The installation of standpipes are per Section 905 and NFPA 14. Where there is a conflict between the two, the model code provisions apply. Either way, the AHJ should be consulted on the location preferred.
102.7.1 Conflicts. Where conflicts occur between provisions of this code and referenced codes and standards, the provisions of this code shall apply. 102.7.2 Provisions in referenced codes and standards. Where the extent of the reference to a referenced code or standard includes subject matter that is within the scope of this code, the provisions of this code, as applicable, shall take precedence over the provisions in the referenced code or standard. 905.2 Installation standard. Standpipe systems shall be installed in accordance with this section and NFPA 14. From: Sprinklerforum [mailto:[email protected]] On Behalf Of [email protected] Sent: Tuesday, May 10, 2016 11:03 AM To: [email protected] Subject: RE: Class I Standpipe Hose Valve Location 905.4 (1) - intermediate level for hose valves, Unless Otherwise Approved. NFPA 14 - 7.3.2 (1) at main floor landings OR 7.3.2.1 allows connection on intermediate landings where required by the AHJ. Regardless of whether or not the specific paragraph mentions NFPA 14, NFPA 14 is the adopted Standard for Standpipes per the Code per 905.2. This is one item that I make the call to the local FD and find out what the local preference will be. No point in guessing. Craig L. Prahl Fire Protection Group Lead/SME CH2M 200 Verdae Blvd. Greenville, SC 29607 Direct - 864.920.7540 Fax - 864.920.7129 CH2MHILL Extension 77540 [email protected]<mailto:[email protected]> From: Sprinklerforum [mailto:[email protected]] On Behalf Of James Litvak Sent: Tuesday, May 10, 2016 1:44 PM To: [email protected]<mailto:[email protected]> Subject: Class I Standpipe Hose Valve Location IFC (2012) 905.4.1 requires hose valves to be on intermediate landings, unless approved otherwise. NFPA 14 (2010) 7.3.2 requires hose valves to be on the main landing, unless required otherwise, per 7.3.2.1. The IFC specifically references NFPA 14-10 for 905.4.2, but not 905.4.1. My question is, when both documents are referenced as adopted standards, with no exceptions mentioned, which document takes precedence? James Litvak
_______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org