That requirement has been in the standard since 2002. It was further clarified in the 2007 edition. I don't think it has changed since 2007. The CC3 sprinklers are relatively new to get the 16' spacing. Used to be max 12' spacing 144 sq ft with the Viking COIN and Tyco CC1/CC2.
Travis Mack, SET MFP Design, LLC 2508 E Lodgepole Drive Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 email:[email protected] http://www.mfpdesign.com https://www.facebook.com/pages/MFP-Design-LLC/92218417692 Send large files to us via: https://www.hightail.com/u/MFPDesign On 2/12/2016 9:40 AM, Brad Casterline wrote:
Good advice Travis, I'll try to start thinking for myself. Why CC sprinklers though if this is your case? Brad On Feb 12, 2016 10:32 AM, "Travis Mack, SET" <[email protected]> wrote:Think outside your bubble. Tyco CC3...16' max spacing...5.6k sprinkler... Things are constantly evolving in this industry. You have to stay on the edge to always keep up to date on available products. It can be a full time job just doing that. Travis Mack, SET MFP Design, LLC 2508 E Lodgepole Drive Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 email:[email protected] http://www.mfpdesign.com https://www.facebook.com/pages/MFP-Design-LLC/92218417692 Send large files to us via: https://www.hightail.com/u/MFPDesign On 2/12/2016 9:28 AM, Brad Casterline wrote:I'm thinking very quick activation time, 10 x 10 max, min 10 psi on a 2.8 K, in a small volume--- I get visions not unlike what I imagine high efficiency water mist systems might look like-- But I am not the mnf rep, pe, t.c. member or ahj-- B On Feb 12, 2016 10:16 AM, "Travis Mack, SET" <[email protected]> wrote: The max application for CC3 is 60". However, it is not the height. It isthe sheer number of them that are needed. Don't think single building. Think apartment complex...multiple buildings / multiple floors. Travis Mack, SET MFP Design, LLC 2508 E Lodgepole Drive Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 email:[email protected] http://www.mfpdesign.com https://www.facebook.com/pages/MFP-Design-LLC/92218417692 Send large files to us via: https://www.hightail.com/u/MFPDesign On 2/12/2016 8:57 AM, Brad Casterline wrote: For crying out loud though, isn't the max 'ceiling height' for thisapplication THREE FEET? On Feb 12, 2016 9:54 AM, "Travis Mack, SET" <[email protected]> wrote: You and I are on the same page. We were just hoping to get a definitiveanswer from the manufacturer. Travis Mack, SET MFP Design, LLC 2508 E Lodgepole Drive Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 email:[email protected] http://www.mfpdesign.com https://www.facebook.com/pages/MFP-Design-LLC/92218417692 Send large files to us via: https://www.hightail.com/u/MFPDesign On 2/12/2016 8:53 AM, Ed Kramer wrote: The AHJ is going to have to make the final call. My pay scale isn't highenough to make those types decisions, but if it were, I'd say no. If water spray from the 1st sprinkler or 2 damages the insulation to allow heat to flow past it, you've lost your heat barrier and the 1000 sf design area is out-the-window. Back to my regularly scheduled program. Ed Kramer Bamford Fire Sprinkler -----Original Message----- From: Sprinklerforum [mailto: [email protected]] On Behalf Of Travis Mack, SET Sent: Friday, February 12, 2016 9:28 AM To: [email protected] Subject: Re: Tyco CC sprinklers / draft curtain That is what the contractor is arguing. The NFPA 13 definitions of draft curtains are in reference to separation of ESFR and SR, water spray systems and hazard separation. It is an outside the box thinking for sure. As you say, if it is stapled to the deck, that would prevent heat from passing through and over. That is the only criteria in the datasheet. Travis Mack, SET MFP Design, LLC 2508 E Lodgepole Drive Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 email:[email protected] http://www.mfpdesign.com https://www.facebook.com/pages/MFP-Design-LLC/92218417692 Send large files to us via: https://www.hightail.com/u/MFPDesign On 2/12/2016 8:19 AM, Matthew J Willis wrote: LOL.I say it does meet it. Insulation by default blocks heat.. R/ Matt Matthew J. Willis Project Manager Rapid Fire Protection Inc. *NEW ADDRESS* 1530 Samco Road Rapid City, SD 57702 Office-605.348.2342 Direct Line-605.593.5063 Cell-605.391.2733 Fax:-605.348.0108 -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Travis Mack Sent: Friday, February 12, 2016 8:16 AM To: [email protected] Subject: Re: Tyco CC sprinklers / draft curtain Well, the customer called Tyco and they could not say definitively if the insulation would meet the requirements or not.Travis Mack, SETMFP Design, LLC "Follow" us on Facebook: https://www.facebook.com/pages/MFP-Design-LLC/92218417692 Send large files to MFP Design via: https://www.hightail.com/u/MFPDesign Sent from my iPhone On Feb 11, 2016, at 4:49 PM, Travis Mack, SET <[email protected]> wrote: I have a customer that is asking if batt insulation can be secured to the roof decking and used as a draft curtain for the Tyco CC sprinklers. I havenever seen an application such as this, but it doesn't seem to be prohibited in the datasheet. The only requirement is that it must be constructed of a material so that heat can not pass through or over. What do you think? Could insulation secured to the roof/floor deckserve as a draft curtain for these sprinklers? My gut feeling is that it would not be suitable, but I can't find something in the data sheet tosupport that. My only thought is that activation of a sprinkler could possibly knock the insulation down. --Travis Mack, SETMFP Design, LLC 2508 E Lodgepole Drive Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 email:[email protected] http://www.mfpdesign.com https://www.facebook.com/pages/MFP-Design-LLC/92218417692 Send large files to us via: https://www.hightail.com/u/MFPDesign _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink ler.org _______________________________________________Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl er.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl er.org _______________________________________________Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org_______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org_______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org