I would respectfully disagree with the below analogy. 

Example: (4) Story building consisting of 30K SF per floor

Single lead-in supply- combo standpipe with floor controls.

How can it be considered a single system when it exceeds the allowable floor 
space per riser?

Just sayin’

 

Jeff Bridges

JBFP Inc

 

 

 

 

I have to disagree with this analysis that a floor control valve defines a 
system. A floor control valve is not even defined individually in 2013 whereas 
a sprinkler system is (no mention of floor control valves) as are control 
valves. As always, I would consider a system to be what it has always been and 
the addition of the required floor control valve and associated requirements on 
systems in multi-story buildings just nationally codifies a common practice 
hereabouts of building a system that has isolatable floors. This way an entire 
large building does not need to be drained to make a repair or for a T.I., 
leaves fore protection in service on floors not effected and also conserves 
water.  I'm open to an argument that changes my mind but this one doesn't.

 