They both do.  Ask the serving FD where they want the valves.

My opinion only,
Steve Leyton

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of James Litvak
Sent: Tuesday, May 10, 2016 10:44 AM
To: [email protected]
Subject: Class I Standpipe Hose Valve Location

IFC (2012) 905.4.1 requires hose valves to be on intermediate landings, unless 
approved otherwise. NFPA 14 (2010) 7.3.2 requires hose valves to be on the main 
landing, unless required otherwise, per 7.3.2.1. The IFC specifically 
references NFPA 14-10 for 905.4.2, but not 905.4.1.

My question is, when both documents are referenced as adopted standards, with 
no exceptions mentioned, which document takes precedence?


James Litvak