There is a difference because we select pumps based on our codes and our
codes are different.

All pumps have a Required Net Positive Suction Head that is independent of
site specific Available NPSH and so-called 'demand'. NFPA 20 requires a
minimum Available NPSH that is conservative (~27 ft). For most pumps I have
seen the Required NPSH is 10-15 ft, so that should take care of that unruly
area closest to the pump.

Brad
On Feb 3, 2017 1:53 PM, "Reza Esmaeili" <[email protected]> wrote:

> Thanks for all the comments.
>
> Foreword: If your total flow demand is 1000GPM, you MUST select a 1000GPM
> rated pump!
>
> Some years ago, when I was reading about fire pumps, I came across two
> points as follows:
> Point 1- Pumps shall furnish not less than 150 percent of rated capacity
> at not less than 65 percent of total rated head.
> Point 2- Motors should operate on any point of the fire pump curve without
> exceeding the motor service factor.
>
> To me the philosophy behind mentioned points are: If the calculated flow
> demand at the most remote area is for example1000GPM, there is a
> possibility that more sprinklers are activated in fire condition (or the
> sprinklers closer to pumps are activated) and the flow may increase up to
> 1500GPM, in this case both the pump and the motor should be able to endure
> such increase. The above point 1 guarantees that the pump can provide
> 1500GPM at a reasonable pressure drop not making serious problem for the
> sprinkler system. The point 2 also guarantees that the motor can endure
> working at 1500GPM. In other words, in my opinion, if flow demand at the
> most remote area is 1000GPM, I should select a 1000GPM rated capacity pump
> which can run up to 1500GPM. This is like having 50% safety factor. This is
> my understanding of the above two mentioned points.
>
> My problem is the below point 3 which destroys the above theory.
> Point 3- Maximum system demand flow should be between 90% and 140% of
> pump’s rated capacity, but, in no case, greater than 150% of the pump’s
> rated capacity.
> Based on point 3, if my flow demand at the most remote area is 1000GPM, I
> am allowed to simply choose a pump rated at 750GPM, this is not a tight
> selection and every fire protection engineer accept such selection. But
> imagine a designer select a 750GPM rated pump for 1125GPM flow demand and
> NFPA allows this selection. However I don't accept a 750GPM for my 1000GPM
> flow demand because it's against my theory in point 1 & 2. I believe that
> the pump rated capacity should fall below the flow demand. That's what
> European standards require as follows:
>
> VdS CEA 4001 Standard in Europe: The flow demand for the most remote area
> shall fall below the permitted rate at all times.(In other words: If your
> flow demand is 1000GPM, the pump should be rated at least for 1000GPM). The
> maximum flow demand may exceed the permitted rate by up to 40%. The
> pressure shall not fall by more than 30%. (In other words: Pumps shall
> furnish not less than 140 percent of rated capacity at not less than 70
> percent of total rated head.).
>
> Would you please let mw know where I am making mistake and why there is
> such a big difference between Americans and Europeans in selecting fire
> pumps. Thank you!
>
>  All Best,
>
>  Reza Esmaeili
>
>  Email:[email protected]
>  Cell: +98 912 2444875
>  Web: www.sarian.ir
>
>
>
>
> --------------------------------------------
> On Tue, 1/31/17, Steve Leyton <[email protected]> wrote:
>
>  Subject: RE: Selecting a Fire Pump/ Europeans vs. Americans
>  To: "[email protected]" <sprinklerforum@lists.
> firesprinkler.org>, "[email protected]" <[email protected]
> >
>  Date: Tuesday, January 31, 2017, 12:58 AM
>
>  And if an area closer to
>  the water supply - i.e. LESS hydraulically remote - than the
>  design should flow, it will not overflow more than the water
>  supply can produce.  If a design area requires 1,400 GPM,
>  more hydraulically efficient groups of sprinklers might
>  theoretically flow more at the same residual pressure, but
>  that doesn't create an 1,800 GPM demand in one or more
>  of those areas.  It's all on paper ...
>
>  So the pump will produce to
>  its rated residual pressure at overload (150%) and that will
>  adequately supply any area in the building up to the demand
>  that was calculated at the MRA.   We only need
>  1,400 and the less remote areas will flow that at a higher
>  residual at the pump than will the MRA (higher net K), so
>  everything's okay.
>
>  Right?
>
>  SL
>
>  -----Original Message-----
>  From: Sprinklerforum [mailto:[email protected].
> org]
>  On Behalf Of [email protected]
>  Sent: Monday, January 30, 2017 1:14 PM
>  To: [email protected];
>  [email protected]
>  Subject: RE: Selecting a Fire Pump/ Europeans
>  vs. Americans
>
>  A 1000 GPM
>  rated pump will not likely produce a flow rate of 1800 GPM.
>  It will limit out most likely around 1650 to maybe 1700 GPM.
>  It should then, nonetheless provide the minimum design
>  density at the lest demanding design area. There is no code
>  requirement to produce the maximum flow capacity of a design
>  area, only the minimum.
>  Mark at Aero
>  602 820-7894
>
>  -----Original Message-----
>  From: Sprinklerforum [mailto:[email protected].
> org]
>  On Behalf Of Reza Esmaeili
>  Sent: Monday,
>  January 30, 2017 1:56 PM
>  To: [email protected]
>  Subject: Selecting a Fire Pump/ Europeans vs.
>  Americans
>
>   I am glad to
>  write in this nice forum again!
>
>  I don’t understand NFPA 20 for selecting fire
>  pump: “Maximum system demand flow should be between 90%
>  and 140% of pump’s rated capacity, but, in no case,
>  greater than 150% of the pump’s rated capacity”.
>
>  That is to say if my total
>  sprinkler and hose demand is 1400GPM, I can simply choose a
>  1000GPM rated pump. 1400GPM is calculated based on the most
>  remote sprinklers, so what if the sprinklers nearer to pumps
>  are activated and my demand jump to 1800GPM? Then at high
>  flow, there is a possibility for cavitation and overloading
>  the motor. Am I wrong?
>
>  Europeans calculate differently. They calculate
>  the demand both at the most unfavourable area (most remote
>  area) and most favourable area (near the pump). For example
>  if they calculate 1400GPM at most unfavourable and 1800GPM
>  at most favourable area, then based on these figures they
>  choose a pump. They also check 1800GPM on the pump curve to
>  be sure it’s less than 140% of rated capacity and also
>  less than 16m NPSHr.
>
>  VdS
>  CEA 4001 Standard in Europe: The pump set shall be capable
>  of providing at least the flow and pressure of both the most
>  favourable and the most unfavourable areas. The maximum flow
>  demand (Qmax) for supplying the most favourable area may
>  exceed the permitted rate by up to 40 %. The pressure shall
>  not fall by more than 30 % (of the pressure prevailing with
>  the permitted rate). The flow demand for the most
>  unfavourable area shall fall below the permitted rate at all
>  times.
>
>  NFPA 20 and VdS are
>  somehow the same. They limit the maximum flow demand up to
>  140% of rated capacity, but Europeans really calculate the
>  minimum and maximum demand and check this is less than 140%
>  but American don’t check anything. So if like the above
>  example an American designer make a tight selection
>  (Choosing a 1000GPM pump for 1400GPM demand), is there any
>  possible problem if the sprinklers near the pumps are
>  activated and the pump runs at 1800GPM?
>
>  Best,
>
>  Reza
>  Esmaeili
>
>  Email:[email protected]
>  Cell: +98 912 2444875
>  Web:
>  www.sarian.ir
>  _______________________________________________
>  Sprinklerforum mailing list
>  [email protected]
>  http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>  _______________________________________________
>  Sprinklerforum mailing list
>  [email protected]
>  http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to