Ron,

Thank you for the input.  That's one of the things that drives me crazy.  I'm a 
numbers person and like to know the supporting information.  My jaw hit the 
floor when I found out the 3x rule was made up because it had to be 
something...and the 4x rule for EC heads was chosen because it is larger than 
3.  Come on guys!

Brad,

For your puzzle, I think it rhymes with Whoosh

Thanks,
Sean VG





-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Brad Casterline
Sent: Thursday, April 28, 2016 3:37 PM
To: [email protected]
Subject: Re: NFPA 13 (2013) 8.6.4.1.2(5) - why the 3ft minimum?

How about stems at 7-10 Ron?

p.s. I'm working on an X-word puzzle... 6 letters starts with d ends with e... 
a little help?
p.s.s. you were right a couple years ago when you told me if I'm looking for a 
little love I might be looking in the wrong place.
I wish I was Larry, or Steve L right about now.
On Apr 28, 2016 5:14 PM, "rongreenman ." <[email protected]> wrote:

> I hate to state the obvious, nor sound like a d....e, but it's because 
> it os the rule. It's the same if I have a duct that is 48" wide I need 
> to place sprinklers under the duct but i can have multiple ducts 47" 
> wide with a gap 1" wide between them, and I can have then all across 
> the room and don't have to sprinkler under them. So at some point you 
> have to look at common practice and you'd never see my scenario. What 
> about yours? Do you regularly run into 2' 11" and 3' 1" stems?
>
> On Thu, Apr 28, 2016 at 3:02 PM, Larry Keeping <[email protected]>
> wrote:
>
> > It may be of help if you reference the 2016 edition of NFPA 13.
> >
> > There, in Section 8.6.4.1.2(5) the 3 ft limit has been deleted.
> >
> > The Committee Statement for that revision was that concrete tees are 
> > capable of withstanding the heat long enough for sprinklers to 
> > activate even when the tees are closer than 3 feet on centers.
> >
> > Larry Keeping
> >
> > -----Original Message-----
> > From: Sprinklerforum [mailto:
> > [email protected]] On Behalf Of 
> > [email protected]
> > Sent: April-28-16 5:35 PM
> > To: [email protected]
> > Subject: NFPA 13 (2013) 8.6.4.1.2(5) - why the 3ft minimum?
> >
> > Forum,
> >
> > We have concrete tee construction.  Bottom of stems measured from 
> > the ceiling is 26" down.  Centerline of stems are spaced apart in an 
> > every other fashion of 7', 2'8", 7', 2'8", etc.  Ideally we would 
> > like to use NFPA 13 (2013) 8.6.4.1.2(5) to protect the area so we 
> > don't have to add additional sprinklers/piping.  However it states 
> > this is only applicable for 3ft to 7.5ft stem spacing.  Can someone 
> > tell me the purpose behind
> the
> > 3ft minimum threshold?  Even though we have some 2'8" sections, do 
> > you believe the intent of this code was for my situation?  Or do you 
> > believe the intent is for concrete tee construction where every stem 
> > is 3ft or less?  I can see people interpreting this passage either 
> > way as all stems are spaced away from another stem more than 3ft, 
> > yet all stems are spaced away from another stem less than 3ft.
> >
> > To me, it seems ridiculous that I can have stems with any depth 
> > (let's
> say
> > 10ft)  and spaced 3'1" apart and the deflector can be located 1" 
> > below
> the
> > bottom of the stem (10'1") and branchlines can be spaced 15ft apart.  
> > Yet if the same depth stems are spaced 2'11" apart the deflector 
> > can't be
> lower
> > than 22" below the ceiling and because they are now obstructed, they 
> > have to be in every pocket.
> >
> > I appreciate anyone's opinion on my situation and/or 
> > knowledge/history of this codes development.
> >
> > Note: As I allude to, I know there are other ways to design this 
> > system utilizing 22" and beam rule.  I am more looking for the 
> > "Why's" or the
> "You
> > missed this blurb" that agrees with your stance .
> >
> > Thanks,
> > Sean VG
> >
> >
> >
> >
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
> >
>
>
>
> --
> Ron Greenman
>
> 4110 Olson Dr., NW
> Gig Harbor, WA 98335
>
> [email protected]
>
> 253.576.9700
>
> A problem well stated is a problem half solved. -Charles F. Kettering, 
> inventor and engineer (1876-1958) 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to