If the sprinklers are 18' apart or 9' off of walls, then 5 x 324 SF would be 
correct.



Steve


-------- Original message --------
From: Travis Mack <[email protected]>
Date: 6/27/16 6:22 PM (GMT-08:00)
To: [email protected]
Subject: Re: EXTENDED COVERAGE SPRINKLERS

You are reading wrong. You need to calculate 5 ex  COV sprinklers at a minimum. 
You don't have to do 5x324. If they only cover 1400 sq ft for whatever reason 
so be it. You still calc 5.

Travis Mack, SET
MFP Design, LLC
"Follow" us on Facebook: 
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign

Sent from my iPhone

On Jun 27, 2016, at 6:07 PM, Trillium Fire Sprinkler Design Inc. 
<[email protected]<mailto:[email protected]>> wrote:

I HAVE A 750 SQFT CLASS ROOM. DUE TO THE CONFIGUARTION OF THE LIGHTS AND A FEW 
BUMP OUTS IN THE WALLS. I NEED TO USE  FIVE   18x18 EC SPRINKLERS.

IF I READ THE CODE CORRECTLY. I NEED TO CALCULATE 5 TIMES 324 SQFT. WHICH IS 
1620 SQFT.  WONDERING IF I AM READING THIS RIGHT?

I DON'T SEE THE ADVANTAGE WHEN I CAN USE 7 STANDARD Q.R. SPRINKLERS TO COVER 
THE SAME ROOM. 11' CEILINGS MY DESIGN AREA WOULD ONLY BE 923 SQFT.

AM I MISSING SOMETHING?

THANKS