Craig,
Is it possible to tell if any area, height, or travel distances for
sprinklers been taken?
I think your path would be where 13 specifies all areas must be sprinklers
unless specifically omitted. So you have the areas you would normally
exclude if they meet the specified criteria in 13 or if the jurisdiction
has a specific ordinance allowing you leave an area unprotected. Seattle
used to have a life safety provision for retrofit of hotels and group homes
where you just sprinklered the hllls and ran a head into each unit over the
door.

On Wednesday, July 27, 2016, Parsley Consulting <[email protected]>
wrote:

> Craig,
>     I don't know where that exists, however my concern would be that
> you'll still need to establish a standard for design, including coverage
> areas, calculations, materials, and on and on.  I haven't done anything
> like that in more than a decade so I'd be interested to see what you come
> up with.
>
> *Ken Wagoner, SET Parsley Consulting*
>
>
>
> * 350 West 9th Avenue, Suite 206 Escondido, California 92025 Phone
> 760-745-6181 <760-745-6181> Visit our website
> <http://www.parsleyconsulting.com/> *
> On 07/27/2016 2:58 PM, [email protected] wrote:
>
> Somewhere within NFPA 13 I recall seeing a statement which says basically
> that if you install a system voluntarily (not required by Code) it must
> still be installed per the NFPA Standard.
>
>
>
> Anyone know where that is, I’ve hunted all over and can’t find it within
> either the 2010 or 2013 NFPA 13 editions.
>
>
>
>
> *Craig L. Prahl*
> Fire Protection Group Lead/SME
> *CH2M*
> 200 Verdae Blvd.
> Greenville, SC  29607
> Direct - 864.920.7540
>
> Fax - 864.920.7129
>
> CH2MHILL Extension  77540
> [email protected]
>
>
>
> _______________________________________________
> Sprinklerforum mailing 
> [email protected]http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
>
>

-- 
Sent from Gmail Mobile

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to