To all, both the Flex Head and the Victaulic brand are UL listed and FM
approved for installation in fire sprinkler systems. Thus as long as you are
installing per the manufacturers instructions then you are good.
 NFPA 13 section 9.2.3.3.1 Says " shall be installed in accordance with
their listing" so if you have followed the listing for the brand you are
using then you are in accordance with NFPA 13 and there should be no further
requirements.


-----Original Message-----
From: Sprinklerforum <[email protected]> On
Behalf Of [email protected]
Sent: Friday, June 1, 2018 12:45 PM
To: [email protected]
Subject: Sprinklerforum Digest, Vol 63, Issue 1

Send Sprinklerforum mailing list submissions to
        [email protected]

To subscribe or unsubscribe via the World Wide Web, visit
        
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

or, via email, send a message with subject or body 'help' to
        [email protected]

You can reach the person managing the list at
        [email protected]

When replying, please edit your Subject line so it is more specific than
"Re: Contents of Sprinklerforum digest..."

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to