No building code is the kicker here. Where ICC gives you IBC, IRC & IFC as
the basic building code/safety code/maintenance code grouping NFPA gives
you 1, 101 & 5000. What do they use in this secret location as a building
code for stuff not necessarily life safety? Does every little structure
need to be fully engineered?

On Thu, Jul 28, 2016 at 5:45 AM, <[email protected]> wrote:

> Well here’s the kicker, since the LSC is the prevailing Building Code and
> the LSC does not require sprinklers, NFPA 13 is irrelevant as far as
> mandatory compliance.  Also in this part of the country State law allows
> the owner to act as the AHJ on their property if there is no local
> municipal AHJ. Do you see why I’m having so much fun with this one?
>
>
>
> 13 doesn’t direct what occupancies get sprinklered, that’s the building or
> fire code or in this case the Life Safety Code.  The LSC allows the
> occupancy in question to be constructed with no sprinkler requirement.  My
> guess is that this was an internal Safety Group directive by someone who
> felt sprinklers would be beneficial in the warehouse part of the building
> only but who also had no real knowledge of installations or requirements
> and the contractor just did as he was asked.  There is no documentation and
> no one on the site from when this work was done.
>
>
>
> So the best I can come up with are recommendations for their consideration
> but they are not constrained by any laws or codes to take any of the
> recommendations.
>
>
>
> Personally I do love the fact that this is an area where you are not
> constrained by a million laws regulating every aspect of your life but from
> a code study and analysis standpoint, it creates a real challenge.
>
>
>
> Thanks to all for the ideas, thoughts and recommendations,
>
>
> *Craig L. Prahl*
> Fire Protection Group Lead/SME
> *CH2M*
> 200 Verdae Blvd.
> Greenville, SC  29607
> Direct - 864.920.7540
>
> Fax - 864.920.7129
>
> CH2MHILL Extension  77540
> [email protected]
>
>
>
> *From:* Sprinklerforum [mailto:
> [email protected]] *On Behalf Of *rongreenman
> .
> *Sent:* Wednesday, July 27, 2016 7:28 PM
> *To:* [email protected]
> *Subject:* Re: Installing non-required systems [EXTERNAL]
>
>
>
> I think your path would be where 13 specifies all areas must be sprinklers
> unless specifically omitted. So you have the areas you would normally
> exclude if they meet the specified criteria in 13 or if the jurisdiction
> has a specific ordinance allowing you leave an area unprotected. Seattle
> used to have a life safety provision for retrofit of hotels and group homes
> where you just sprinklered the hllls and ran a head into each unit over the
> door.
>
>
> On Wednesday, July 27, 2016, Parsley Consulting <[email protected]>
> wrote:
>
> Craig,
>     I don't know where that exists, however my concern would be that
> you'll still need to establish a standard for design, including coverage
> areas, calculations, materials, and on and on.  I haven't done anything
> like that in more than a decade so I'd be interested to see what you come
> up with.
>
>
>
>
>
>
> *Ken Wagoner, SET Parsley Consulting 350 West 9th Avenue, Suite 206
> Escondido, California 92025 Phone 760-745-6181 <760-745-6181> Visit our
> website <http://www.parsleyconsulting.com/> *
>
> On 07/27/2016 2:58 PM, [email protected] wrote:
>
> Somewhere within NFPA 13 I recall seeing a statement which says basically
> that if you install a system voluntarily (not required by Code) it must
> still be installed per the NFPA Standard.
>
>
>
> Anyone know where that is, I’ve hunted all over and can’t find it within
> either the 2010 or 2013 NFPA 13 editions.
>
>
>
>
> *Craig L. Prahl*
> Fire Protection Group Lead/SME
> *CH2M*
> 200 Verdae Blvd.
> Greenville, SC  29607
> Direct - 864.920.7540
>
> Fax - 864.920.7129
>
> CH2MHILL Extension  77540
> [email protected]
>
>
>
> _______________________________________________
>
> Sprinklerforum mailing list
>
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
>
>
>
>
> --
> Sent from Gmail Mobile
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
>


-- 
Ron Greenman

4110 Olson Dr., NW
Gig Harbor, WA 98335

[email protected]

253.576.9700

A problem well stated is a problem half solved. -Charles F. Kettering,
inventor and engineer (1876-1958)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to