Thanks Sean.
As to stems at 7-10, take a look at the full scale (though limited) cloud
ceiling studies that Research Foundation did, where-by they found that, the
higher the ceiling, the greater the gap between clouds could be- - - it's
the same kind of numbers thing, activation-wise.
On Apr 28, 2016 5:41 PM, <[email protected]> wrote:

> Ron,
>
> Thank you for the input.  That's one of the things that drives me crazy.
> I'm a numbers person and like to know the supporting information.  My jaw
> hit the floor when I found out the 3x rule was made up because it had to be
> something...and the 4x rule for EC heads was chosen because it is larger
> than 3.  Come on guys!
>
> Brad,
>
> For your puzzle, I think it rhymes with Whoosh
>
> Thanks,
> Sean VG
>
>
>
>
>
> -----Original Message-----
> From: Sprinklerforum [mailto:
> [email protected]] On Behalf Of Brad
> Casterline
> Sent: Thursday, April 28, 2016 3:37 PM
> To: [email protected]
> Subject: Re: NFPA 13 (2013) 8.6.4.1.2(5) - why the 3ft minimum?
>
> How about stems at 7-10 Ron?
>
> p.s. I'm working on an X-word puzzle... 6 letters starts with d ends with
> e... a little help?
> p.s.s. you were right a couple years ago when you told me if I'm looking
> for a little love I might be looking in the wrong place.
> I wish I was Larry, or Steve L right about now.
> On Apr 28, 2016 5:14 PM, "rongreenman ." <[email protected]> wrote:
>
> > I hate to state the obvious, nor sound like a d....e, but it's because
> > it os the rule. It's the same if I have a duct that is 48" wide I need
> > to place sprinklers under the duct but i can have multiple ducts 47"
> > wide with a gap 1" wide between them, and I can have then all across
> > the room and don't have to sprinkler under them. So at some point you
> > have to look at common practice and you'd never see my scenario. What
> > about yours? Do you regularly run into 2' 11" and 3' 1" stems?
> >
> > On Thu, Apr 28, 2016 at 3:02 PM, Larry Keeping <[email protected]>
> > wrote:
> >
> > > It may be of help if you reference the 2016 edition of NFPA 13.
> > >
> > > There, in Section 8.6.4.1.2(5) the 3 ft limit has been deleted.
> > >
> > > The Committee Statement for that revision was that concrete tees are
> > > capable of withstanding the heat long enough for sprinklers to
> > > activate even when the tees are closer than 3 feet on centers.
> > >
> > > Larry Keeping
> > >
> > > -----Original Message-----
> > > From: Sprinklerforum [mailto:
> > > [email protected]] On Behalf Of
> > > [email protected]
> > > Sent: April-28-16 5:35 PM
> > > To: [email protected]
> > > Subject: NFPA 13 (2013) 8.6.4.1.2(5) - why the 3ft minimum?
> > >
> > > Forum,
> > >
> > > We have concrete tee construction.  Bottom of stems measured from
> > > the ceiling is 26" down.  Centerline of stems are spaced apart in an
> > > every other fashion of 7', 2'8", 7', 2'8", etc.  Ideally we would
> > > like to use NFPA 13 (2013) 8.6.4.1.2(5) to protect the area so we
> > > don't have to add additional sprinklers/piping.  However it states
> > > this is only applicable for 3ft to 7.5ft stem spacing.  Can someone
> > > tell me the purpose behind
> > the
> > > 3ft minimum threshold?  Even though we have some 2'8" sections, do
> > > you believe the intent of this code was for my situation?  Or do you
> > > believe the intent is for concrete tee construction where every stem
> > > is 3ft or less?  I can see people interpreting this passage either
> > > way as all stems are spaced away from another stem more than 3ft,
> > > yet all stems are spaced away from another stem less than 3ft.
> > >
> > > To me, it seems ridiculous that I can have stems with any depth
> > > (let's
> > say
> > > 10ft)  and spaced 3'1" apart and the deflector can be located 1"
> > > below
> > the
> > > bottom of the stem (10'1") and branchlines can be spaced 15ft apart.
> > > Yet if the same depth stems are spaced 2'11" apart the deflector
> > > can't be
> > lower
> > > than 22" below the ceiling and because they are now obstructed, they
> > > have to be in every pocket.
> > >
> > > I appreciate anyone's opinion on my situation and/or
> > > knowledge/history of this codes development.
> > >
> > > Note: As I allude to, I know there are other ways to design this
> > > system utilizing 22" and beam rule.  I am more looking for the
> > > "Why's" or the
> > "You
> > > missed this blurb" that agrees with your stance .
> > >
> > > Thanks,
> > > Sean VG
> > >
> > >
> > >
> > >
> > >
> > > _______________________________________________
> > > Sprinklerforum mailing list
> > > [email protected]
> > >
> > >
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> > er.org
> > > _______________________________________________
> > > Sprinklerforum mailing list
> > > [email protected]
> > >
> > >
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> > er.org
> > >
> >
> >
> >
> > --
> > Ron Greenman
> >
> > 4110 Olson Dr., NW
> > Gig Harbor, WA 98335
> >
> > [email protected]
> >
> > 253.576.9700
> >
> > A problem well stated is a problem half solved. -Charles F. Kettering,
> > inventor and engineer (1876-1958)
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> > er.org
> >
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to