To reiterate:  If you have any doubt about what the serving fire department 
wants or prefers, contact them for direction.

Steve

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Ben Young
Sent: Tuesday, May 10, 2016 3:08 PM
To: [email protected]
Subject: Re: Class I Standpipe Hose Valve Location

They did change it back to the intermediate landings in the 2013 edition of 14, 
FYI...


Benjamin Young

On Tue, May 10, 2016 at 2:27 PM, Kylie Kelly 
<[email protected]<mailto:[email protected]>> 
wrote:
The installation of standpipes are per Section 905 and NFPA 14.  Where there is 
a conflict between the two, the model code provisions apply.  Either way, the 
AHJ should be consulted on the location preferred.

102.7.1 Conflicts. Where conflicts occur between provisions
of this code and referenced codes and standards, the
provisions of this code shall apply.
102.7.2 Provisions in referenced codes and standards.
Where the extent of the reference to a referenced code or
standard includes subject matter that is within the scope of
this code, the provisions of this code, as applicable, shall
take precedence over the provisions in the referenced code
or standard.

905.2 Installation standard. Standpipe systems shall be
installed in accordance with this section and NFPA 14.

From: Sprinklerforum 
[mailto:[email protected]<mailto:[email protected]>]
 On Behalf Of [email protected]<mailto:[email protected]>
Sent: Tuesday, May 10, 2016 11:03 AM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Class I Standpipe Hose Valve Location

905.4 (1) - intermediate level for hose valves, Unless Otherwise Approved.
 NFPA 14 - 7.3.2 (1) at main floor landings OR
7.3.2.1 allows connection on intermediate landings where required by the AHJ.

Regardless of whether or not the specific paragraph mentions NFPA 14, NFPA 14 
is the adopted Standard for Standpipes per the Code per 905.2.

This is one item that I make the call to the local FD and find out what the 
local preference will be.  No point in guessing.


Craig L. Prahl
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd.
Greenville, SC  29607
Direct - 864.920.7540<tel:864.920.7540>
Fax - 864.920.7129<tel:864.920.7129>
CH2MHILL Extension  77540
[email protected]<mailto:[email protected]>

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of James Litvak
Sent: Tuesday, May 10, 2016 1:44 PM
To: 
[email protected]<mailto:[email protected]>
Subject: Class I Standpipe Hose Valve Location

IFC (2012) 905.4.1 requires hose valves to be on intermediate landings, unless 
approved otherwise. NFPA 14 (2010) 7.3.2 requires hose valves to be on the main 
landing, unless required otherwise, per 7.3.2.1. The IFC specifically 
references NFPA 14-10 for 905.4.2, but not 905.4.1.

My question is, when both documents are referenced as adopted standards, with 
no exceptions mentioned, which document takes precedence?


James Litvak

_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to