I'm sorry, just noticed a typo after sending the last email. First sentence
should've said "change order for cane protection". Big thumbs, little phone
keyboard.


James


On Fri, Nov 17, 2017 at 2:17 PM James Litvak <[email protected]> wrote:

> The conversation started when the architect sent a photo to us of a turned
> up hose valve and said that on a previous project they got hit with a
> change rider for can protection after an inspection failed for not meeting
> accessibility requirements. The architect said that on this project their
> accessibility consultant made sure to point out 307.2 and 307.3, since
> we're in NC and A117.1 is an adopted code here.
>
> As it is, I contacted the local code enforcement and spoke to two people.
> First person said they had never heard of those requirements, but from
> reading them came up with the thought that since the hose valve is parallel
> to the wall, then it might not be considered protruding or overhanging,
> where both code sections are concerned. I was referred to a plans examiner
> who was aware of the sections. It turns out that the NC Department of
> Insurance released their periodic accessibility newsletter addressing
> standpipe valves and accessibility clearance. Interestingly, it focused
> more on the location of standpipes with regard to door maneuvering
> clearances in section 403.2.3.2, and included two photos of a hose valve
> not meeting that sections requirement, but making no mention of it
> violating 307.3. There were also two photos of a hose valve sticking out of
> a wall of a breezeway that is noted as violating 307.2. So it seems that
> both the NC DOI and the local building officials don't interpret a
> standpipe hose valve out of the required accessible clearance path in a
> stairwell to be in violation of 307.3.
>
> I've emailed the architect back, mentioning my conversations with the code
> officials, with a copy of the newsletter, and also a mention of my post and
> the responses here (admittedly, Steve, also highlighting your position on
> the 14 TC and how this is the first you've heard of this). They've sent it
> back to their accessibility consultant for review. For now, it seems the
> preferred design is to turn the valve up because that would put it in
> compliance with 307.3. However, I don't like the idea of a
> misinterpretation of the code leading to a possible precedent, so I'm going
> to seek out a more in depth answer from code enforcement.
>
>
> James
>
>
>
>
> On Thu, Nov 16, 2017 at 11:02 AM Steve Leyton <[email protected]>
> wrote:
>
>> Concur and I’m still puzzled as to how the conversation with the EOR
>> ended up in the context of ANSI A1171.1.   We have always coordinated the
>> location of standpipe risers (and the attached hose valves), floor control
>> assemblies and collection drain risers with the available space on the
>> landing.   There’s a minimum required path of travel clearance and (at
>> least in the markets we serve) NOTHING can be in that space.   So you draw
>> a dashed line for the radius of that path and keep your stuff out of it.
>>
>>
>> SL
>>
>>
>>
>> *From:* Sprinklerforum [mailto:
>> [email protected]] *On Behalf Of *John
>> Drucker
>> *Sent:* Thursday, November 16, 2017 5:48 AM
>>
>>
>> *To:* [email protected]
>> *Subject:* RE: ANSI A1171.1 Figure 307.3
>>
>>
>>
>> Guys,
>>
>>
>>
>> It’s pretty simple code section, the opening text of 307 sets the scope;
>> “Many items along the path of travel can be protruding object for persons
>> with visual impairments, or persons who may be momentarily distracted.
>> There are additional concerns during emergency events where smoke may
>> obscure objects and people are hurrying to escape”  There’s also concerns
>> with visually impaired persons being able to detect protrucing objects with
>> a long cane.
>>
>>
>>
>> The idea is to NOT have anything sticking out, generally more than 4”,
>> that a person could walk into.   I’ve seen this plenty of times where
>> risers come up a stair in the middle of the landing with the valve sticking
>> straight out. That puts it in the travel path and subjects pedestrians to
>> striking the object, injury, risk of falling etc.   Keep in mind also that
>> a stairways primary function is means of egress and not a mechanical shaft
>> so technically anything that impairs that primary mission could be cited.
>>
>>
>>
>> We need to reach back to the core mission and not get caught up in the
>> manusha.  Get the stuff out of the travel path, ours are in the corners
>> with the valves parallel and tight enough to the wall to allow the valve to
>> be hand opened and slightly canted outward to allow coupling up of the
>> hose.
>>
>>
>>
>> Bottom line this is something that requires a collaborative approach
>> between the architect and the fire protection engineer at the design stage
>> not at the installation phase, i.e. 10# of stuff in 5# bag.
>>
>>
>>
>>
>>
>> John Drucker, CET
>>
>> Assistant Construction Official
>>
>> Fire Protection Subcode Official
>>
>> Electrical Subcode Official
>>
>> Building Inspector
>>
>> Borough of Red Bank, NJ
>>
>> 90 Monmouth Street
>>
>> Red Bank, New Jersey 07701
>>
>> Cel/Text: 732-904-6823
>>
>> Email: [email protected]
>>
>>
>>
>>
>>
>>
>>
>>
>>
>> *From:* Sprinklerforum [
>> mailto:[email protected]
>> <[email protected]>] *On Behalf Of *Travis
>> Allen- Allen Engineering
>> *Sent:* Wednesday, November 15, 2017 5:37 PM
>> *To:* [email protected]
>> *Subject:* RE: ANSI A1171.1 Figure 307.3
>>
>>
>>
>> Much Ado About Nothing, indeed :-). The safe answer is always to check
>> with the AHJ, for sure.
>>
>>
>>
>> However, whether it’s a post or pylon has little to do with following the
>> bouncing ball of the code, even if it leaves us shaking our heads. The
>> provision doesn’t only apply to posts or pylons. A117.1.2009 has the same
>> requirement in 307.2 for any protrusion in a circulation path: “307.2
>> Protrusion Limits. Objects with leading edges more than 27 inches (685 mm)
>> and not more than 80 inches (2030 mm) above the floor shall protrude 4
>> inches (100 mm) maximum horizontally into the circulation path. EXCEPTION:
>> Handrails shall be permitted to protrude 4 1/2 inches (115 mm) maximum.”
>> Same language as the IBC.
>>
>> This sure smells like a circulation path as defined by the code:
>> “CIRCULATION PATH. An exterior or interior way of passage from one place to
>> another for pedestrians.” And I can’t find any exceptions for exit
>> enclosures or fire systems. And I hate to say it, but NFPA 14 is not the
>> governing code, and it is silent on protruding objects in circulation paths
>> anyway. Hopefully the AHJ will weigh the factors and design efforts to keep
>> the sprinkler system from becoming an occupant hazard, where an
>> accessibility consultant might not.
>>
>>
>>
>> I’ll get back to my college football playoff pool now, since it was
>> upended this weekend.
>>
>>
>>
>> - Travis
>>
>>
>>
>> *From:* Steve Leyton [mailto:[email protected]
>> <[email protected]>]
>> *Sent:* Tuesday, November 14, 2017 3:07 PM
>> *To:* [email protected]
>> *Subject:* RE: ANSI A1171.1 Figure 307.3
>>
>>
>>
>> James:
>>
>> I know this comes off sounding a little big-headed but …  I’m the chair
>> of the committee and I’ve never heard of such balderdash.   This isn’t a
>> “post” or a “pylon” – those are structures.   This is a pipe and part of a
>> “building system” and also a part of the fire/life safety apparatus.   The
>> applicable dimensions are the ones that define clear egress path on the
>> landings (as per the building code) and the elevation above fin floor as
>> prescribed in NFPA 14 and/or per the responding fire agency.     Whether
>> the ports point out, down at a 45° angle or straight down at the floor is
>> also up to the responding fire agency.   I think your idea of getting an
>> superseding opinion from the local AHJ (BO or FO) is sound.
>>
>>
>> SL
>>
>>
>>
>> *From:* Sprinklerforum [
>> mailto:[email protected]
>> <[email protected]>] *On Behalf Of *James
>> Litvak
>> *Sent:* Tuesday, November 14, 2017 1:09 PM
>> *To:* [email protected]
>> *Subject:* Re: ANSI A1171.1 Figure 307.3
>>
>>
>>
>> The standpipe is in a stairwell. Some of the stairs it'll be in the
>> corner, others beside the door. All of them will be outside the required
>> path of egress clearance. The definition of circulation path in A117.1 is
>> "An exterior or interior way of passage from one place to another for
>> pedestrians". It's pretty vague. Unfortunately there's no differentiation
>> between, say, a hallway or a stairwell. I think I'll contact the building
>> department and see what they think. Hopefully they'll write something for
>> me saying that section doesn't apply.
>>
>>
>>
>>
>>
>> On Tue, Nov 14, 2017 at 3:40 PM Mike B Morey <[email protected]>
>> wrote:
>>
>> Unfortunately other than the fact that the drawings in the 3## section
>> make it pretty obvious this isn't what they're talking about, there's no
>> definitions.  I figured if its a stairwell it's an easier shoot down for
>> someone who wants to write their own interpretations since the conspicuous
>> absence of stairs in pretty much this entire standard should make it pretty
>> open and shut.  You could argue its not those things and that the previous
>> section says leading edge, which the leading edge of the handle if you put
>> it parallel to the floor probably isn't more than 4" out.  Basically this
>> code section is to keep someone tapping a cane against the edge of the
>> walking path from slamming into some random protruding object, if they hit
>> the hand wheel it may not be super pleasant but its not the kind of
>> protrusion, IMHO, this section addresses.  Just one of those fun common
>> sense vs power trip things probably.  Standard disclaimer, these are my
>> opinions only and have not been approved or reviewed by my employer.
>> ------------------------------
>>
>>
>> *Mike Morey*
>> *CFPS 3229 • NICET S.E.T. 123677*
>> *Project Manager* • Fire Protection Group
>> * Shambaugh & Son, LP **an EMCOR Company*
>> 7614 Opportunity Drive • Fort Wayne, IN • 46825
>> *direct *260.487.7824* /  cell *260.417.0625* /  fax *260.487.7991
>> * email *[email protected]
>>
>>
>>
>>
>>
>>
>>
>> From:        "rongreenman ." <[email protected]>
>> To:        [email protected]
>> Date:        11/14/2017 03:25 PM
>> Subject:        Re: ANSI A1171.1 Figure 307.3
>> Sent by:        "Sprinklerforum" <
>> [email protected]>
>> ------------------------------
>>
>>
>>
>>
>> Does the standard define the standpipe as a post or pylon?
>>
>> On Tue, Nov 14, 2017 at 12:10 PM Mike B Morey <[email protected]>
>> wrote:
>> Where is the standpipe located?  Are we talking a typical stairwell
>> install or elsewhere?  Section 307 starts off by stating that it governs
>> circulation paths, and stairs aren't part of that definition in section
>> 1005 based on a quick look.  The standard is available several places
>> online if you google it, not sure if they're "legal" copies but for the
>> sake of answering the question I'd take a look at that angle.  If its in a
>> hall or something I'd imagine it could be put in a box in the wall or
>> something.
>> ------------------------------
>>
>>
>> * Mike Morey*
>> * CFPS 3229 • NICET S.E.T. 123677*
>> * Project Manager* • Fire Protection Group
>> * Shambaugh & Son, LP **an EMCOR Company*
>> 7614 Opportunity Drive • Fort Wayne, IN • 46825
>> * direct *260.487.7824* /  cell *260.417.0625* /  fax *260.487.7991
>> * email *[email protected]
>>
>>
>>
>>
>>
>>
>>
>> From:        James Litvak <[email protected]>
>> To:        "[email protected]" <
>> [email protected]>
>> Date:        11/14/2017 02:59 PM
>> Subject:        ANSI A1171.1 Figure 307.3
>> Sent by:        "Sprinklerforum" <
>> [email protected]>
>> ------------------------------
>>
>>
>>
>>
>> I'm working on building permit plans for a job, and the architect passed
>> on an email from their accessibility consultant that the fire department
>> hose valves can't protrude beyond the standpipe riser more than 4", per
>> ANSI A117.1 figure 307.3. The text of that section is:
>>
>> 307.3 Post-Mounted Objects. Objects on posts or pylons shall be permitted
>> to overhang 4 inches (100 mm) maximum where more than 27 inches (685 mm)
>> and not more than 80 inches (2030 mm) above the floor. Objects on multiple
>> posts or pylons where the clear distance between the posts or pylons is
>> greater than 12 inches (305 mm) shall have the lowest edge of such object
>> either 27 inches (685 mm) maximum or 80 inches (2030 mm) minimum above the
>> floor.
>>
>> What they're saying is that we will need to turn an elbow up from the
>> outlet of the standpipe and install the valve vertical. I've already told
>> them this won't work anyway, since the valve itself has a 5" hand wheel,
>> and due to takeouts, the least amount of projection physically possible is
>> about 8". According to the consultant, the way to mitigate this is to
>> install cane protection, which the architect appears to want to avoid. Is
>> anyone aware of this code section, and does it apply the way I'm being told
>> it does? In nearly 13 years as a designer, I've never been told such a
>> requirement exists.
>>
>>
>> James
>> Charlotte, NC_______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>>
>> https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwICAg&c=GKdB6-XpYq_0W-WluyVHtw&r=z4t2hrRBa-JsS06T4X_uuYOSJoclVWgSRO8Nq6TDdsg&m=wiCt1iqr5u69Txm-iBELel0Xzd3F5uGuCJUQXBz1wqg&s=xRsf5UToNzmQSkkENHTI-JrcpESCaLYKnTi-kcXYGmg&e=
>>
>> This message is for the named person's use only. It may contain
>> confidential, proprietary or legally privileged information. No
>> confidentiality or privilege is waived or lost by any mistransmission. If
>> you receive this message in error, please immediately delete it and all
>> copies of it from your system, destroy any hard copies of it and notify the
>> sender. You must not, directly or indirectly, use, disclose, distribute,
>> print, or copy any part of this message if you are not the intended
>> recipient.
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>>
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> <https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwMFaQ&c=GKdB6-XpYq_0W-WluyVHtw&r=z4t2hrRBa-JsS06T4X_uuYOSJoclVWgSRO8Nq6TDdsg&m=5qwVwJLjSTa1NIX64A78M2wWVYYDHlGdPLp5aekf9Eg&s=hCvxa01YwdjeSk4O21JWnAfEVWaoF93WIMHJkrFr_lM&e=>
>> --
>> Sent from Gmail Mobile[attachment "attcgpkb.jpg" deleted by Mike B
>> Morey/Shambaugh/EMCORGROUP]
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>>
>> https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwICAg&c=GKdB6-XpYq_0W-WluyVHtw&r=z4t2hrRBa-JsS06T4X_uuYOSJoclVWgSRO8Nq6TDdsg&m=5qwVwJLjSTa1NIX64A78M2wWVYYDHlGdPLp5aekf9Eg&s=hCvxa01YwdjeSk4O21JWnAfEVWaoF93WIMHJkrFr_lM&e=
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>>
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>>
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to