Here is another way to approach this. You say you can protect the room with 7 standard coverage sprinklers and then calc a 923 sq.ft. area which would probably result in smaller pipe size than using E.C. heads. I have found that sometimes going this route is more efficient from a pipe size standpoint. It may not always be about saving heads.
Either way, with EC, you always calc a minimum of 5. Lamar Vaughn,SET On Mon, Jun 27, 2016 at 9:07 PM, Trillium Fire Sprinkler Design Inc. < [email protected]> wrote: > I HAVE A 750 SQFT CLASS ROOM. DUE TO THE CONFIGUARTION OF THE LIGHTS AND A > FEW BUMP OUTS IN THE WALLS. I NEED TO USE FIVE 18x18 EC SPRINKLERS. > > > > IF I READ THE CODE CORRECTLY. I NEED TO CALCULATE 5 TIMES 324 SQFT. WHICH > IS 1620 SQFT. WONDERING IF I AM READING THIS RIGHT? > > > > I DON'T SEE THE ADVANTAGE WHEN I CAN USE 7 STANDARD Q.R. SPRINKLERS TO > COVER THE SAME ROOM. 11' CEILINGS MY DESIGN AREA WOULD ONLY BE 923 SQFT. > > > > AM I MISSING SOMETHING? > > > > THANKS > > > > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > > -- Lamar Vaughn Vaughn & Company 678-429-3563