Not a P.E. Place high weight on being able to follow listing.

Sent from my iPhone

> On May 31, 2018, at 16:11, Parsley Consulting <[email protected]> 
> wrote:
> 
> Scott, 
> 
> I agree completely.  Thanks for sharing that video, and it does identify 
> quite clearly that when they're installed properly the Flex Heads supplying 
> sprinklers will resist the resulting forces and remain in the installed 
> position. Pretty decent proof of their response.
> 
> This does make me think over the provisions in §9.2.3.4.4.1, §9.2.3.4.4.4, 
> §9.2.3.5.2.2, and §9.2.5.4.2 with respect to upward motion or thrust that 
> were placed in the standard, probably by some stodgy old TC members who need 
> to be voted out.
> 
> There is some provision in the standard in §9.2.1.3.3.3 which requires any 
> flexible drop fitting longer than 6' is provided with a hanger.  For such a 
> stodgy old TC member my memory of that discussion was that it was quite 
> "energetic" and was a frank exchange of contrary ideas at high decibel levels.
> 
> just my memories,
> Ken Wagoner, SET
> Parsley Consulting
> 350 West 9th Avenue, Suite 206
> Escondido, California 92025
> Phone 760-745-6181
> Visit the website
> 
>> On 05/31/2018 2:45 PM, Mitchell, Scott wrote:
>> https://www.youtube.com/watch?v=n5fJ1lCVE98
>> 
>> Looks like a decent kick to me.
>> 
>> Scott
>> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to