Here is another way to approach this. You say you can protect the room with
7 standard coverage sprinklers and then calc a 923 sq.ft. area which would
probably result in smaller pipe size than using E.C. heads. I have found
that sometimes going this route is more efficient from a pipe size
standpoint. It may not always be about saving heads.

Either way, with EC, you always calc a minimum of 5.

Lamar Vaughn,SET

On Mon, Jun 27, 2016 at 9:07 PM, Trillium Fire Sprinkler Design Inc. <
[email protected]> wrote:

> I HAVE A 750 SQFT CLASS ROOM. DUE TO THE CONFIGUARTION OF THE LIGHTS AND A
> FEW BUMP OUTS IN THE WALLS. I NEED TO USE  FIVE   18x18 EC SPRINKLERS.
>
>
>
> IF I READ THE CODE CORRECTLY. I NEED TO CALCULATE 5 TIMES 324 SQFT. WHICH
> IS 1620 SQFT.  WONDERING IF I AM READING THIS RIGHT?
>
>
>
> I DON'T SEE THE ADVANTAGE WHEN I CAN USE 7 STANDARD Q.R. SPRINKLERS TO
> COVER THE SAME ROOM. 11' CEILINGS MY DESIGN AREA WOULD ONLY BE 923 SQFT.
>
>
>
> AM I MISSING SOMETHING?
>
>
>