkler...
>
> Things are constantly evolving in this industry.  You have to stay on the
> edge to always keep up to date on available products.  It can be a full
> time job just doing that.
>
> Travis Mack, SET
> MFP Design, LLC
> 2508 E Lodgepole Drive
> Gilbert, AZ 85298
> 480-505-9271
> fax: 866-430-6107
> email:[email protected]
>
> http://www.mfpdesign.com
> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
> Send large files to us via: https://www.hightail.com/u/MFPDesign
>
> On 2/12/2016 9:28 AM, Brad Casterline wrote:
>
>> I'm thinking very quick activation time, 10 x 10 max, min 10 psi on a 2.8
>> K, in a small volume--- I get visions not unlike what I imagine high
>> efficiency water mist systems might look like--
>> But I am not the mnf rep, pe, t.c. member or ahj--
>>
>> B
>> On Feb 12, 2016 10:16 AM, "Travis Mack, SET" <[email protected]> wrote:
>>
>> The max application for CC3 is 60".  However, it is not the height. It is
>>> the sheer number of them that are needed.  Don't think single building.
>>> Think apartment complex...multiple buildings / multiple floors.
>>>
>>> Travis Mack, SET
>>> MFP Design, LLC
>>> 2508 E Lodgepole Drive
>>> Gilbert, AZ 85298
>>> 480-505-9271
>>> fax: 866-430-6107
>>> email:[email protected]
>>>
>>> http://www.mfpdesign.com
>>> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
>>> Send large files to us via: https://www.hightail.com/u/MFPDesign
>>>
>>> On 2/12/2016 8:57 AM, Brad Casterline wrote:
>>>
>>> For crying out loud though, isn't the max 'ceiling height' for this
>>>> application THREE FEET?
>>>> On Feb 12, 2016 9:54 AM, "Travis Mack, SET" <[email protected]>
>>>> wrote:
>>>>
>>>> You and I are on the same page.  We were just hoping to get a definitive
>>>>
>>>>> answer from the manufacturer.
>>>>>
>>>>> Travis Mack, SET
>>>>> MFP Design, LLC
>>>>> 2508 E Lodgepole Drive
>>>>> Gilbert, AZ 85298
>>>>> 480-505-9271
>>>>> fax: 866-430-6107
>>>>> email:[email protected]
>>>>>
>>>>> http://www.mfpdesign.com
>>>>> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
>>>>> Send large files to us via: https://www.hightail.com/u/MFPDesign
>>>>>
>>>>> On 2/12/2016 8:53 AM, Ed Kramer wrote:
>>>>>
>>>>> The AHJ is going to have to make the final call.  My pay scale isn't
>>>>> high
>>>>>
>>>>>> enough to make those types decisions, but if it were,  I'd say no.  If
>>>>>> water
>>>>>> spray from the 1st sprinkler or 2 damages the insulation to allow heat
>>>>>> to
>>>>>> flow past it, you've lost your heat barrier and the 1000 sf design
>>>>>> area
>>>>>> is
>>>>>> out-the-window.
>>>>>>
>>>>>> Back to my regularly scheduled program.
>>>>>>
>>>>>> Ed Kramer
>>>>>> Bamford Fire Sprinkler
>>>>>>
>>>>>> -----Original Message-----
>>>>>> From: Sprinklerforum [mailto:
>>>>>> [email protected]]
>>>>>> On Behalf Of Travis Mack, SET
>>>>>> Sent: Friday, February 12, 2016 9:28 AM
>>>>>> To: [email protected]
>>>>>> Subject: Re: Tyco CC sprinklers / draft curtain
>>>>>>
>>>>>> That is what the contractor is arguing.  The NFPA 13 definitions of
>>>>>> draft
>>>>>> curtains are in reference to separation of ESFR and SR, water spray
>>>>>> systems
>>>>>> and hazard separation.
>>>>>>
>>>>>> It is an outside the box thinking for sure.  As you say, if it is
>>>>>> stapled
>>>>>> to
>>>>>> the deck, that would prevent heat from passing through and over.  That
>>>>>> is
>>>>>> the only criteria in the datasheet.
>>>>>>
>>>>>>
>>>>>> Travis Mack, SET
>>>>>> MFP Design, LLC
>>>>>> 2508 E Lodgepole Drive
>>>>>> Gilbert, AZ 85298
>>>>>> 480-505-9271
>>>>>> fax: 866-430-6107
>>>>>> email:[email protected]
>>>>>>
>>>>>> http://www.mfpdesign.com
>>>>>> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
>>>>>> Send large files to us via: https://www.hightail.com/u/MFPDesign
>>>>>>
>>>>>> On 2/12/2016 8:19 AM, Matthew J Willis wrote:
>>>>>>
>>>>>> LOL.
>>>>>>
>>>>>>> I say it does meet it.
>>>>>>> Insulation by default blocks heat..
>>>>>>>
>>>>>>> R/
>>>>>>> Matt
>>>>>>>
>>>>>>>
>>>>>>> Matthew J. Willis
>>>>>>> Project Manager
>>>>>>> Rapid Fire Protection Inc.
>>>>>>> *NEW ADDRESS*
>>>>>>> 1530 Samco Road
>>>>>>> Rapid City, SD 57702
>>>>>>> Office-605.348.2342
>>>>>>> Direct Line-605.593.5063
>>>>>>> Cell-605.391.2733
>>>>>>> Fax:-605.348.0108
>>>>>>>
>>>>>>>
>>>>>>>
>>>>>>>
>>>>>>>
>>>>>>>
>>>>>>> -----Original Message-----
>>>>>>> From: Sprinklerforum
>>>>>>> [mailto:[email protected]] On Behalf Of
>>>>>>> Travis Mack
>>>>>>> Sent: Friday, February 12, 2016 8:16 AM
>>>>>>> To: [email protected]
>>>>>>> Subject: Re: Tyco CC sprinklers / draft curtain
>>>>>>>
>>>>>>> Well, the customer called Tyco and they could not say definitively if
>>>>>>> the
>>>>>>>
>>>>>>> insulation would meet the requirements or not.
>>>>>>>
>>>>>>
>>>>>> Travis Mack, SET
>>>>>>> MFP Design, LLC
>>>>>>> "Follow" us on Facebook:
>>>>>>> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
>>>>>>> Send large files to MFP Design via:
>>>>>>> https://www.hightail.com/u/MFPDesign
>>>>>>>
>>>>>>> Sent from my iPhone
>>>>>>>
>>>>>>> On Feb 11, 2016, at 4:49 PM, Travis Mack, SET <[email protected]>
>>>>>>> wrote:
>>>>>>> I have a customer that is asking if batt insulation can be secured to
>>>>>>> the
>>>>>>> roof decking and used as a draft curtain for the Tyco CC
>>>>>>> sprinklers.  I
>>>>>>>
>>>>>>> have
>>>>>> never seen an application such as this, but it doesn't seem to be
>>>>>> prohibited
>>>>>> in the datasheet.  The only requirement is that it must be constructed
>>>>>> of
>>>>>> a
>>>>>> material so that heat can not pass through or over.
>>>>>>
>>>>>> What do you think?  Could insulation secured to the roof/floor deck
>>>>>>
>>>>>>> serve
>>>>>>> as a draft curtain for these sprinklers?  My gut feeling is that it
>>>>>>> would
>>>>>>>
>>>>>>> not be suitable, but I can't find something in the data sheet to
>>>>>> support
>>>>>> that.  My only thought is that activation of a sprinkler could
>>>>>> possibly
>>>>>> knock the insulation down.
>>>>>>
>>>>>> --
>>>>>>
>>>>>>> Travis Mack, SET
>>>>>>>> MFP Design, LLC
>>>>>>>> 2508 E Lodgepole Drive
>>>>>>>> Gilbert, AZ 85298
>>>>>>>> 480-505-9271
>>>>>>>> fax: 866-430-6107
>>>>>>>> email:[email protected]
>>>>>>>>
>>>>>>>> http://www.mfpdesign.com
>>>>>>>> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
>>>>>>>> Send large files to us via: https://www.hightail.com/u/MFPDesign
>>>>>>>>
>>>>>>>> _______________________________________________
>>>>>>>> Sprinklerforum mailing list
>>>>>>>> [email protected]
>>>>>>>>
>>>>>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
>>>>>>>> ler.org
>>>>>>>>
>>>>>>>> _______________________________________________
>>>>>>>>
>>>>>>> Sprinklerforum mailing list
>>>>>>> [email protected]
>>>>>>>
>>>>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>>>>>>> er.org
>>>>>>>
>>>>>>> _______________________________________________
>>>>>>> Sprinklerforum mailing list
>>>>>>> [email protected]
>>>>>>>
>>>>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>>>>>>> er.org
>>>>>>>
>>>>>>> _______________________________________________
>>>>>>>
>>>>>> Sprinklerforum mailing list
>>>>>> [email protected]
>>>>>>
>>>>>>
>>>>>>
>>>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>>>>>
>>>>>> _______________________________________________
>>>>>> Sprinklerforum mailing list
>>>>>> [email protected]
>>>>>>
>>>>>>
>>>>>>
>>>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>>>>>
>>>>>> _______________________________________________
>>>>>>
>>>>> Sprinklerforum mailing list
>>>>> [email protected]
>>>>>
>>>>>
>>>>>
>>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>>>>
>>>>> _______________________________________________
>>>>>
>>>> Sprinklerforum mailing list
>>>> [email protected]
>>>>
>>>>
>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>>>
>>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>>
>>>
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>>
>>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>>
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to