I agree Don, but there are no sidewalls listed for EH PERIOD.

There are Ups and Pends listed for EH, and then what you cited could be
applicable.

 

This is just my understanding.

 

Brad

 

  _____  

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Don Casey
Sent: Wednesday, August 10, 2016 1:12 PM
To: [email protected]
Subject: RE: Paint spray application

 



 

Heads get used in ways they haven't been listed in multiple scenarios.

 

One easy one is for protecting steel columns when working with NFPA 15.
I've used both pens and sidewalls depending on the configuration.

 

In a duct, we're typically looking to dump a certain amount of water into
the duct which can be achieved using a sidewall or a pendant.

 

Side note: a pen in a vertical duct  would not be installed per it's listing
and in a horizontal duct, it won't meet the obstruction rules unless the
duct diameter was greater than 18inches.  

 

As long as you can calculate the head(s) to deliver/operate at the
flows/pressures stated by the applicable Standard (13 or 33 in this case)
and is designed to operate at the minimum pressure as specified by the
head's listing (okay..not likely to come into play unless you wanted to use
a K25 head and even then).

 

Lastly, if you're a stamping professional, you can come up with any design
you think will work (which you've presumably based on data, experience,
calculations, etc.). 

 

 

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of [email protected]
Sent: 2016/08/10 1:46 PM
To: [email protected]
Subject: RE: Paint spray application

 

Ductwork is like protecting specialty equipment, there isn't necessarily a
box you can put it in when it comes to NFPA 13 occupancies.  You have to be
able to analyze the process and determine the hazard before you can assign a
protection scheme for things such as this.

 

One additional tool in the designer's toolbox is the FM Global data sheets.
NFPA 13 doesn't always address every single possible protection scheme where
a water based sprinkler would be beneficial.  If you have questions about a
particular application you can refer to other recognized industry Standards
for additional information and insight.

 

The owner doesn't have to be FM insured to be able to use this data to
defend or establish a design criteria for unique applications that NFPA may
not address.  I have yet to run across an AHJ that rejected the use of FM
Global criteria when NFPA didn't address the situation.  

 


Craig L. Prahl 
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd. 
Greenville, SC  29607
Direct - 864.920.7540

Fax - 864.920.7129

CH2MHILL Extension  77540
[email protected]

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Brad Casterline
Sent: Wednesday, August 10, 2016 1:03 PM
To: [email protected]
Subject: RE: Paint spray application [EXTERNAL]

 

Well, it's all I got.

 

I think there is a little wiggle room regarding occupancy classification.
For example, in the duct we can be max 12'-0" whilst outside the duct it is
10' max.

That's a little weak, but, seeing as how I am a NICET certified engineering
technician I see no wiggle room in using a sprinkler outside it's listing. I
believe like you that deflector orientation in a duct is a non-issue due to
deflectors determine the pattern at the floor, butt....

 

see "Ken's well known aversion to courtrooms" for details :) 

 

Brad

 

ps, thank you, and you too Bob, for helping me out of the doldrums yesterday

 

 

  _____  

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of [email protected]
Sent: Wednesday, August 10, 2016 7:44 AM
To: [email protected]
Subject: RE: Paint spray application

 

How do you know the quantity of combustibles?  

 

Typically the issues with ductwork is based on a hazardous environment
(transporting flammable or combustible vapors or combustible particulate)
that's the whole reason behind the requirement of protection of the
ductwork.  The other condition is that there is accumulation of the same
material on the interior of the duct over time creating a hazardous
environment.

 

So in either case there is no way to call it an ordinary hazard environment.

 


Craig L. Prahl 
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd. 
Greenville, SC  29607
Direct - 864.920.7540

Fax - 864.920.7129

CH2MHILL Extension  77540
[email protected]

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Brad Casterline
Sent: Wednesday, August 10, 2016 8:40 AM
To: [email protected]
Subject: RE: Paint spray application [EXTERNAL]

 

To be completely formal, is it possible to consider the duct to be an OH
portion of the EH Classification? Not much quantity of combustible there.