And in most of the jurisdictions I work in it is flushed with a garden hose 
only.  You'd be surprised by the green grass, asphalt, rocks, sticks, burlap 
and so I find when it is flushed properly when we tear them apart to find out 
what went wrong.

I've had the same UG contractor tell me he never flushes them only to have me 
remind him he always does on my projects.

Commissioning project on State Capitol new fire pump recently where we had them 
flush the UG the day before the pump test (acceptance) because it had not been 
flushed to 1860 gpm...they only did it after I told the GC he bought the pump 
if we hear rocks or anything of the sort.

Scott

Office: (763) 425-1001 x 202
Cell: (612) 759-5556

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Steve Leyton
Sent: Tuesday, March 29, 2016 11:17 PM
To: [email protected]
Subject: RE: UG 5 ft outside building

That's pretty much the issue now isn't it? In most of the jurisdictions where 
we work, if the work is divided as we are discussing, then to hydrostatic test 
and two flushes are required. The problem for the owner is when a leak occurs 
or some sort of inspection card goes missing, and then you have two different 
contractors pointing their fingers at each other.


Steve


-------- Original message --------
From: Scott Futrell <[email protected]>
Date: 3/29/2016 7:15 PM (GMT-08:00)
To: [email protected]
Subject: RE: UG 5 ft outside building

Who flushes all of it in accordance with 13 & 24? Who accepts the liability for 
all of it?

Scott