Travis,

What you say here is true.  It is also very helpful as you mention when you 
have multiple areas to calculate and you can't "eyeball" the most hydraulically 
remote.  However it isn't without risk.  Many times we have done this, and 
during our QC process realized some of the sprinklers were not setup properly 
for the hazard they are protecting, or found that a sprinkler was disconnected, 
or accidentally picked up sprinklers we didn't intend to.  Same can be said 
about the piping network.  Or someone accidentally copied a pipe that they 
manually overwrote 90's Tee's Valve's etc into a straight run rather than 
drawing them.

So, I agree AutoSprink can be very helpful with multiple calcs.  I just offer 
the word of warning to those who think computers will be replacing smart 
designers anytime soon.

Thanks,
Sean VG





From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Travis Mack, SET
Sent: Tuesday, August 30, 2016 9:14 AM
To: [email protected]
Subject: Re: Flexheads in small renovation (Calculation Software)


And that is the beauty of software like AutoSprink.  Just put the boundary on 
the plan.  Select all of them you have and tell it to keep the hydraulically 
most demanding.  Simple and sweet.

When it may be a challenge for the AHJ to believe the area I select, then I 
will submit multiple areas just to eliminate questions.

The software packages today and power of the personal computer make this entire 
thread a mute point - provided the information is available.  If you have the 
system drawn, it is literally a matter of seconds to calculate an area.  It is 
not like those of us who learned by hand back in the day and it would be a long 
drawn out process.

Travis Mack, SET

MFP Design, LLC

2508 E Lodgepole Drive

Gilbert, AZ 85298

480-505-9271

fax: 866-430-6107

email:[email protected]<mailto:email:[email protected]>



http://www.mfpdesign.com

https://www.facebook.com/pages/MFP-Design-LLC/92218417692

Send large files to us via: https://www.hightail.com/u/MFPDesign

LinkedIn: https://www.linkedin.com/in/travismack
On 8/30/2016 9:08 AM, rongreenman . wrote:
I'd agree with Mark except for two little irritations of mine when discussing 
this. "Remote Area" was a term that worked when we just sprinklered big boxes 
that housed either factories or warehouses as the "remote area" (furthest from 
the rider) was typically the hydraulically most demanding area. These days that 
area can be anywhere (a grid being the always example). Hydraulically most 
demanding area is too muchoif a mouthful for describing itself so I just prefer 
design or demand area. This pet peeve came about from teaching newbies the 
basics as they'd often get it in their minds that remote meant furthest away 
and so would want to calculate the the x number of heads at the greatest 
distance as the crow flies over the plan. That is also the basis of pet peeve 
two that "remote area" also suggests that there is only one possibility and 
it's easy to find. Determining the design area(s) is an art. I have an exercise 
based on a building no one would ever build but it gas over a dozen potential 
design areas and just as Mark says the student needs to determine where and 
which are most likely by estimating demand at each location.

On Tuesday, August 30, 2016, 
<[email protected]<mailto:[email protected]>> wrote:
My personal belief is that the designer "designs" the "remote" area into the 
system, and a good designer will design the overall system to economically 
benefit from "where" the remote area lies. Unfortunately, I think most systems 
are laid out, sized, and then calculations are performed to determine where the 
remote area lies.
As Steve says "just my opinion"
Mark at Aero
602 820-7894

From: Sprinklerforum 
[mailto:[email protected]<javascript:_e(%7B%7D,'cvml','[email protected]');>]
 On Behalf Of Bill Brooks
Sent: Tuesday, August 30, 2016 8:32 AM
To: 
[email protected]<javascript:_e(%7B%7D,'cvml','[email protected]');>
Subject: RE: Flexheads in small renovation (Calculation Software)

You will be able to tell this question is based on minimum software application 
experience, but does current software automatically determine "most demanding"? 
 Or, is it up to the human operator to guess where this area might be?  If it's 
a guess, how do you know you have chosen correctly?

Bill Brooks

From: Sprinklerforum 
[mailto:[email protected]<javascript:_e(%7B%7D,'cvml','[email protected]');>]
 On Behalf Of Steve Leyton
Sent: Tuesday, August 30, 2016 10:40 AM
To: 
[email protected]<javascript:_e(%7B%7D,'cvml','[email protected]');>
Subject: RE: Flexheads in small renovation

To underscore John's point, these fittings impose with a SUBSTANTIAL pressure 
loss.   As 3rd party, we would ask for calculations to prove the performance of 
the revised configuration.

SL

From: Sprinklerforum 
[mailto:[email protected]<javascript:_e(%7B%7D,'cvml','[email protected]');>]
 On Behalf Of Michael Hill
Sent: Tuesday, August 30, 2016 6:11 AM
To: 
[email protected]<javascript:_e(%7B%7D,'cvml','[email protected]');>
Subject: RE: Flexheads in small renovation

I agree with Richard, it needs to be evaluated. It is known that flex piping is 
generally more demanding than their hard piped counterparts. If the base 
building design did not include flex piping, I would look at it as a change to 
base building design and perform a quick calculation to see how it looks. I 
assume they didn't use excessively long flex pipe with more bends or lops than 
were needed.

Mike Hill

From: Sprinklerforum 
[mailto:[email protected]<javascript:_e(%7B%7D,'cvml','[email protected]');>]
 On Behalf Of Todd Williams
Sent: Tuesday, August 30, 2016 8:39 AM
To: 
[email protected]<javascript:_e(%7B%7D,'cvml','[email protected]');>
Subject: RE: Flexheads in small renovation

This is a single story building. Multiple looped 4" and 3" cross mains with 
branches to wings. (Think nursing home with interior court yards). No fire 
pump. 100 psi static with a flat curve (2 year old test, DeltaE = 0). Area in 
question not most hydraulically remote but toward that end of the building. 
Branch lines are fed from the loop, not a DE branch main. LH occupancy.

I am not worried about this not being adequate, more a consensus of what needs 
to be done and what is correct.
Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080 (ofc)
860-608-4559 (cell)

Sent using CloudMagic<https://cloudmagic.com/k/d/mailapp?ct=ti&cv=6.0.64&pv=8.2>

On Tue, Aug 30, 2016 at 8:22 AM, Richard Carr 
<[email protected]<javascript:_e(%7B%7D,'cvml','[email protected]');>> wrote:
I can't disagree with John (Hi John) but we need more info to make the call,
In remote area?
Fire pump?
What is safety margin on existing?
What is friction loss on the flex?

Just because you add 4 flex piping to an existing system does not require it to 
be calculated. But does need to be evaluated.

Richard Carr, SET
Branch Manager
Cox Fire Protection, Inc
6555 Grace Lane.
Jacksonville, Fl. 32205
[email protected]<javascript:_e(%7B%7D,'cvml','[email protected]');>
904-781-8227

From: Sprinklerforum 
[mailto:[email protected]<javascript:_e(%7B%7D,'cvml','[email protected]');>]
 On Behalf Of John Irwin
Sent: Tuesday, August 30, 2016 7:14 AM
To: 
[email protected]<javascript:_e(%7B%7D,'cvml','[email protected]');>
Subject: RE: Flexheads in small renovation

I disagree with Richard. (Hi Richard!)

Relocating these sprinklers with flex heads may very well change the location 
of the most hydraulically remote area to the place you are working. Flex-heads 
come with a substantial pressure loss. Even if doing calculations wasn't 
required, I would want to do them for myself for peace of mind. My belief has 
always been that you can't tax the system without verifying that it still works.

John Irwin
Manger - Fire Sprinkler Division
Critical System Solutions, LLC
Cell:     813.618.2781
Email:  
[email protected]<javascript:_e(%7B%7D,'cvml','[email protected]');>


From: Sprinklerforum 
[mailto:[email protected]<javascript:_e(%7B%7D,'cvml','[email protected]');>]
 On Behalf Of Richard Carr
Sent: Tuesday, August 30, 2016 7:08 AM
To: 
[email protected]<javascript:_e(%7B%7D,'cvml','[email protected]');>
Subject: RE: Flexheads in small renovation

Are the relocates in the remote area? if not I would not calc. also , some flex 
brands are better that others as far as friction loss.

Richard Carr, SET
Branch Manager
Cox Fire Protection, Inc
6555 Grace Lane.
Jacksonville, Fl. 32205
[email protected]<javascript:_e(%7B%7D,'cvml','[email protected]');>
904-781-8227

From: Sprinklerforum 
[mailto:[email protected]<javascript:_e(%7B%7D,'cvml','[email protected]');>]
 On Behalf Of Todd Williams
Sent: Tuesday, August 30, 2016 6:30 AM
To: 
[email protected]<javascript:_e(%7B%7D,'cvml','[email protected]');>
Subject: Flexheads in small renovation

I have a client that did a 4 sprinkler relocate job in an office and used 
Flexheads (no sprinklers added). If the sprinklers were connected with hard 
pipe, I would probably not do hydraulic calculations. Given that we have FHs, 
should I be doing a full 900 or 1500 sqft calculation?
Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080 (ofc)
860-608-4559 (cell)

Sent using CloudMagic<https://cloudmagic.com/k/d/mailapp?ct=ti&cv=6.0.64&pv=8.2>



--
Sent from Gmail Mobile




_______________________________________________

Sprinklerforum mailing list

[email protected]<mailto:[email protected]>

http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to