They did change it back to the intermediate landings in the 2013 edition of
14, FYI...


Benjamin Young

On Tue, May 10, 2016 at 2:27 PM, Kylie Kelly <
[email protected]> wrote:

> The installation of standpipes are per Section 905 *and* NFPA 14.  Where
> there is a conflict between the two, the model code provisions apply.
> Either way, the AHJ should be consulted on the location preferred.
>
>
>
> *102.7.1 Conflicts. *Where conflicts occur between provisions
>
> of this code and referenced codes and standards, the
>
> provisions of this code shall apply.
>
> *102.7.2 Provisions in referenced codes and standards.*
>
> Where the extent of the reference to a referenced code or
>
> standard includes subject matter that is within the scope of
>
> this code, the provisions of this code, as applicable, shall
>
> take precedence over the provisions in the referenced code
>
> or standard.
>
>
>
> *905.2 Installation standard. *Standpipe systems shall be
>
> installed in accordance with this section and NFPA 14.
>
>
>
> *From:* Sprinklerforum [mailto:
> [email protected]] *On Behalf Of *
> [email protected]
> *Sent:* Tuesday, May 10, 2016 11:03 AM
> *To:* [email protected]
> *Subject:* RE: Class I Standpipe Hose Valve Location
>
>
>
> 905.4 (1) - intermediate level for hose valves, Unless Otherwise Approved.
>
>  NFPA 14 - 7.3.2 (1) at main floor landings OR
>
> 7.3.2.1 allows connection on intermediate landings where required by the
> AHJ.
>
>
>
> Regardless of whether or not the specific paragraph mentions NFPA 14, NFPA
> 14 is the adopted Standard for Standpipes per the Code per 905.2.
>
>
>
> This is one item that I make the call to the local FD and find out what
> the local preference will be.  No point in guessing.
>
>
>
>
> *Craig L. Prahl*
> Fire Protection Group Lead/SME
> *CH2M*
> 200 Verdae Blvd.
> Greenville, SC  29607
> Direct - 864.920.7540
>
> Fax - 864.920.7129
>
> CH2MHILL Extension  77540
> [email protected]
>
>
>
> *From:* Sprinklerforum [
> mailto:[email protected]
> <[email protected]>] *On Behalf Of *James
> Litvak
> *Sent:* Tuesday, May 10, 2016 1:44 PM
> *To:* [email protected]
> *Subject:* Class I Standpipe Hose Valve Location
>
>
>
> IFC (2012) 905.4.1 requires hose valves to be on intermediate landings,
> unless approved otherwise. NFPA 14 (2010) 7.3.2 requires hose valves to be
> on the main landing, unless required otherwise, per 7.3.2.1. The IFC
> specifically references NFPA 14-10 for 905.4.2, but not 905.4.1.
>
>
>
> My question is, when both documents are referenced as adopted standards,
> with no exceptions mentioned, which document takes precedence?
>
>
>
>
>
> James Litvak
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to