Well, I guess it's time to jump in here.   For the record, I spent the first 
14+ years of my career in contracting but the past 21 have been as a design 
consultant.  I still and will always consider myself a "sprinkie" but the fact 
is that I'm the A/E.   But I'm proud of my firm's reputation for competence and 
I've trained our staff and tried to maintain a corporate culture where we're 
not "that guy".   Our work is 75+% A/E with architect and developer clients; 
about 15% of our revenues come from sprinkler contractors for whom we work as a 
subconsultant and about 10% of our work is specialty consulting, MIC and other 
impairments.    So I think that I have a pretty good perspective on all of this.

Mike hits the nail squarely with regard to the ridiculous timing and lack of 
lead times afforded the sprinkler contractor to design on a deferred basis.  In 
fact, I'd say that most developers and general contractors don't give a damn 
about how much work is actually involved in designing a sprinkler and/or 
standpipe system today.   Hold the contract until the last minute, let it and 
then start beating on the sub for submittals.   I've said countless times that 
sprinkler contracting is the dumbest business model in the industry - you take 
on all the liability regardless of the countless variables, you don't receive 
authorization to proceed in a timely manner, you don't get the background files 
and cooperation of the other disciplines in a timely manner (if ever) and all 
of this is a race to get pipe on the job and begin installation of a system 
that is going to have to be squeezed into a building that was design by an 
architect who gave ZERO consideration to the sprinkler syste
 m.  Like, there's not even a riser room.   However, the 200 hours spent on 
interior design of the lobby and public restrooms will look fantastic ...

When I started my firm, I vowed to be part of the solution and not the problem. 
 To that end we have created a business model that considers contracting 
practices, the requirements of the AHJs, the need for real and sincere 
partnering with our installing contractors and of course, the commitment to 
code-compliance and constructable designs.   We serve as Engineer of Record 
(EOR) on mostly public projects: we have two agencies in California that do not 
allow deferred submittals so architects in fact do have to undertake the design 
and coordination "up front".   This is of no value is the EOR isn't competent 
and many of the architects in our markets are regressive regarding sprinklers 
and go with the lowest of the low prices they can find.   Our firm charges a 
lot more than what sprinkler contractors or many of our ME competitors do, but 
we firmly believe that our work speaks for itself and we have clients using us 
voluntarily on private projects now because they've learned the
  value of our services.  We currently have 3 retail projects and a large 
warehouse campus where we're doing full design packages that will be bid and 
installed as "plans and specs" instead of deferred.   We also displace the 
civil engineer as EOR for private site fire main system improvements on many 
projects so now we own the entire design from the property lines in.   We 
follow the projects from conceptual design through final acceptance testing and 
we work as advocates for both the owner and the installers.  Yes it's a fine 
line and yes, to a degree it's fence sitting.  But, it's starting to get 
traction.

Coordination of a sprinkler system is critical.  An early-phase design doesn't 
offset the need to coordinate trades on a construction team.  When we design a 
system and obtain approval and permit, it establishes the basis of design for 
that system.  We include a set of coordination notes on all of our documents 
that lay out the intent: use these documents as your base files to create 
coordinated shop drawings with the design team.  Those notes outline that the 
exact elevation of piping, the exact horizontal location of piping, the lengths 
of hangers, sprigs and pendent drops are all subject to change and final 
verification by the installing contractor.  We specify materials as a basis but 
if you want to use a different equivalent sprinkler or coupling, the notes and 
spec's afford you the option of processing "no cost" change orders for 
substitutions.   We furnish CAD files to the installing contractor so the 
approved design can be detailed for fabrication.  We review the coor
 dinated shop drawings and run new calc's if there are significant changes to 
be sure that the basis of design is intact.   Anyone with a passing knowledge 
of hydraulics should know that if you have to arm some sprinklers over off of a 
line that doesn't have arm-overs, the system demand actually goes down because 
the overflow is reduced by lowering the net K-factor of the drops.   We try to 
inform the inspectors and other stakeholders of where changes are impactful or 
not.  We work hand-in-hand with our installers to assure to the greatest extent 
possible that they can prosecute the approved design without radical changes.

But if there are changes to the approved basis of design (perhaps because of a 
conflict or omission on our part), we process those construction changes with 
the AHJ and we solicit a fair additive CO from the contractor.  I like to think 
that we are the installer's best friend on the project because we're very fair 
when it comes to assessing when an additive CO is in order.  But the 
contracting community has to remember that there are two aspects to a CO: 
entitlement and value.   If our contractors are partnered on the project, it 
goes smoothly but if not ...

Just because you're entitled to a CO, it doesn't mean you get paid list price 
and Means labor for the work.    We tell all of our installing subs (if we're 
working with them for the first time), "We can be your best friend or worst 
enemy on this project."    Don't eff with us on cutting or lengthening hanger 
rods unless the entire project has had to be reconfigured.  Don't charge us $25 
for a 2" grooved ell.  Don't try to tell us it took 24 hours to add 2 sway 
braces - the crap we've seen the past 3 or 4 years is just awesome.    And 
here's the really important part:  when you're doing your shop drawings, DON'T 
change the design just because.   We've seen contractors completely redesign 
the work because they want to save a few sprinklers.  Guess what?  You don't 
get to do that.  You bid the work, you detail the work, you install the work 
and there are almost always very good reasons why a design looks a certain way, 
even if it's not the cheapest solution.

We're now drawing in 3D, along with the other disciplines and architect on the 
design team.  The number of conflicts in the field on our latest projects has 
dropped while the overall quality of our design product continues to rise.   
Dramatically.    And I'm proud of that and committed to being the BEST 3rd 
party design firm in the markets we serve.  But I also understand that we're 
the exception and that probably 85% or more of the EORs who oversee fire 
protection work are uninformed asshats.    And I LOVE that because we're 
getting new clients every few weeks who, after a couple projects, are telling 
us how glad they are that the finally found a service provider who can do 
viable designs and get them built.  I'll take some credit for that but we still 
rely on the proactive and professional intent of our contractor partners.  If 
you go into a project assuming the worst, you'll get contention.  If you go in 
open-minded, I've got your back because the faster that project gets 
 completed as closely as possible to the approved plans, the better we all do 
and we're in that part of it together.  

Steve L.

-----Original Message-----
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Justin Stewart
Sent: Thursday, July 14, 2016 10:17 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Change Orders 

I believe if you have to have a sprinkler system. The A/E should be required to 
do the shop drawings and everything so it will be coordinated a little better 
and they can overlay it with their drawings. 

Sent from my iPhone

> On Jul 14, 2016, at 10:55 AM, Rocci Cetani 3 <roc...@norcalfire.com> wrote:
> 
> Glad to see we aren't the only company dealing with the EXACT same 
> issue.......how long is it going to take before architects/builders 
> realize they need to get sprinkler contractors involved a lot earlier 
> in the process.
> 
> Rocci Cetani III, CET
> Designer
> Water-Based Fire Protections Systems Layout, Nicet Level III
> 
> Northern California Fire Protection Services Inc.
> 16840 Joleen Way Bldg. A
> Morgan Hill, CA 93037
> P-(408) 776-1580 EXT.111
> F-(408) 776-1590
> 
> 
> roc...@norcalfire.com
> www.norcalfire.com
> 
> CONFIDENTIALITY NOTICE: This message and any document accompanying it 
> may contain confidential information belonging to the sender. The 
> information is intended only for the use of individual or entity named 
> above. If you are not the intended recipient, or the employee or agent 
> responsible to deliver this message to the intended recipient, you are 
> hereby notified that any disclosure, copying or taking of any action 
> in reliance on the contents of this information is strictly 
> prohibited. If you have received this transmission in error, please 
> immediately notify us by telephone to arrange for return of the documents.
> 
> 
> -----Original Message-----
> From: Sprinklerforum 
> [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
> On Behalf Of Michael Hill
> Sent: Thursday, July 14, 2016 8:42 AM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: RE: Change Orders
> 
> I once had an A/E argue with me about coordination on a project and 
> told me to just go by his coordinated plans. I told my installer to go 
> get a core driller, I then pointed to a spot on the exterior wall and said I 
> need a 6"
> hole right there. The A/E asked why the hell I needed a hole there, so 
> I explained since the existing building is actually 6' to 8' shorter 
> than what he claims (depending on which dimensions you use), that I 
> need to install this "coordinated" piping out there. We never saw that guy 
> again.
> 
> The problem today, as I see it, is everything is driven by time. 
> Contractors agree to ridiculous 4 week schedules not realizing (or 
> perhaps they do) that sprinkler plan review takes 2-3 weeks and you 
> have to wait another 2-3 weeks for your scheduled hydro. Oh, they 
> release on the project 2 weeks in after they realize sprinklers are in 
> the way of the new walls. It is a struggle to maintain quality control 
> when you are always trying to catch up. I am guessing this happens 
> with all aspects of the construction industry from initial 
> architectural design all the way through construction and 
> installation. Our industry is unique. Most other trades can work off 
> of the approved building plans and permit, not so for sprinkler and 
> alarm, we are required to generate our own drawings and apply for 
> separate permits. This is exactly how it should be. Would sure be nice 
> if construction didn't start until ALL permits were obtained. It 
> amazes me how many times contractors get a demo permit and go so far 
> as to have all the walls one sided with drywall and all the other 
> trades roughed in before the building permit has been issued and then 
> scream up and down how sprinkler is holding them up. Yet, I still 
> can't even submit my plans because they do not have an approved building 
> permit, which is the very first thing the AHJ checks when we submit our 
> application.
> 
> Of course there are exceptions to everything and not all contractors 
> are ruthless, but it is harder to find the good ones.
> 
> Anyone else been in this industry long enough to remember when it was fun?
> Fun is not how I would describe the last 6-8 years.
> 
> Mike Hill
> 
> 
> -----Original Message-----
> From: Sprinklerforum 
> [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
> On Behalf Of Justin Stewart
> Sent: Thursday, July 14, 2016 11:04 AM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: Re: Change Orders
> 
> Michael,
> 
> You hit the nail on the head I was just kind of curious if it was just 
> us that had that issue and if I was missing something.  I have also 
> had a GC recently tell me well your designer should have caught that 
> and asked the A/E. I went as far as going back through the entire bid 
> documents and found the issue and called the mechanical engineer 
> himself and he didn't really tell me why there were so many conflicts 
> on this project until I told him I was in school for mechanical 
> engineering as well and just wanted to learn how to avoid these kind 
> of issues. Long story short he told me it was the structural engineer and no 
> one overlays anything anymore.
> 
> Sent from my iPhone
> 
>> On Jul 14, 2016, at 9:40 AM, Michael Hill <mi...@phoenixfp.net> wrote:
>> 
>> In our recent experience, it doesn't matter if you get an approved 
>> change order or not. The GC just refuses to pay for it at the end of 
>> the project claiming they couldn't get it approved by the building owner.
>> 
>> In general, it has to be determined why the sprinkler pipe is in 
>> conflict with other trades. If there is any chance that the sprinkler 
>> company is at fault you may as well move the pipe. It usually isn't 
>> worth ruining a relationship with a contractor over it. If it is 
>> solely someone else's fault AND a substantial amount of work to 
>> correct then we would pursue a change order and would not do any work 
>> until it was approved. Small changes are just made next time we are 
>> on site, usually not worth arguing over, no matter who is at fault.
>> 
>> All the rules are subject to change from project to project and from 
>> GC to GC.
>> 
>> Mike Hill
>> 
>> -----Original Message-----
>> From: Sprinklerforum
>> [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
>> On Behalf Of Justin Stewart
>> Sent: Thursday, July 14, 2016 10:00 AM
>> To: sprinklerforum@lists.firesprinkler.org
>> Subject: Change Orders
>> 
>> I am just curious how everyone else in the fire sprinkler industry 
>> deals with change orders. For example, everything for a project is 
>> prefabricated besides the return bends. Say you have an issue with 
>> the HVAC and your main has to be moved how do you go about that? Do 
>> you
> request for a change order?
>> Even if in your quote you have a clause stating after material has 
>> been ordered anything extra for moving pipe is an extra to the 
>> contract
> amount.
>> Does this fall under coordination? Thank you very much for any 
>> replies in advance.
>> 
>> Sent from my iPhone
>> _______________________________________________
>> Sprinklerforum mailing list
>> Sprinklerforum@lists.firesprinkler.org
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
>> l
>> er.org
>> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> Sprinklerforum@lists.firesprinkler.org
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
>> l
>> er.org
> 
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
> 
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to