The explanation on page 598 of the handbook 2013 is a bit confusing. I was always under the impression 5 sprinklers. But once I read it again. it does say if you don`t meet the criteria of 11.2.3.2.3 .
thanks for the help. From: Sprinklerforum [mailto:[email protected]] On Behalf Of Travis Mack Sent: June-27-16 9:23 PM To: [email protected] Subject: Re: EXTENDED COVERAGE SPRINKLERS You are reading wrong. You need to calculate 5 ex COV sprinklers at a minimum. You don't have to do 5x324. If they only cover 1400 sq ft for whatever reason so be it. You still calc 5. Travis Mack, SET MFP Design, LLC "Follow" us on Facebook: <https://www.facebook.com/pages/MFP-Design-LLC/92218417692> https://www.facebook.com/pages/MFP-Design-LLC/92218417692 Send large files to MFP Design via: https://www.hightail.com/u/MFPDesign Sent from my iPhone On Jun 27, 2016, at 6:07 PM, Trillium Fire Sprinkler Design Inc. <[email protected]> wrote: I HAVE A 750 SQFT CLASS ROOM. DUE TO THE CONFIGUARTION OF THE LIGHTS AND A FEW BUMP OUTS IN THE WALLS. I NEED TO USE FIVE 18x18 EC SPRINKLERS. IF I READ THE CODE CORRECTLY. I NEED TO CALCULATE 5 TIMES 324 SQFT. WHICH IS 1620 SQFT. WONDERING IF I AM READING THIS RIGHT? I DON'T SEE THE ADVANTAGE WHEN I CAN USE 7 STANDARD Q.R. SPRINKLERS TO COVER THE SAME ROOM. 11' CEILINGS MY DESIGN AREA WOULD ONLY BE 923 SQFT. AM I MISSING SOMETHING? THANKS _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org