It's called 'AHJ wiggle room'.
Hopefully you haven't pi$$ed yours off in the past.

:) b ;) c :)
On Apr 28, 2016 4:35 PM, <[email protected]> wrote:

> Forum,
>
> We have concrete tee construction.  Bottom of stems measured from the
> ceiling is 26" down.  Centerline of stems are spaced apart in an every
> other fashion of 7', 2'8", 7', 2'8", etc.  Ideally we would like to use
> NFPA 13 (2013) 8.6.4.1.2(5) to protect the area so we don't have to add
> additional sprinklers/piping.  However it states this is only applicable
> for 3ft to 7.5ft stem spacing.  Can someone tell me the purpose behind the
> 3ft minimum threshold?  Even though we have some 2'8" sections, do you
> believe the intent of this code was for my situation?  Or do you believe
> the intent is for concrete tee construction where every stem is 3ft or
> less?  I can see people interpreting this passage either way as all stems
> are spaced away from another stem more than 3ft, yet all stems are spaced
> away from another stem less than 3ft.
>
> To me, it seems ridiculous that I can have stems with any depth (let's say
> 10ft)  and spaced 3'1" apart and the deflector can be located 1" below the
> bottom of the stem (10'1") and branchlines can be spaced 15ft apart.  Yet
> if the same depth stems are spaced 2'11" apart the deflector can't be lower
> than 22" below the ceiling and because they are now obstructed, they have
> to be in every pocket.
>
> I appreciate anyone's opinion on my situation and/or knowledge/history of
> this codes development.
>
> Note: As I allude to, I know there are other ways to design this system
> utilizing 22" and beam rule.  I am more looking for the "Why's" or the "You
> missed this blurb" that agrees with your stance .
>
> Thanks,
> Sean VG
>
>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to