You need 30 gpm at the sprinklers in the paint booth duct. That is a lot of pressure with a 5.6K sprinkler. So that would be one reason for the larger threads....larger orifice...lower starting pressure.

Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]

http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign
LinkedIn: https://www.linkedin.com/in/travismack

On 8/9/2016 2:48 PM, Douglas Hicks wrote:
OK to change the topic a bit. 1. I have noticed that some duct, plenum. and work spaces have 3/4 “ threads, which I assume is ELO. And some do not have ELO heads. Why?
*From:* [email protected] <mailto:[email protected]>
*Sent:* Tuesday, August 09, 2016 2:27 PM
*To:* [email protected] <mailto:[email protected]>
*Subject:* RE: Paint spray application

You’re welcomed to install how you see fit but spraying inside a duct is a lot different than out in a room or on a dock.

It’s a comparison of apples to elephants.

You have no issues or concersn about whether or not the water spray can reach the other side of the duct or whether or not heat will collect and set it off in such a confined space. So if you install it at 3 o’clock, 9 o’clock or 12 o’clock it really doesn’t matter as far as discharge is concerned.

Rooms and space rules have no application inside a piece of ductwork.


*Craig L. Prahl**
*Fire Protection Group Lead/SME
*CH2M*
200 Verdae Blvd.
Greenville, SC  29607
Direct - 864.920.7540

Fax - 864.920.7129

CH2MHILL Extension  77540
[email protected]

*From:*Sprinklerforum [mailto:[email protected]] *On Behalf Of *IPA
*Sent:* Tuesday, August 09, 2016 5:18 PM
*To:* [email protected]
*Subject:* Re: Paint spray application [EXTERNAL]

I don't find the lack of an orientation in 22.4.2 a compelling enough reason to install it horizontally especially since 3.6.2.3 states that pendant sprinklers are to spray water 'downward against the deflector.' The old dry pendant at the dock scenario at least has it at a 45 degree angle but not horizontal.

On Tue, Aug 9, 2016 at 1:47 PM, <[email protected] <mailto:[email protected]>> wrote:

    Inside a duct no matter the orientation, the sprinkler sees the
    same shape and the discharge will more than adequately cover the
    small space.

    Look at 22.4.2 in 2013 edition of 13.

    Orientation is not specified.  Now you might pick a location based
    on drainage or other factors.  But there is no specific NFPA
    constraint.


    *Craig L. Prahl**
    *Fire Protection Group Lead/SME
    *CH2M*
    200 Verdae Blvd.
    Greenville, SC  29607
    Direct - 864.920.7540 <tel:864.920.7540>

    Fax - 864.920.7129 <tel:864.920.7129>

    CH2MHILL Extension  77540
    [email protected] <mailto:[email protected]>

    *From:*Sprinklerforum
    [mailto:[email protected]
    <mailto:[email protected]>] *On
    Behalf Of *IPA
    *Sent:* Tuesday, August 09, 2016 2:28 PM
    *To:* [email protected]
    <mailto:[email protected]>
    *Subject:* Re: Paint spray application [EXTERNAL]

    So, where is the code section that says pendant sprinklers can be
    installed in any orientation in ducts? I've just scoured '13 and
    can't find it.

    On Tue, Aug 9, 2016 at 11:26 AM, Bob <[email protected]
    <mailto:[email protected]>> wrote:

        Brad,

        It’s all good.  I tend to agree with the QR on small booths.
        Especially since we are calc’ing for the worst case that all
        sprinklers will flow anyway.  Seems that opening faster would
        be a good idea, but then again I’m not an engineer, just a guy
        who draws lots of lines and circles.

        Thank you,

        Bob Knight, CET III

        208-318-3057 <tel:208-318-3057>

        *From:*Sprinklerforum
        [mailto:[email protected]
        <mailto:[email protected]>] *On
        Behalf Of *Brad Casterline
        *Sent:* Tuesday, August 09, 2016 12:21 PM
        *To:* [email protected]
        <mailto:[email protected]>;
        [email protected] <mailto:[email protected]>


        *Subject:* RE: Paint spray application

        Yes indeed.
        I knew as soon as I hit send it was a bad idea.
        I have thought for several years there should be an exception
        for no QR in EH, ever since I understood the reasoning.
        I should have more soberly made my point that I think small
        paint booths are an excellent application -- if you calc all
        heads flowing why not use low temp QR? It would be the next
        best thing to open head deluge, would it not?
        And I apologize for the name calling and meaness of spirit,
        FWIW. There is no excuse for that. A big part of how I feel
        about myself is based on how i act on this Forum.

        Thanks,
        Brad

        On Aug 9, 2016 1:02 PM, "Bob" <[email protected]
        <mailto:[email protected]>> wrote:

        I have an example of one that I did in Salt Lake recently. It
        has 144 sprinklers in it. This counts all the exhaust ducts
        and stacks plus the ceiling sprinklers.

        Thank you,

        Bob Knight, CET III

        208-318-3057 <tel:208-318-3057>

        *From:*Sprinklerforum
        [mailto:[email protected]
        <mailto:[email protected]>] *On
        Behalf Of *[email protected] <mailto:[email protected]>
        *Sent:* Tuesday, August 09, 2016 6:29 AM
        *To:* [email protected]
        <mailto:[email protected]>
        *Subject:* RE: Paint spray application

        How many example of industrial spray booths with more than 40
        heads would you like Brad?  They exist and are not all that rare.


        *Craig L. Prahl**
        *Fire Protection Group Lead/SME
        *CH2M*
        200 Verdae Blvd.
        Greenville, SC 29607
        Direct - 864.920.7540 <tel:864.920.7540>

        Fax - 864.920.7129 <tel:864.920.7129>

        CH2MHILL Extension  77540
        [email protected] <mailto:[email protected]>

        *From:*Sprinklerforum
        [mailto:[email protected]] *On
        Behalf Of *Brad Casterline
        *Sent:* Monday, August 08, 2016 8:39 PM
        *To:* [email protected]
        <mailto:[email protected]>
        *Subject:* RE: Paint spray application [EXTERNAL]

        Show me a spray booth with forty sprinklers Steve

        On Aug 8, 2016 7:36 PM, "Steve Leyton"
        <[email protected]
        <mailto:[email protected]>> wrote:

            Sure. And fires that can be spread by running fuel such as
            plastics and FCL’s (not to mention BLEVE’s) can set off 40
            standard response sprinklers in a minute.   I can only
            imagine the sheer volume of responding sprinklers and
            skipping that could occur based on how smooth or bumpy the
            roof/ceiling assembly is if you started wantonly plugging
            QR control-mode sprinklers into EH fires.   (On paper) MDD
            = .80    ADD = .275

            My opinion only,

            Steve L.

            *From:*Sprinklerforum
            [mailto:[email protected]
            <mailto:[email protected]>]
            *On Behalf Of *Brad Casterline
            *Sent:* Monday, August 08, 2016 5:17 PM
            *To:* [email protected]
            <mailto:[email protected]>
            *Subject:* Re: Paint spray application

            Shakey ground is all i have ever known Ken.
            I am no more a professional than you are.
            THINK MAN!
            small spaces with fast fires need the fastest acting
            sprinklers we can muster.
            I've been in court myself a couple times- neither one over
            sprinklers though--
            please stop being so stodgy!

            On Aug 8, 2016 7:05 PM, "Parsley Consulting"
            <[email protected]
            <mailto:[email protected]>> wrote:

            I don't know, Brad.  You're standing on pretty shaky
            ground there.

            The decision to use QR sprinklers in an extra hazard
            occpuancy is a direct contradiction to 8.4.1.1.2 of NFPA
            13, including the 2016 edition, or a similar section
            number, at least as far back as the 1999 edition. If you
            install QR sprinklers in a space that is legitimately
            classed as an extra hazard occupancy, aren't you directly
            contradicting this particular section of NFPA 13?  The
            handbook provides the following explanatory text on the topic:

            Extra hazard occupancies are characterized by the
            probability of fast-developing fires with high heat
            release rates that have the potential to open a large
            number of quick-response sprinklers before the sprinklers
            have time to control the fire. The operation of a large
            number of sprinklers in a relatively short time period has
            the potential to overtax the system. For this reason,
            quick-response sprinklers using the area
            design method of Chapter 11 are not permitted for the
            protection of extra hazard occupancies. Additional
            perspective on this can be found in the discussion of
            safety margin found in B.2.1.

            Further, I'm not aware of any QR sprinkler which has been
            tested and listed by an NRTL for use in protecting extra
            hazard occupancies. Barring that, to follow the guidance
            you're suggesting the contractor/designer/installer has to
            violate both NFPA 13 AND the listing of the sprinkler. I'm
            not suggesting the gloom and doom drama of "people could
            die", however it does concern me greatly when I read
            suggestions to ignore both texts.

            My thought about that is to make sure your insurance is
            paid up, and have a good lawyer on retainer.  I don't know
            of a good defense while sitting in the witness chair to a
            question similar to, "Are you telling me you ignored the
            applicable law and the manufacturer's recommendations for
            the installation of that sprinkler?"

            When I have nightmares I think about having to answer
            questions similar to that.

            *Ken Wagoner, SET
            Parsley Consulting
            350 West 9th Avenue, Suite 206
            Escondido, California 92025
            Phone 760-745-6181 <tel:760-745-6181>
            Visit our website <http://www.parsleyconsulting.com/> *


            On 08/08/2016 4:17 PM, Brad Casterline wrote:

                We're not suppose to use QR in EH either but I say
                balderdash.
                That is for big open spaces beacase you could have a
                bunch of heads going off way over there when the
                emergency is way over here. Small spaces with fast
                fires are better off if you use low temp qr and calc
                every head possible going off


            _______________________________________________
            Sprinklerforum mailing list
            [email protected]
            <mailto:[email protected]>
            
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


            _______________________________________________
            Sprinklerforum mailing list
            [email protected]
            <mailto:[email protected]>
            
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


        _______________________________________________
        Sprinklerforum mailing list
        [email protected]
        <mailto:[email protected]>
        
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


        _______________________________________________
        Sprinklerforum mailing list
        [email protected]
        <mailto:[email protected]>
        
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


    _______________________________________________
    Sprinklerforum mailing list
    [email protected]
    <mailto:[email protected]>
    http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

------------------------------------------------------------------------
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to