Thank you Larry!  That is exactly one of those "you missed this blurb's" I was 
looking for.

Thanks,
Sean VG




-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Larry Keeping
Sent: Thursday, April 28, 2016 3:03 PM
To: [email protected]
Subject: RE: NFPA 13 (2013) 8.6.4.1.2(5) - why the 3ft minimum?

It may be of help if you reference the 2016 edition of NFPA 13. 

There, in Section 8.6.4.1.2(5) the 3 ft limit has been deleted. 

The Committee Statement for that revision was that concrete tees are capable of 
withstanding the heat long enough for sprinklers to activate even when the tees 
are closer than 3 feet on centers.

Larry Keeping

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of [email protected]
Sent: April-28-16 5:35 PM
To: [email protected]
Subject: NFPA 13 (2013) 8.6.4.1.2(5) - why the 3ft minimum?

Forum,

We have concrete tee construction.  Bottom of stems measured from the ceiling 
is 26" down.  Centerline of stems are spaced apart in an every other fashion of 
7', 2'8", 7', 2'8", etc.  Ideally we would like to use NFPA 13 (2013) 
8.6.4.1.2(5) to protect the area so we don't have to add additional 
sprinklers/piping.  However it states this is only applicable for 3ft to 7.5ft 
stem spacing.  Can someone tell me the purpose behind the 3ft minimum 
threshold?  Even though we have some 2'8" sections, do you believe the intent 
of this code was for my situation?  Or do you believe the intent is for 
concrete tee construction where every stem is 3ft or less?  I can see people 
interpreting this passage either way as all stems are spaced away from another 
stem more than 3ft, yet all stems are spaced away from another stem less than 
3ft.

To me, it seems ridiculous that I can have stems with any depth (let's say 
10ft)  and spaced 3'1" apart and the deflector can be located 1" below the 
bottom of the stem (10'1") and branchlines can be spaced 15ft apart.  Yet if 
the same depth stems are spaced 2'11" apart the deflector can't be lower than 
22" below the ceiling and because they are now obstructed, they have to be in 
every pocket.

I appreciate anyone's opinion on my situation and/or knowledge/history of this 
codes development.

Note: As I allude to, I know there are other ways to design this system 
utilizing 22" and beam rule.  I am more looking for the "Why's" or the "You 
missed this blurb" that agrees with your stance .

Thanks,
Sean VG





_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to