I'm thinking very quick activation time, 10 x 10 max, min 10 psi on a 2.8
K, in a small volume--- I get visions not unlike what I imagine high
efficiency water mist systems might look like--
But I am not the mnf rep, pe, t.c. member or ahj--

B
On Feb 12, 2016 10:16 AM, "Travis Mack, SET" <[email protected]> wrote:

> The max application for CC3 is 60".  However, it is not the height. It is
> the sheer number of them that are needed.  Don't think single building.
> Think apartment complex...multiple buildings / multiple floors.
>
> Travis Mack, SET
> MFP Design, LLC
> 2508 E Lodgepole Drive
> Gilbert, AZ 85298
> 480-505-9271
> fax: 866-430-6107
> email:[email protected]
>
> http://www.mfpdesign.com
> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
> Send large files to us via: https://www.hightail.com/u/MFPDesign
>
> On 2/12/2016 8:57 AM, Brad Casterline wrote:
>
>> For crying out loud though, isn't the max 'ceiling height' for this
>> application THREE FEET?
>> On Feb 12, 2016 9:54 AM, "Travis Mack, SET" <[email protected]> wrote:
>>
>> You and I are on the same page.  We were just hoping to get a definitive
>>> answer from the manufacturer.
>>>
>>> Travis Mack, SET
>>> MFP Design, LLC
>>> 2508 E Lodgepole Drive
>>> Gilbert, AZ 85298
>>> 480-505-9271
>>> fax: 866-430-6107
>>> email:[email protected]
>>>
>>> http://www.mfpdesign.com
>>> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
>>> Send large files to us via: https://www.hightail.com/u/MFPDesign
>>>
>>> On 2/12/2016 8:53 AM, Ed Kramer wrote:
>>>
>>> The AHJ is going to have to make the final call.  My pay scale isn't high
>>>> enough to make those types decisions, but if it were,  I'd say no.  If
>>>> water
>>>> spray from the 1st sprinkler or 2 damages the insulation to allow heat
>>>> to
>>>> flow past it, you've lost your heat barrier and the 1000 sf design area
>>>> is
>>>> out-the-window.
>>>>
>>>> Back to my regularly scheduled program.
>>>>
>>>> Ed Kramer
>>>> Bamford Fire Sprinkler
>>>>
>>>> -----Original Message-----
>>>> From: Sprinklerforum [mailto:
>>>> [email protected]]
>>>> On Behalf Of Travis Mack, SET
>>>> Sent: Friday, February 12, 2016 9:28 AM
>>>> To: [email protected]
>>>> Subject: Re: Tyco CC sprinklers / draft curtain
>>>>
>>>> That is what the contractor is arguing.  The NFPA 13 definitions of
>>>> draft
>>>> curtains are in reference to separation of ESFR and SR, water spray
>>>> systems
>>>> and hazard separation.
>>>>
>>>> It is an outside the box thinking for sure.  As you say, if it is
>>>> stapled
>>>> to
>>>> the deck, that would prevent heat from passing through and over.  That
>>>> is
>>>> the only criteria in the datasheet.
>>>>
>>>>
>>>> Travis Mack, SET
>>>> MFP Design, LLC
>>>> 2508 E Lodgepole Drive
>>>> Gilbert, AZ 85298
>>>> 480-505-9271
>>>> fax: 866-430-6107
>>>> email:[email protected]
>>>>
>>>> http://www.mfpdesign.com
>>>> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
>>>> Send large files to us via: https://www.hightail.com/u/MFPDesign
>>>>
>>>> On 2/12/2016 8:19 AM, Matthew J Willis wrote:
>>>>
>>>> LOL.
>>>>>
>>>>> I say it does meet it.
>>>>> Insulation by default blocks heat..
>>>>>
>>>>> R/
>>>>> Matt
>>>>>
>>>>>
>>>>> Matthew J. Willis
>>>>> Project Manager
>>>>> Rapid Fire Protection Inc.
>>>>> *NEW ADDRESS*
>>>>> 1530 Samco Road
>>>>> Rapid City, SD 57702
>>>>> Office-605.348.2342
>>>>> Direct Line-605.593.5063
>>>>> Cell-605.391.2733
>>>>> Fax:-605.348.0108
>>>>>
>>>>>
>>>>>
>>>>>
>>>>>
>>>>>
>>>>> -----Original Message-----
>>>>> From: Sprinklerforum
>>>>> [mailto:[email protected]] On Behalf Of
>>>>> Travis Mack
>>>>> Sent: Friday, February 12, 2016 8:16 AM
>>>>> To: [email protected]
>>>>> Subject: Re: Tyco CC sprinklers / draft curtain
>>>>>
>>>>> Well, the customer called Tyco and they could not say definitively if
>>>>> the
>>>>>
>>>>> insulation would meet the requirements or not.
>>>>
>>>>
>>>>> Travis Mack, SET
>>>>> MFP Design, LLC
>>>>> "Follow" us on Facebook:
>>>>> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
>>>>> Send large files to MFP Design via:
>>>>> https://www.hightail.com/u/MFPDesign
>>>>>
>>>>> Sent from my iPhone
>>>>>
>>>>> On Feb 11, 2016, at 4:49 PM, Travis Mack, SET <[email protected]>
>>>>> wrote:
>>>>> I have a customer that is asking if batt insulation can be secured to
>>>>> the
>>>>> roof decking and used as a draft curtain for the Tyco CC sprinklers.  I
>>>>>
>>>> have
>>>> never seen an application such as this, but it doesn't seem to be
>>>> prohibited
>>>> in the datasheet.  The only requirement is that it must be constructed
>>>> of
>>>> a
>>>> material so that heat can not pass through or over.
>>>>
>>>> What do you think?  Could insulation secured to the roof/floor deck
>>>>> serve
>>>>> as a draft curtain for these sprinklers?  My gut feeling is that it
>>>>> would
>>>>>
>>>> not be suitable, but I can't find something in the data sheet to support
>>>> that.  My only thought is that activation of a sprinkler could possibly
>>>> knock the insulation down.
>>>>
>>>> --
>>>>>
>>>>>> Travis Mack, SET
>>>>>> MFP Design, LLC
>>>>>> 2508 E Lodgepole Drive
>>>>>> Gilbert, AZ 85298
>>>>>> 480-505-9271
>>>>>> fax: 866-430-6107
>>>>>> email:[email protected]
>>>>>>
>>>>>> http://www.mfpdesign.com
>>>>>> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
>>>>>> Send large files to us via: https://www.hightail.com/u/MFPDesign
>>>>>>
>>>>>> _______________________________________________
>>>>>> Sprinklerforum mailing list
>>>>>> [email protected]
>>>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
>>>>>> ler.org
>>>>>>
>>>>>> _______________________________________________
>>>>> Sprinklerforum mailing list
>>>>> [email protected]
>>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>>>>> er.org
>>>>>
>>>>> _______________________________________________
>>>>> Sprinklerforum mailing list
>>>>> [email protected]
>>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>>>>> er.org
>>>>>
>>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> [email protected]
>>>>
>>>>
>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>>>
>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> [email protected]
>>>>
>>>>
>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>>>
>>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>>
>>>
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>>
>>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>>
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to