If they cover less, then you still have to do the minimum area.

Keep this simple. 5 sprinklers minimum. If the 5 sprinklers doesn't get your total area using the density/area curve, then add sprinklers until you get there.

Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]

http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign
LinkedIn: https://www.linkedin.com/in/travismack

On 6/27/2016 6:43 PM, Trillium Fire Sprinkler Design Inc. wrote:

what if the 5 ec sprinklers cover less than 900 sqft or in this case since 11`ceilings 923 sqft

*From:*Sprinklerforum [mailto:[email protected]] *On Behalf Of *Trillium Fire Sprinkler Design Inc.
*Sent:* June-27-16 9:38 PM
*To:* [email protected]
*Subject:* RE: EXTENDED COVERAGE SPRINKLERS

its say on page 598n 2013 handbook. ``if the reduction of area is applicable such as that the minimum area density area was 900 sqft, then the 1280 sqft area would be required.`` according to 11.2.3.2.2.3

*From:*Sprinklerforum [mailto:[email protected]] *On Behalf Of *Steve Leyton
*Sent:* June-27-16 9:30 PM
*To:* [email protected] <mailto:[email protected]>
*Subject:* RE: EXTENDED COVERAGE SPRINKLERS

If the sprinklers are 18' apart or 9' off of walls, then 5 x 324 SF would be correct.

Steve

-------- Original message --------

From: Travis Mack <[email protected] <mailto:[email protected]>>

Date: 6/27/16 6:22 PM (GMT-08:00)

To: [email protected] <mailto:[email protected]>

Subject: Re: EXTENDED COVERAGE SPRINKLERS

You are reading wrong. You need to calculate 5 ex COV sprinklers at a minimum. You don't have to do 5x324. If they only cover 1400 sq ft for whatever reason so be it. You still calc 5.

Travis Mack, SET

MFP Design, LLC

"Follow" us on Facebook: https://www.facebook.com/pages/MFP-Design-LLC/92218417692

Send large files to MFP Design via:

https://www.hightail.com/u/MFPDesign

Sent from my iPhone


On Jun 27, 2016, at 6:07 PM, Trillium Fire Sprinkler Design Inc. <[email protected] <mailto:[email protected]>> wrote:

    I HAVE A 750 SQFT CLASS ROOM. DUE TO THE CONFIGUARTION OF THE
    LIGHTS AND A FEW BUMP OUTS IN THE WALLS. I NEED TO USE  FIVE
      18x18 EC SPRINKLERS.

    IF I READ THE CODE CORRECTLY. I NEED TO CALCULATE 5 TIMES 324
    SQFT. WHICH IS 1620 SQFT.  WONDERING IF I AM READING THIS RIGHT?

    I DON'T SEE THE ADVANTAGE WHEN I CAN USE 7 STANDARD Q.R.
    SPRINKLERS TO COVER THE SAME ROOM. 11' CEILINGS MY DESIGN AREA
    WOULD ONLY BE 923 SQFT.

    AM I MISSING SOMETHING?

    THANKS

    _______________________________________________
    Sprinklerforum mailing list
    [email protected]
    <mailto:[email protected]>
    http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to