Pendents. A pendant is a piece of jewelry. We use hangers.  Airplanes are 
stored in hangars. There is no such thing as a sprinkler head. That is all for 
today.

Steve


-------- Original message --------
From: Brad Casterline <[email protected]>
Date: 8/11/16 4:28 AM (GMT-08:00)
To: [email protected]
Subject: Re: Paint spray application


Don,

I just wanted to add that I have seen sidewalls and pendants for column 
protection accepted also. I suppose the reasoning is that the columns are not 
the building contents determining the hazard classification. And sprinklers are 
just one of a few methods for protecting the columns.

good catch by the way with your clip,

Brad

On Aug 10, 2016 2:13 PM, "IPA" <[email protected]<mailto:[email protected]>> 
wrote:
There we go... the justification for the horizontally mounted pendants. Thank 
you!


On Wed, Aug 10, 2016 at 11:11 AM, Don Casey 
<[email protected]<mailto:[email protected]>> wrote:
[cid:[email protected]]

Heads get used in ways they haven’t been listed in multiple scenarios.

One easy one is for protecting steel columns when working with NFPA 15.  I’ve 
used both pens and sidewalls depending on the configuration.

In a duct, we’re typically looking to dump a certain amount of water into the 
duct which can be achieved using a sidewall or a pendant.

Side note: a pen in a vertical duct  would not be installed per it’s listing 
and in a horizontal duct, it won’t meet the obstruction rules unless the duct 
diameter was greater than 18inches.

As long as you can calculate the head(s) to deliver/operate at the 
flows/pressures stated by the applicable Standard (13 or 33 in this case) and 
is designed to operate at the minimum pressure as specified by the head’s 
listing (okay….not likely to come into play unless you wanted to use a K25 head 
and even then).

Lastly, if you’re a stamping professional, you can come up with any design you 
think will work (which you’ve presumably based on data, experience, 
calculations, etc.).


From: Sprinklerforum 
[mailto:[email protected]<mailto:[email protected]>]
 On Behalf Of [email protected]<mailto:[email protected]>
Sent: 2016/08/10 1:46 PM

To: 
[email protected]<mailto:[email protected]>
Subject: RE: Paint spray application

Ductwork is like protecting specialty equipment, there isn’t necessarily a box 
you can put it in when it comes to NFPA 13 occupancies.  You have to be able to 
analyze the process and determine the hazard before you can assign a protection 
scheme for things such as this.

One additional tool in the designer’s toolbox is the FM Global data sheets.  
NFPA 13 doesn’t always address every single possible protection scheme where a 
water based sprinkler would be beneficial.  If you have questions about a 
particular application you can refer to other recognized industry Standards for 
additional information and insight.

The owner doesn’t have to be FM insured to be able to use this data to defend 
or establish a design criteria for unique applications that NFPA may not 
address.  I have yet to run across an AHJ that rejected the use of FM Global 
criteria when NFPA didn’t address the situation.


Craig L. Prahl
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd.
Greenville, SC  29607
Direct - 864.920.7540<tel:864.920.7540>
Fax - 864.920.7129<tel:864.920.7129>
CH2MHILL Extension  77540
[email protected]<mailto:[email protected]>

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Brad Casterline
Sent: Wednesday, August 10, 2016 1:03 PM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Paint spray application [EXTERNAL]

Well, it's all I got.

I think there is a little wiggle room regarding occupancy classification. For 
example, in the duct we can be max 12'-0" whilst outside the duct it is 10' max.
That's a little weak, but, seeing as how I am a NICET certified engineering 
technician I see no wiggle room in using a sprinkler outside it's listing. I 
believe like you that deflector orientation in a duct is a non-issue due to 
deflectors determine the pattern at the floor, butt....

see "Ken's well known aversion to courtrooms" for details :)

Brad

ps, thank you, and you too Bob, for helping me out of the doldrums yesterday


________________________________
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of [email protected]<mailto:[email protected]>
Sent: Wednesday, August 10, 2016 7:44 AM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Paint spray application

How do you know the quantity of combustibles?

Typically the issues with ductwork is based on a hazardous environment 
(transporting flammable or combustible vapors or combustible particulate) 
that’s the whole reason behind the requirement of protection of the ductwork.  
The other condition is that there is accumulation of the same material on the 
interior of the duct over time creating a hazardous environment.

So in either case there is no way to call it an ordinary hazard environment.


Craig L. Prahl
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd.
Greenville, SC  29607
Direct - 864.920.7540<tel:864.920.7540>
Fax - 864.920.7129<tel:864.920.7129>
CH2MHILL Extension  77540
[email protected]<mailto:[email protected]>

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Brad Casterline
Sent: Wednesday, August 10, 2016 8:40 AM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Paint spray application [EXTERNAL]


To be completely formal, is it possible to consider the duct to be an OH 
portion of the EH Classification? Not much quantity of combustible there.

_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org



_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to