And that is the beauty of software like AutoSprink. Just put the boundary on the plan. Select all of them you have and tell it to keep the hydraulically most demanding. Simple and sweet.

When it may be a challenge for the AHJ to believe the area I select, then I will submit multiple areas just to eliminate questions.

The software packages today and power of the personal computer make this entire thread a mute point - provided the information is available. If you have the system drawn, it is literally a matter of seconds to calculate an area. It is not like those of us who learned by hand back in the day and it would be a long drawn out process.

Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]

http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign
LinkedIn: https://www.linkedin.com/in/travismack

On 8/30/2016 9:08 AM, rongreenman . wrote:
I'd agree with Mark except for two little irritations of mine when discussing this. "Remote Area" was a term that worked when we just sprinklered big boxes that housed either factories or warehouses as the "remote area" (furthest from the rider) was typically the hydraulically most demanding area. These days that area can be anywhere (a grid being the always example). Hydraulically most demanding area is too muchoif a mouthful for describing itself so I just prefer design or demand area. This pet peeve came about from teaching newbies the basics as they'd often get it in their minds that remote meant furthest away and so would want to calculate the the x number of heads at the greatest distance as the crow flies over the plan. That is also the basis of pet peeve two that "remote area" also suggests that there is only one possibility and it's easy to find. Determining the design area(s) is an art. I have an exercise based on a building no one would ever build but it gas over a dozen potential design areas and just as Mark says the student needs to determine where and which are most likely by estimating demand at each location.

On Tuesday, August 30, 2016, <[email protected] <mailto:[email protected]>> wrote:

    My personal belief is that the designer “designs” the “remote”
    area into the system, and a good designer will design the overall
    system to economically benefit from “where” the remote area lies.
    Unfortunately, I think most systems are laid out, sized, and then
    calculations are performed to determine where the remote area lies.

    As Steve says “just my opinion”

    Mark at Aero

    602 820-7894

    *From:*Sprinklerforum
    [mailto:[email protected]
    
<javascript:_e(%7B%7D,'cvml','[email protected]');>]
    *On Behalf Of *Bill Brooks
    *Sent:* Tuesday, August 30, 2016 8:32 AM
    *To:* [email protected]
    <javascript:_e(%7B%7D,'cvml','[email protected]');>
    *Subject:* RE: Flexheads in small renovation (Calculation Software)

    You will be able to tell this question is based on minimum
    software application experience, but does current software
    automatically determine “most demanding”? Or, is it up to the
    human operator to guess where this area might be?  If it’s a
    guess, how do you know you have chosen correctly?

    Bill Brooks

    *From:*Sprinklerforum
    [mailto:[email protected]
    
<javascript:_e(%7B%7D,'cvml','[email protected]');>]
    *On Behalf Of *Steve Leyton
    *Sent:* Tuesday, August 30, 2016 10:40 AM
    *To:* [email protected]
    <javascript:_e(%7B%7D,'cvml','[email protected]');>
    *Subject:* RE: Flexheads in small renovation

    To underscore John’s point, these fittings impose with a
    SUBSTANTIAL pressure loss.   As 3^rd party, we would ask for
    calculations to prove the performance of the revised configuration.

    SL

    *From:*Sprinklerforum
    [mailto:[email protected]
    
<javascript:_e(%7B%7D,'cvml','[email protected]');>]
    *On Behalf Of *Michael Hill
    *Sent:* Tuesday, August 30, 2016 6:11 AM
    *To:* [email protected]
    <javascript:_e(%7B%7D,'cvml','[email protected]');>
    *Subject:* RE: Flexheads in small renovation

    I agree with Richard, it needs to be evaluated. It is known that
    flex piping is generally more demanding than their hard piped
    counterparts. If the base building design did not include flex
    piping, I would look at it as a change to base building design and
    perform a quick calculation to see how it looks. I assume they
    didn’t use excessively long flex pipe with more bends or lops than
    were needed.

    Mike Hill

    *From:*Sprinklerforum
    [mailto:[email protected]
    
<javascript:_e(%7B%7D,'cvml','[email protected]');>]
    *On Behalf Of *Todd Williams
    *Sent:* Tuesday, August 30, 2016 8:39 AM
    *To:* [email protected]
    <javascript:_e(%7B%7D,'cvml','[email protected]');>
    *Subject:* RE: Flexheads in small renovation

    This is a single story building. Multiple looped 4" and 3" cross
    mains with branches to wings. (Think nursing home with interior
    court yards). No fire pump. 100 psi static with a flat curve (2
    year old test, DeltaE = 0). Area in question not most
    hydraulically remote but toward that end of the building. Branch
    lines are fed from the loop, not a DE branch main. LH occupancy.

    I am not worried about this not being adequate, more a consensus
    of what needs to be done and what is correct.

    Todd G Williams, PE

    Fire Protection Design/Consulting

    Stonington, CT

    860-535-2080 (ofc)

    860-608-4559 (cell)

    Sent using CloudMagic
    <https://cloudmagic.com/k/d/mailapp?ct=ti&cv=6.0.64&pv=8.2>

    On Tue, Aug 30, 2016 at 8:22 AM, Richard Carr <[email protected]
    <javascript:_e(%7B%7D,'cvml','[email protected]');>> wrote:

        I can’t disagree with John (Hi John) but we need more info to
        make the call,

        In remote area?

        Fire pump?

        What is safety margin on existing?

        What is friction loss on the flex?

        Just because you add 4 flex piping to an existing system does
        not require it to be calculated. But does need to be evaluated.

        Richard Carr, SET

        Branch Manager

        Cox Fire Protection, Inc

        6555 Grace Lane.

        Jacksonville, Fl. 32205

        [email protected]
        <javascript:_e(%7B%7D,'cvml','[email protected]');>

        904-781-8227

        *From:*Sprinklerforum
        [mailto:[email protected]
        
<javascript:_e(%7B%7D,'cvml','[email protected]');>]
        *On Behalf Of *John Irwin
        *Sent:* Tuesday, August 30, 2016 7:14 AM
        *To:* [email protected]
        <javascript:_e(%7B%7D,'cvml','[email protected]');>
        *Subject:* RE: Flexheads in small renovation

        I disagree with Richard. (Hi Richard!)

        Relocating these sprinklers with flex heads may very well
        change the location of the most hydraulically remote area to
        the place you are working. Flex-heads come with a substantial
        pressure loss. Even if doing calculations wasn’t required, I
        would want to do them for myself for peace of mind. My belief
        has always been that you can’t tax the system without
        verifying that it still works.

        *John Irwin*

        Manger – Fire Sprinkler Division

        *Critical System Solutions, LLC
        *Cell: 813.618.2781

        Email: [email protected]
        <javascript:_e(%7B%7D,'cvml','[email protected]');>

        *From:*Sprinklerforum
        [mailto:[email protected]
        
<javascript:_e(%7B%7D,'cvml','[email protected]');>]
        *On Behalf Of *Richard Carr
        *Sent:* Tuesday, August 30, 2016 7:08 AM
        *To:* [email protected]
        <javascript:_e(%7B%7D,'cvml','[email protected]');>
        *Subject:* RE: Flexheads in small renovation

        Are the relocates in the remote area? if not I would not calc.
        also , some flex brands are better that others as far as
        friction loss.

        Richard Carr, SET

        Branch Manager

        Cox Fire Protection, Inc

        6555 Grace Lane.

        Jacksonville, Fl. 32205

        [email protected]
        <javascript:_e(%7B%7D,'cvml','[email protected]');>

        904-781-8227

        *From:*Sprinklerforum
        [mailto:[email protected]
        
<javascript:_e(%7B%7D,'cvml','[email protected]');>]
        *On Behalf Of *Todd Williams
        *Sent:* Tuesday, August 30, 2016 6:30 AM
        *To:* [email protected]
        <javascript:_e(%7B%7D,'cvml','[email protected]');>
        *Subject:* Flexheads in small renovation

        I have a client that did a 4 sprinkler relocate job in an
        office and used Flexheads (no sprinklers added). If the
        sprinklers were connected with hard pipe, I would probably not
        do hydraulic calculations. Given that we have FHs, should I be
        doing a full 900 or 1500 sqft calculation?

        Todd G Williams, PE

        Fire Protection Design/Consulting

        Stonington, CT

        860-535-2080 (ofc)

        860-608-4559 (cell)

        Sent using CloudMagic
        <https://cloudmagic.com/k/d/mailapp?ct=ti&cv=6.0.64&pv=8.2>



--
Sent from Gmail Mobile


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to