I hate spellchecker too Ron
On Aug 9, 2016 8:51 PM, "rongreenman ." <[email protected]> wrote:

> Sidewalks are not listed for EH. Pendants are. Using pendants is
> considered both standard and best practice in this special application
> where sidewalks are not.
>
> On Tuesday, August 9, 2016, IPA <[email protected]> wrote:
>
>> I just found it amusing that sidewall sprinklers in a duct were
>> pooh-poohed for not being in conformance with the standard by people who
>> advocated using pendants in a horizontal position which apparently is not
>> in conformance with '13 either. :-P
>>
>>
>> On Tue, Aug 9, 2016 at 2:27 PM, <[email protected]> wrote:
>>
>>> You’re welcomed to install how you see fit but spraying inside a duct is
>>> a lot different than out in a room or on a dock.
>>>
>>>
>>>
>>> It’s a comparison of apples to elephants.
>>>
>>>
>>>
>>> You have no issues or concersn about whether or not the water spray can
>>> reach the other side of the duct or whether or not heat will collect and
>>> set it off in such a confined space.  So if you install it at 3 o’clock, 9
>>> o’clock or 12 o’clock it really doesn’t matter as far as discharge is
>>> concerned.
>>>
>>>
>>>
>>> Rooms and space rules have no application inside a piece of ductwork.
>>>
>>>
>>> *Craig L. Prahl*
>>> Fire Protection Group Lead/SME
>>> *CH2M*
>>> 200 Verdae Blvd.
>>> Greenville, SC  29607
>>> Direct - 864.920.7540
>>>
>>> Fax - 864.920.7129
>>>
>>> CH2MHILL Extension  77540
>>> [email protected]
>>>
>>>
>>>
>>> *From:* Sprinklerforum [mailto:sprinklerforum-bounces
>>> @lists.firesprinkler.org] *On Behalf Of *IPA
>>> *Sent:* Tuesday, August 09, 2016 5:18 PM
>>>
>>> *To:* [email protected]
>>> *Subject:* Re: Paint spray application [EXTERNAL]
>>>
>>>
>>>
>>> I don't find the lack of an orientation in 22.4.2 a compelling enough
>>> reason to install it horizontally especially since 3.6.2.3 states that
>>> pendant sprinklers are to spray water 'downward against the deflector.' The
>>> old dry pendant at the dock scenario at least has it at a 45 degree angle
>>> but not horizontal.
>>>
>>>
>>>
>>> On Tue, Aug 9, 2016 at 1:47 PM, <[email protected]> wrote:
>>>
>>> Inside a duct no matter the orientation, the sprinkler sees the same
>>> shape and the discharge will more than adequately cover the small space.
>>>
>>>
>>>
>>> Look at 22.4.2 in 2013 edition of 13.
>>>
>>>
>>>
>>> Orientation is not specified.  Now you might pick a location based on
>>> drainage or other factors.  But there is no specific NFPA constraint.
>>>
>>>
>>>
>>>
>>> *Craig L. Prahl*
>>> Fire Protection Group Lead/SME
>>> *CH2M*
>>> 200 Verdae Blvd.
>>> Greenville, SC  29607
>>> Direct - 864.920.7540
>>>
>>> Fax - 864.920.7129
>>>
>>> CH2MHILL Extension  77540
>>> [email protected]
>>>
>>>
>>>
>>> *From:* Sprinklerforum [mailto:sprinklerforum-bounces
>>> @lists.firesprinkler.org] *On Behalf Of *IPA
>>> *Sent:* Tuesday, August 09, 2016 2:28 PM
>>> *To:* [email protected]
>>> *Subject:* Re: Paint spray application [EXTERNAL]
>>>
>>>
>>>
>>> So, where is the code section that says pendant sprinklers can be
>>> installed in any orientation in ducts? I've just scoured '13 and can't find
>>> it.
>>>
>>>
>>>
>>> On Tue, Aug 9, 2016 at 11:26 AM, Bob <[email protected]> wrote:
>>>
>>> Brad,
>>>
>>> It’s all good.  I tend to agree with the QR on small booths.  Especially
>>> since we are calc’ing for the worst case that all sprinklers will flow
>>> anyway.  Seems that opening faster would be a good idea, but then again I’m
>>> not an engineer, just a guy who draws lots of lines and circles.
>>>
>>>
>>>
>>>
>>>
>>> Thank you,
>>>
>>>
>>>
>>> Bob Knight, CET III
>>>
>>> 208-318-3057
>>>
>>>
>>>
>>> *From:* Sprinklerforum [mailto:sprinklerforum-bounces
>>> @lists.firesprinkler.org] *On Behalf Of *Brad Casterline
>>> *Sent:* Tuesday, August 09, 2016 12:21 PM
>>> *To:* [email protected]; [email protected]
>>>
>>>
>>> *Subject:* RE: Paint spray application
>>>
>>>
>>>
>>> Yes indeed.
>>> I knew as soon as I hit send it was a bad idea.
>>> I have thought for several years there should be an exception for no QR
>>> in EH, ever since I understood the reasoning.
>>> I should have more soberly made my point that I think small paint booths
>>> are an excellent application -- if you calc all heads flowing why not use
>>> low temp QR? It would be the next best thing to open head deluge, would it
>>> not?
>>> And I apologize for the name calling and meaness of spirit, FWIW. There
>>> is no excuse for that. A big part of how I feel about myself is based on
>>> how i act on this Forum.
>>>
>>> Thanks,
>>> Brad
>>>
>>> On Aug 9, 2016 1:02 PM, "Bob" <[email protected]> wrote:
>>>
>>> I have an example of one that I did in Salt Lake recently.  It has 144
>>> sprinklers in it.  This counts all the exhaust ducts and stacks plus the
>>> ceiling sprinklers.
>>>
>>>
>>>
>>> Thank you,
>>>
>>>
>>>
>>> Bob Knight, CET III
>>>
>>> 208-318-3057
>>>
>>>
>>>
>>> *From:* Sprinklerforum [mailto:sprinklerforum-bounces
>>> @lists.firesprinkler.org] *On Behalf Of *[email protected]
>>> *Sent:* Tuesday, August 09, 2016 6:29 AM
>>> *To:* [email protected]
>>> *Subject:* RE: Paint spray application
>>>
>>>
>>>
>>> How many example of industrial spray booths with more than 40 heads
>>> would you like Brad?  They exist and are not all that rare.
>>>
>>>
>>>
>>>
>>> *Craig L. Prahl*
>>> Fire Protection Group Lead/SME
>>> *CH2M*
>>> 200 Verdae Blvd.
>>> Greenville, SC  29607
>>> Direct - 864.920.7540
>>>
>>> Fax - 864.920.7129
>>>
>>> CH2MHILL Extension  77540
>>> [email protected]
>>>
>>>
>>>
>>> *From:* Sprinklerforum [mailto:sprinklerforum-bounces
>>> @lists.firesprinkler.org] *On Behalf Of *Brad Casterline
>>> *Sent:* Monday, August 08, 2016 8:39 PM
>>> *To:* [email protected]
>>> *Subject:* RE: Paint spray application [EXTERNAL]
>>>
>>>
>>>
>>> Show me a spray booth with forty sprinklers Steve
>>>
>>> On Aug 8, 2016 7:36 PM, "Steve Leyton" <[email protected]>
>>> wrote:
>>>
>>> Sure.  And fires that can be spread by running fuel such as plastics and
>>> FCL’s (not to mention BLEVE’s) can set off 40 standard response sprinklers
>>> in a minute.   I can only imagine the sheer volume of responding sprinklers
>>> and skipping that could occur based on how smooth or bumpy the roof/ceiling
>>> assembly is if you started wantonly plugging QR control-mode sprinklers
>>> into EH fires.   (On paper) MDD = .80    ADD = .275
>>>
>>>
>>>
>>> My opinion only,
>>>
>>> Steve L.
>>>
>>>
>>>
>>>
>>>
>>>
>>>
>>> *From:* Sprinklerforum [mailto:sprinklerforum-bounces
>>> @lists.firesprinkler.org] *On Behalf Of *Brad Casterline
>>> *Sent:* Monday, August 08, 2016 5:17 PM
>>> *To:* [email protected]
>>> *Subject:* Re: Paint spray application
>>>
>>>
>>>
>>> Shakey ground is all i have ever known Ken.
>>> I am no more a professional than you are.
>>> THINK MAN!
>>> small spaces with fast fires need the fastest acting sprinklers we can
>>> muster.
>>> I've been in court myself a couple times- neither one over sprinklers
>>> though--
>>> please stop being so stodgy!
>>>
>>> On Aug 8, 2016 7:05 PM, "Parsley Consulting" <[email protected]>
>>> wrote:
>>>
>>> I don't know, Brad.  You're standing on pretty shaky ground there.
>>>
>>> The decision to use QR sprinklers in an extra hazard occpuancy is a
>>> direct contradiction to 8.4.1.1.2 of NFPA 13, including the 2016 edition,
>>> or a similar section number, at least as far back as the 1999 edition.  If
>>> you install QR sprinklers in a space that is legitimately classed as an
>>> extra hazard occupancy, aren't you directly contradicting this particular
>>> section of NFPA 13?  The handbook provides the following explanatory text
>>> on the topic:
>>>
>>> Extra hazard occupancies are characterized by the probability of
>>> fast-developing fires with high heat release rates that have the potential
>>> to open a large number of quick-response sprinklers before the sprinklers
>>> have time to control the fire. The operation of a large number of
>>> sprinklers in a relatively short time period has the potential to overtax
>>> the system. For this reason, quick-response sprinklers using the area
>>> design method of Chapter 11 are not permitted for the protection of
>>> extra hazard occupancies. Additional perspective on this can be found in
>>> the discussion of safety margin found in B.2.1.
>>>
>>> Further, I'm not aware of any QR sprinkler which has been tested and
>>> listed by an NRTL for use in protecting extra hazard occupancies.  Barring
>>> that, to follow the guidance you're suggesting the
>>> contractor/designer/installer has to violate both NFPA 13 AND the listing
>>> of the sprinkler.  I'm not suggesting the gloom and doom drama of "people
>>> could die", however it does concern me greatly when I read suggestions to
>>> ignore both texts.
>>>
>>> My thought about that is to make sure your insurance is paid up, and
>>> have a good lawyer on retainer.  I don't know of a good defense while
>>> sitting in the witness chair to a question similar to, "Are you telling me
>>> you ignored the applicable law and the manufacturer's recommendations for
>>> the installation of that sprinkler?"
>>>
>>> When I have nightmares I think about having to answer questions similar
>>> to that.
>>>
>>>
>>>
>>>
>>>
>>>
>>> *Ken Wagoner, SET Parsley Consulting 350 West 9th Avenue, Suite 206
>>> Escondido, California 92025 Phone 760-745-6181 <760-745-6181> Visit our
>>> website <http://www.parsleyconsulting.com/> *
>>>
>>>
>>> On 08/08/2016 4:17 PM, Brad Casterline wrote:
>>>
>>> We're not suppose to use QR in EH either but I say balderdash.
>>> That is for big open spaces beacase you could have a bunch of heads
>>> going off way over there when the emergency is way over here. Small spaces
>>> with fast fires are better off if you use low temp qr and calc every head
>>> possible going off
>>>
>>>
>>>
>>>
>>>
>>>
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-f
>>> iresprinkler.org
>>>
>>>
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-f
>>> iresprinkler.org
>>>
>>>
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-f
>>> iresprinkler.org
>>>
>>>
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-f
>>> iresprinkler.org
>>>
>>>
>>>
>>>
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-f
>>> iresprinkler.org
>>>
>>>
>>>
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-f
>>> iresprinkler.org
>>>
>>>
>>
>
> --
> Sent from Gmail Mobile
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to