Inside a duct no matter the orientation, the sprinkler sees the same shape and 
the discharge will more than adequately cover the small space.

Look at 22.4.2 in 2013 edition of 13.

Orientation is not specified.  Now you might pick a location based on drainage 
or other factors.  But there is no specific NFPA constraint.


Craig L. Prahl
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd.
Greenville, SC  29607
Direct - 864.920.7540
Fax - 864.920.7129
CH2MHILL Extension  77540
[email protected]


From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of IPA
Sent: Tuesday, August 09, 2016 2:28 PM
To: [email protected]
Subject: Re: Paint spray application [EXTERNAL]

So, where is the code section that says pendant sprinklers can be installed in 
any orientation in ducts? I've just scoured '13 and can't find it.

On Tue, Aug 9, 2016 at 11:26 AM, Bob 
<[email protected]<mailto:[email protected]>> wrote:
Brad,
It’s all good.  I tend to agree with the QR on small booths.  Especially since 
we are calc’ing for the worst case that all sprinklers will flow anyway.  Seems 
that opening faster would be a good idea, but then again I’m not an engineer, 
just a guy who draws lots of lines and circles.


Thank you,

Bob Knight, CET III
208-318-3057<tel:208-318-3057>

From: Sprinklerforum 
[mailto:[email protected]<mailto:[email protected]>]
 On Behalf Of Brad Casterline
Sent: Tuesday, August 09, 2016 12:21 PM
To: 
[email protected]<mailto:[email protected]>;
 [email protected]<mailto:[email protected]>

Subject: RE: Paint spray application


Yes indeed.
I knew as soon as I hit send it was a bad idea.
I have thought for several years there should be an exception for no QR in EH, 
ever since I understood the reasoning.
I should have more soberly made my point that I think small paint booths are an 
excellent application -- if you calc all heads flowing why not use low temp QR? 
It would be the next best thing to open head deluge, would it not?
And I apologize for the name calling and meaness of spirit, FWIW. There is no 
excuse for that. A big part of how I feel about myself is based on how i act on 
this Forum.

Thanks,
Brad
On Aug 9, 2016 1:02 PM, "Bob" 
<[email protected]<mailto:[email protected]>> wrote:
I have an example of one that I did in Salt Lake recently.  It has 144 
sprinklers in it.  This counts all the exhaust ducts and stacks plus the 
ceiling sprinklers.

Thank you,

Bob Knight, CET III
208-318-3057<tel:208-318-3057>

From: Sprinklerforum 
[mailto:[email protected]<mailto:[email protected]>]
 On Behalf Of [email protected]<mailto:[email protected]>
Sent: Tuesday, August 09, 2016 6:29 AM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Paint spray application

How many example of industrial spray booths with more than 40 heads would you 
like Brad?  They exist and are not all that rare.


Craig L. Prahl
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd.
Greenville, SC  29607
Direct - 864.920.7540<tel:864.920.7540>
Fax - 864.920.7129<tel:864.920.7129>
CH2MHILL Extension  77540
[email protected]<mailto:[email protected]>

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Brad Casterline
Sent: Monday, August 08, 2016 8:39 PM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Paint spray application [EXTERNAL]


Show me a spray booth with forty sprinklers Steve
On Aug 8, 2016 7:36 PM, "Steve Leyton" 
<[email protected]<mailto:[email protected]>> wrote:
Sure.  And fires that can be spread by running fuel such as plastics and FCL’s 
(not to mention BLEVE’s) can set off 40 standard response sprinklers in a 
minute.   I can only imagine the sheer volume of responding sprinklers and 
skipping that could occur based on how smooth or bumpy the roof/ceiling 
assembly is if you started wantonly plugging QR control-mode sprinklers into EH 
fires.   (On paper) MDD = .80    ADD = .275

My opinion only,
Steve L.



From: Sprinklerforum 
[mailto:[email protected]<mailto:[email protected]>]
 On Behalf Of Brad Casterline
Sent: Monday, August 08, 2016 5:17 PM
To: 
[email protected]<mailto:[email protected]>
Subject: Re: Paint spray application


Shakey ground is all i have ever known Ken.
I am no more a professional than you are.
THINK MAN!
small spaces with fast fires need the fastest acting sprinklers we can muster.
I've been in court myself a couple times- neither one over sprinklers though--
please stop being so stodgy!
On Aug 8, 2016 7:05 PM, "Parsley Consulting" 
<[email protected]<mailto:[email protected]>> wrote:
I don't know, Brad.  You're standing on pretty shaky ground there.

The decision to use QR sprinklers in an extra hazard occpuancy is a direct 
contradiction to 8.4.1.1.2 of NFPA 13, including the 2016 edition, or a similar 
section number, at least as far back as the 1999 edition.  If you install QR 
sprinklers in a space that is legitimately classed as an extra hazard 
occupancy, aren't you directly contradicting this particular section of NFPA 
13?  The handbook provides the following explanatory text on the topic:
Extra hazard occupancies are characterized by the probability of 
fast-developing fires with high heat release rates that have the potential to 
open a large number of quick-response sprinklers before the sprinklers have 
time to control the fire. The operation of a large number of sprinklers in a 
relatively short time period has the potential to overtax the system. For this 
reason, quick-response sprinklers using the area
design method of Chapter 11 are not permitted for the protection of extra 
hazard occupancies. Additional perspective on this can be found in the 
discussion of safety margin found in B.2.1.
Further, I'm not aware of any QR sprinkler which has been tested and listed by 
an NRTL for use in protecting extra hazard occupancies.  Barring that, to 
follow the guidance you're suggesting the contractor/designer/installer has to 
violate both NFPA 13 AND the listing of the sprinkler.  I'm not suggesting the 
gloom and doom drama of "people could die", however it does concern me greatly 
when I read suggestions to ignore both texts.

My thought about that is to make sure your insurance is paid up, and have a 
good lawyer on retainer.  I don't know of a good defense while sitting in the 
witness chair to a question similar to, "Are you telling me you ignored the 
applicable law and the manufacturer's recommendations for the installation of 
that sprinkler?"

When I have nightmares I think about having to answer questions similar to that.
Ken Wagoner, SET
Parsley Consulting
350 West 9th Avenue, Suite 206
Escondido, California 92025
Phone 760-745-6181<tel:760-745-6181>
Visit our website<http://www.parsleyconsulting.com/>

On 08/08/2016 4:17 PM, Brad Casterline wrote:

We're not suppose to use QR in EH either but I say balderdash.
That is for big open spaces beacase you could have a bunch of heads going off 
way over there when the emergency is way over here. Small spaces with fast 
fires are better off if you use low temp qr and calc every head possible going 
off



_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to