The water might be smart but is it UL Listed?  LOL

Sent from my iPhone

> On Apr 28, 2016, at 6:57 PM, rongreenman . <[email protected]> wrote:
> 
> Rules is rules because they be rules. We calc discharge in rectangles, and
> not consistent rectangles. Sprinklers typically spray in circles. To listen
> to people you'd think a standard spray knew what dimension rectangle the
> designer chose, sprays at that pattern precisely to each corner as long as
> the distance along the pipe and perpendicular to the pipe does not exceed
> 7'6" from the sprinkler and then abruptly drops straight down, and on the
> way, figures out how to place exactly the desired density, not more nor
> less, in each square foot of the described rectangle. Smartest damned water
> on earth.
> 
> 
>> On Thu, Apr 28, 2016 at 3:41 PM, <[email protected]> wrote:
>> 
>> Ron,
>> 
>> Thank you for the input.  That's one of the things that drives me crazy.
>> I'm a numbers person and like to know the supporting information.  My jaw
>> hit the floor when I found out the 3x rule was made up because it had to be
>> something...and the 4x rule for EC heads was chosen because it is larger
>> than 3.  Come on guys!
>> 
>> Brad,
>> 
>> For your puzzle, I think it rhymes with Whoosh
>> 
>> Thanks,
>> Sean VG
>> 
>> 
>> 
>> 
>> 
>> -----Original Message-----
>> From: Sprinklerforum [mailto:
>> [email protected]] On Behalf Of Brad
>> Casterline
>> Sent: Thursday, April 28, 2016 3:37 PM
>> To: [email protected]
>> Subject: Re: NFPA 13 (2013) 8.6.4.1.2(5) - why the 3ft minimum?
>> 
>> How about stems at 7-10 Ron?
>> 
>> p.s. I'm working on an X-word puzzle... 6 letters starts with d ends with
>> e... a little help?
>> p.s.s. you were right a couple years ago when you told me if I'm looking
>> for a little love I might be looking in the wrong place.
>> I wish I was Larry, or Steve L right about now.
>>> On Apr 28, 2016 5:14 PM, "rongreenman ." <[email protected]> wrote:
>>> 
>>> I hate to state the obvious, nor sound like a d....e, but it's because
>>> it os the rule. It's the same if I have a duct that is 48" wide I need
>>> to place sprinklers under the duct but i can have multiple ducts 47"
>>> wide with a gap 1" wide between them, and I can have then all across
>>> the room and don't have to sprinkler under them. So at some point you
>>> have to look at common practice and you'd never see my scenario. What
>>> about yours? Do you regularly run into 2' 11" and 3' 1" stems?
>>> 
>>> On Thu, Apr 28, 2016 at 3:02 PM, Larry Keeping <[email protected]>
>>> wrote:
>>> 
>>>> It may be of help if you reference the 2016 edition of NFPA 13.
>>>> 
>>>> There, in Section 8.6.4.1.2(5) the 3 ft limit has been deleted.
>>>> 
>>>> The Committee Statement for that revision was that concrete tees are
>>>> capable of withstanding the heat long enough for sprinklers to
>>>> activate even when the tees are closer than 3 feet on centers.
>>>> 
>>>> Larry Keeping
>>>> 
>>>> -----Original Message-----
>>>> From: Sprinklerforum [mailto:
>>>> [email protected]] On Behalf Of
>>>> [email protected]
>>>> Sent: April-28-16 5:35 PM
>>>> To: [email protected]
>>>> Subject: NFPA 13 (2013) 8.6.4.1.2(5) - why the 3ft minimum?
>>>> 
>>>> Forum,
>>>> 
>>>> We have concrete tee construction.  Bottom of stems measured from
>>>> the ceiling is 26" down.  Centerline of stems are spaced apart in an
>>>> every other fashion of 7', 2'8", 7', 2'8", etc.  Ideally we would
>>>> like to use NFPA 13 (2013) 8.6.4.1.2(5) to protect the area so we
>>>> don't have to add additional sprinklers/piping.  However it states
>>>> this is only applicable for 3ft to 7.5ft stem spacing.  Can someone
>>>> tell me the purpose behind
>>> the
>>>> 3ft minimum threshold?  Even though we have some 2'8" sections, do
>>>> you believe the intent of this code was for my situation?  Or do you
>>>> believe the intent is for concrete tee construction where every stem
>>>> is 3ft or less?  I can see people interpreting this passage either
>>>> way as all stems are spaced away from another stem more than 3ft,
>>>> yet all stems are spaced away from another stem less than 3ft.
>>>> 
>>>> To me, it seems ridiculous that I can have stems with any depth
>>>> (let's
>>> say
>>>> 10ft)  and spaced 3'1" apart and the deflector can be located 1"
>>>> below
>>> the
>>>> bottom of the stem (10'1") and branchlines can be spaced 15ft apart.
>>>> Yet if the same depth stems are spaced 2'11" apart the deflector
>>>> can't be
>>> lower
>>>> than 22" below the ceiling and because they are now obstructed, they
>>>> have to be in every pocket.
>>>> 
>>>> I appreciate anyone's opinion on my situation and/or
>>>> knowledge/history of this codes development.
>>>> 
>>>> Note: As I allude to, I know there are other ways to design this
>>>> system utilizing 22" and beam rule.  I am more looking for the
>>>> "Why's" or the
>>> "You
>>>> missed this blurb" that agrees with your stance .
>>>> 
>>>> Thanks,
>>>> Sean VG
>>>> 
>>>> 
>>>> 
>>>> 
>>>> 
>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> [email protected]
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>>> er.org
>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> [email protected]
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>>> er.org
>>> 
>>> 
>>> 
>>> --
>>> Ron Greenman
>>> 
>>> 4110 Olson Dr., NW
>>> Gig Harbor, WA 98335
>>> 
>>> [email protected]
>>> 
>>> 253.576.9700
>>> 
>>> A problem well stated is a problem half solved. -Charles F. Kettering,
>>> inventor and engineer (1876-1958)
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> 
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>>> er.org
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> 
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> 
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
> 
> 
> -- 
> Ron Greenman
> 
> 4110 Olson Dr., NW
> Gig Harbor, WA 98335
> 
> [email protected]
> 
> 253.576.9700
> 
> A problem well stated is a problem half solved. -Charles F. Kettering,
> inventor and engineer (1876-1958)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to