Mike,
    Don't kid yourself.
If I could force one task one "computer operator" who sends me a set of hydraulic calculations performed by integrated software it would be "Show it to someone who _*knows how to read*_ a set of calcs before you submit it." I've seen integrated software tell me that it was perfectly acceptable to have a sprinkler show a flowing pressure of less than 6.5 psi, flow from reference points with a 0.0 k-factor, and demand pressure which exceeded the available pressure at the required flow by over 13 psi. There's actually integrated software out there which will not provide any proof that a grid system calculation had been peaked. And the "computer operators" who submitted these calculations didn't have a clue why those problems resulted in the submittal being rejected. And the shock on the other end of the phone when these flaws are pointed out rivals the "Cone of Silence" from the old TV show "Get Smart". When the design of fire sprinkler systems and the preparation of hydraulic calculations becomes just another computer video game, then GIGO rears it's hammer, as it always will.
*Ken Wagoner, SET
*Parsley Consulting***
*350 West 9th Avenue, Suite 206
*Escondido, California 92025
*****Phone 760-745-6181*
Visit our website <http://www.parsleyconsulting.com/> ***
On 08/30/2016 9:27 AM, Michael Hill wrote:

The new software is so powerful, it only needs computer operators to use. The sprinkler system designer has nearly been eliminated from the process.

Mike Hill

*From:*Sprinklerforum [mailto:[email protected]] *On Behalf Of *Travis Mack, SET
*Sent:* Tuesday, August 30, 2016 12:14 PM
*To:* [email protected]
*Subject:* Re: Flexheads in small renovation (Calculation Software)

And that is the beauty of software like AutoSprink. Just put the boundary on the plan. Select all of them you have and tell it to keep the hydraulically most demanding. Simple and sweet.

When it may be a challenge for the AHJ to believe the area I select, then I will submit multiple areas just to eliminate questions.

The software packages today and power of the personal computer make this entire thread a mute point - provided the information is available. If you have the system drawn, it is literally a matter of seconds to calculate an area. It is not like those of us who learned by hand back in the day and it would be a long drawn out process.

Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected] <mailto:email:[email protected]>
http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via:https://www.hightail.com/u/MFPDesign LinkedIn:https://www.linkedin.com/in/travismack

On 8/30/2016 9:08 AM, rongreenman . wrote:

    I'd agree with Mark except for two little irritations of mine when
    discussing this. "Remote Area" was a term that worked when we just
    sprinklered big boxes that housed either factories or warehouses
    as the "remote area" (furthest from the rider) was typically the
    hydraulically most demanding area. These days that area can be
    anywhere (a grid being the always example). Hydraulically most
    demanding area is too muchoif a mouthful for describing itself so
    I just prefer design or demand area. This pet peeve came about
    from teaching newbies the basics as they'd often get it in their
    minds that remote meant furthest away and so would want to
    calculate the the x number of heads at the greatest distance as
    the crow flies over the plan. That is also the basis of pet peeve
    two that "remote area" also suggests that there is only one
    possibility and it's easy to find. Determining the design area(s)
    is an art. I have an exercise based on a building no one would
    ever build but it gas over a dozen potential design areas and just
    as Mark says the student needs to determine where and which are
    most likely by estimating demand at each location.


    On Tuesday, August 30, 2016, <[email protected]
    <mailto:[email protected]>> wrote:

        My personal belief is that the designer “designs” the “remote”
        area into the system, and a good designer will design the
        overall system to economically benefit from “where” the remote
        area lies. Unfortunately, I think most systems are laid out,
        sized, and then calculations are performed to determine where
        the remote area lies.

        As Steve says “just my opinion”

        Mark at Aero

        602 820-7894

        *From:*Sprinklerforum
        [mailto:[email protected]
        
<javascript:_e(%7B%7D,'cvml','[email protected]');>]
        *On Behalf Of *Bill Brooks
        *Sent:* Tuesday, August 30, 2016 8:32 AM
        *To:* [email protected]
        <javascript:_e(%7B%7D,'cvml','[email protected]');>
        *Subject:* RE: Flexheads in small renovation (Calculation
        Software)

        You will be able to tell this question is based on minimum
        software application experience, but does current software
        automatically determine “most demanding”?  Or, is it up to the
        human operator to guess where this area might be?  If it’s a
        guess, how do you know you have chosen correctly?

        Bill Brooks

        *From:*Sprinklerforum
        [mailto:[email protected]
        
<javascript:_e(%7B%7D,'cvml','[email protected]');>]
        *On Behalf Of *Steve Leyton
        *Sent:* Tuesday, August 30, 2016 10:40 AM
        *To:* [email protected]
        <javascript:_e(%7B%7D,'cvml','[email protected]');>
        *Subject:* RE: Flexheads in small renovation

        To underscore John’s point, these fittings impose with a
        SUBSTANTIAL pressure loss.   As 3^rd party, we would ask for
        calculations to prove the performance of the revised
        configuration.

        SL

        *From:*Sprinklerforum
        [mailto:[email protected]
        
<javascript:_e(%7B%7D,'cvml','[email protected]');>]
        *On Behalf Of *Michael Hill
        *Sent:* Tuesday, August 30, 2016 6:11 AM
        *To:* [email protected]
        <javascript:_e(%7B%7D,'cvml','[email protected]');>
        *Subject:* RE: Flexheads in small renovation

        I agree with Richard, it needs to be evaluated. It is known
        that flex piping is generally more demanding than their hard
        piped counterparts. If the base building design did not
        include flex piping, I would look at it as a change to base
        building design and perform a quick calculation to see how it
        looks. I assume they didn’t use excessively long flex pipe
        with more bends or lops than were needed.

        Mike Hill

        *From:*Sprinklerforum
        [mailto:[email protected]
        
<javascript:_e(%7B%7D,'cvml','[email protected]');>]
        *On Behalf Of *Todd Williams
        *Sent:* Tuesday, August 30, 2016 8:39 AM
        *To:* [email protected]
        <javascript:_e(%7B%7D,'cvml','[email protected]');>
        *Subject:* RE: Flexheads in small renovation

        This is a single story building. Multiple looped 4" and 3"
        cross mains with branches to wings. (Think nursing home with
        interior court yards). No fire pump. 100 psi static with a
        flat curve (2 year old test, DeltaE = 0). Area in question not
        most hydraulically remote but toward that end of the building.
        Branch lines are fed from the loop, not a DE branch main. LH
        occupancy.

        I am not worried about this not being adequate, more a
        consensus of what needs to be done and what is correct.

        Todd G Williams, PE

        Fire Protection Design/Consulting

        Stonington, CT

        860-535-2080 (ofc)

        860-608-4559 (cell)

        Sent using CloudMagic
        <https://cloudmagic.com/k/d/mailapp?ct=ti&cv=6.0.64&pv=8.2>

        On Tue, Aug 30, 2016 at 8:22 AM, Richard Carr
        <[email protected]
        <javascript:_e(%7B%7D,'cvml','[email protected]');>> wrote:

            I can’t disagree with John (Hi John) but we need more info
            to make the call,

            In remote area?

            Fire pump?

            What is safety margin on existing?

            What is friction loss on the flex?

            Just because you add 4 flex piping to an existing system
            does not require it to be calculated. But does need to be
            evaluated.

            Richard Carr, SET

            Branch Manager

            Cox Fire Protection, Inc

            6555 Grace Lane.

            Jacksonville, Fl. 32205

            [email protected]
            <javascript:_e(%7B%7D,'cvml','[email protected]');>

            904-781-8227

            *From:*Sprinklerforum
            [mailto:[email protected]
            
<javascript:_e(%7B%7D,'cvml','[email protected]');>]
            *On Behalf Of *John Irwin
            *Sent:* Tuesday, August 30, 2016 7:14 AM
            *To:* [email protected]
            
<javascript:_e(%7B%7D,'cvml','[email protected]');>
            *Subject:* RE: Flexheads in small renovation

            I disagree with Richard. (Hi Richard!)

            Relocating these sprinklers with flex heads may very well
            change the location of the most hydraulically remote area
            to the place you are working. Flex-heads come with a
            substantial pressure loss. Even if doing calculations
            wasn’t required, I would want to do them for myself for
            peace of mind. My belief has always been that you can’t
            tax the system without verifying that it still works.

            *John Irwin*

            Manger – Fire Sprinkler Division

            *Critical System Solutions, LLC
            *Cell: 813.618.2781

            Email: [email protected]
            <javascript:_e(%7B%7D,'cvml','[email protected]');>

            *From:*Sprinklerforum
            [mailto:[email protected]
            
<javascript:_e(%7B%7D,'cvml','[email protected]');>]
            *On Behalf Of *Richard Carr
            *Sent:* Tuesday, August 30, 2016 7:08 AM
            *To:* [email protected]
            
<javascript:_e(%7B%7D,'cvml','[email protected]');>
            *Subject:* RE: Flexheads in small renovation

            Are the relocates in the remote area? if not I would not
            calc. also , some flex brands are better that others as
            far as friction loss.

            Richard Carr, SET

            Branch Manager

            Cox Fire Protection, Inc

            6555 Grace Lane.

            Jacksonville, Fl. 32205

            [email protected]
            <javascript:_e(%7B%7D,'cvml','[email protected]');>

            904-781-8227

            *From:*Sprinklerforum
            [mailto:[email protected]
            
<javascript:_e(%7B%7D,'cvml','[email protected]');>]
            *On Behalf Of *Todd Williams
            *Sent:* Tuesday, August 30, 2016 6:30 AM
            *To:* [email protected]
            
<javascript:_e(%7B%7D,'cvml','[email protected]');>
            *Subject:* Flexheads in small renovation

            I have a client that did a 4 sprinkler relocate job in an
            office and used Flexheads (no sprinklers added). If the
            sprinklers were connected with hard pipe, I would probably
            not do hydraulic calculations. Given that we have FHs,
            should I be doing a full 900 or 1500 sqft calculation?

            Todd G Williams, PE

            Fire Protection Design/Consulting

            Stonington, CT

            860-535-2080 (ofc)

            860-608-4559 (cell)

            Sent using CloudMagic
            <https://cloudmagic.com/k/d/mailapp?ct=ti&cv=6.0.64&pv=8.2>



-- Sent from Gmail Mobile



    _______________________________________________

    Sprinklerforum mailing list

    [email protected]
    <mailto:[email protected]>

    http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to